    Re: Strage Pipework Configuration



    Quote Originally Posted by marc5180 View Post
    Chillerman,
    A suction line accumulator should be sufficiently sized to hold the entire charge of the system.
    Hi Marc

    should it ?

    you got me, when it comes to designing and component choice

    but does seem excessive to me mate

    If correct ...would you say this units accumalator is big enough ?

    R;s chillerman


    If the World did not Suck, We would all fall off !

  2. #52
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    http://www.stara.co.kr/parker_catalo...og/40-10-7.pdf
    Quote Originally Posted by chillerman2006 View Post
    Hi Marc

    should it ?

    you got me, when it comes to designing and component choice

    but does seem excessive to me mate

    If correct ...would you say this units accumalator is big enough ?

    R;s chillerman

  3. #53
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    On a heat pump air conditioner the defrost is nearly (if not always) carried out by the hot gas method, i.e. the reversing valve is energised to flood the outdoor coil with "hot gas". As this coil will be 90% full of liquid it will be pushed down the suction line and has to be collected by the accumulator to protect the compressor - hence the accumulator must be able to hold the entire charge.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #54
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    Systems with a thermostatic expansion valve (TEV), the
    accumulator holding capacity should be approximately 50%
    of the system charge.
    from parker

  5. #55
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    Quote Originally Posted by marc5180 View Post
    On a heat pump air conditioner the defrost is nearly (if not always) carried out by the hot gas method, i.e. the reversing valve is energised to flood the outdoor coil with "hot gas". As this coil will be 90% full of liquid it will be pushed down the suction line and has to be collected by the accumulator to protect the compressor - hence the accumulator must be able to hold the entire charge.
    Argh, I see cheers

    So does the hidden accumalator have that capacity, mate

    (marc's thinking ''I started this thread for answers not starting up a training school )

    R's chillerman
    If the World did not Suck, We would all fall off !

  6. #56
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Strage Pipework Configuration

    I could be wrong but....I always thought a suction accumulator should be sized for 50% of refrigerant charge and a liquid receiver was 100% of charge.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  7. #57
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    http://www.refrigerationbasics.com/1...eat_pumps1.htm
    in defrost mode the liq still travels through the 4 way valve and creates cooling in the evap thats why ur indoor fan slows down whilst in defrost mode

  8. #58
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    stu u are wrong,but u are correct! brownie point for u!!

  9. #59
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    Quote Originally Posted by install monkey View Post
    Thanks Install

    have kept a copy of that, a useful bit of info Cheers

    Quote Originally Posted by stufus View Post
    I could be wrong but....I always thought a suction accumulator should be sized for 50% of refrigerant charge and a liquid receiver was 100% of charge.
    Cheers
    Stu
    Hi Stu

    as per 'Installs' link you would be correct mate on refrigeration systems

    But it does not state clearly for systems with reverse cycle or for heat pumps

    And 'Marc s' comment makes sense, would you agree ?

    R's chillerman
    If the World did not Suck, We would all fall off !

  10. #60
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Haha far from it CM,
    Install, i've read what Parker say that and by the size of the accumulator that is fitted then i would say they have probably used one that is 30-50% of the entire charge but what happens if a componet fails.
    The size of an accumulator is based upon the size of the error, and the likelihood of the error you think can occur
    The difference between genius and stupidity is that genius has its limits.

    Marc

  11. #61
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Haha far from it CM,
    Install, i've read what Parker say that and by the size of the accumulator that is fitted then i would say they have probably used one that is 30-50% of the entire charge but what happens if a componet fails.
    The size of an accumulator is based upon the size of the error, and the likelihood of the error you think can occur
    The difference between genius and stupidity is that genius has its limits.

    Marc

  12. #62
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by chillerman2006; 02-10-2011 at 07:51 PM.
    If the World did not Suck, We would all fall off !

  13. #63
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    you dont have the power to give fractions yet! haha-nike 123 give me a pic of a pint of guiness and a bird wrapped in duct tape- that wasnt frowned upon!!

  14. #64
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Quote Originally Posted by install monkey View Post
    http://www.refrigerationbasics.com/1...eat_pumps1.htm
    in defrost mode the liq still travels through the 4 way valve and creates cooling in the evap thats why ur indoor fan slows down whilst in defrost mode
    Liquid travels through a 4 way valve?? Where?

    On a 4 way rv you have discharge and suction vapour pressures not liquid.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  15. #65
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    my bad

  16. #66
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Strage Pipework Configuration

    Suction accumulators are also system specific IE you should not use a standard SA on a heatpump system due to the orifice size being to big and allowing liquid slugging to the compressor especially in heating.
    http://www.henrytech.com/Tips/HT-TT14.pdf
    C
    heers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  17. #67
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by chillerman2006; 02-10-2011 at 07:51 PM.
    If the World did not Suck, We would all fall off !

  18. #68
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Strage Pipework Configuration

    I've heard half system charge as a rule of thumb for accumilator sizing.

    Jon
    Mostly found in Oxfordshire, UK :)

  19. #69
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    chillerman
    Last edited by install monkey; 02-10-2011 at 08:31 PM.

  20. #70
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Strage Pipework Configuration

    Thanks Marc

    You've had one electrical fault and the other sounds like liquid flood back, i'm with install on this,these dx units must be held off in ambients below 16c, i know theres plenty of heat at the minute but i doubt that was the case before this week? If the units are required to run in lower ambients you've a sizing issue. I can't imagine a heat pump with no accumulator, so look at control strategy and airflow first, see Gary we do listen!!

    al
    Mostly found in the southern part of this green and pleasant land.

  21. #71
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    hmmm-post missed with all the chat over accumulators-other points to consider-
    no crankcase heater on the pot, system is within the airflow so exposed to 10-40deg ambient, no jacket on the compressor, as u say no suction accumulator or evap press reg, as with air handling units normally 100% fresh air then sticking a cooling coil in there there is not a constant load so theyve done well sticking an electronic expansion valve-at least it will be more responsive, also them check vavles will need checking to ensure theyre not passing as with the 4 way valve as its too easy to chuck a pot in and watch it destroy itself, also i would look at the control strategy, comp restart delay, setpoint differential it should have a free cooling setpoint that usually is set around 16 deg which will stop the mechanical cooling and rely on fresh air.
    are the v belts ok,if fitted,panel filters blocked as they normally last 3mth also check alarm history, is there a lp swith on it or transducer, may be sartup of the compressor causing pipework to flex and the lp being auto reset??
    are the fans inverter driven whats the minimum speed or is it controlled of duct pressure?
    i could nip up to site as its in my hood!!haha

  22. #72
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    Install

    Just because no-one replied to your post the last time round

    R's chillerman
    Last edited by chillerman2006; 02-10-2011 at 08:29 PM.
    If the World did not Suck, We would all fall off !

  23. #73
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    my post co






    Last edited by install monkey; 02-10-2011 at 08:30 PM. Reason: cut out the adverts!!

  24. #74
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by MikeHolm; 03-10-2011 at 10:29 PM.

  25. #75
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    molson per
    Last edited by install monkey; 02-10-2011 at 08:29 PM.

  26. #76
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by MikeHolm; 03-10-2011 at 05:47 PM.

  27. #77
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Strage Pipework Configuration

    irrevelant
    Last edited by MikeHolm; 03-10-2011 at 05:47 PM.

  28. #78
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by chillerman2006; 02-10-2011 at 07:50 PM.
    If the World did not Suck, We would all fall off !

  29. #79
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    is that ur
    Last edited by install monkey; 02-10-2011 at 08:29 PM.

  30. #80
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by MikeHolm; 03-10-2011 at 05:46 PM.

  31. #81
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by chillerman2006; 02-10-2011 at 07:49 PM.
    If the World did not Suck, We would all fall off !

  32. #82
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    irrelevant
    Last edited by chillerman2006; 02-10-2011 at 07:48 PM. Reason: sorry marc
    If the World did not Suck, We would all fall off !

  33. #83
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    11 posts spamming.....
    The difference between genius and stupidity is that genius has its limits.

    Marc

  34. #84
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Quote Originally Posted by al View Post
    Thanks Marc

    You've had one electrical fault and the other sounds like liquid flood back, i'm with install on this,these dx units must be held off in ambients below 16c, i know theres plenty of heat at the minute but i doubt that was the case before this week? If the units are required to run in lower ambients you've a sizing issue. I can't imagine a heat pump with no accumulator, so look at control strategy and airflow first, see Gary we do listen!!

    al
    These units are only designed to temper the air and so run all year round using a recouperator and a mixture of fresh air and return air
    When the outdoor temp gets to cold they use full return recirculation with minimum fresh air.
    The minimum air onto the coil is 18DegC.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  35. #85
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Strage Pipework Configuration

    Check the accumulators for size and correct piping (inlet/outlet), could be worth getting a thermal camera for a day to see what's going on?
    al
    Mostly found in the southern part of this green and pleasant land.

  36. #86
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Quote Originally Posted by install monkey View Post
    no crankcase heater on the pot
    Not all compressors have visible crankcases though do they? Many of them have a voltage going through the windings to heat the compressor a few degrees.

    Quote Originally Posted by install monkey View Post
    system is within the airflow so exposed to 10-40deg ambient, no jacket on the compressor
    Minimum air onto these coils/compressors is 18DegC

    Quote Originally Posted by install monkey View Post
    also i would look at the control strategy, comp restart delay, setpoint differential it should have a free cooling setpoint that usually is set around 16 deg which will stop the mechanical cooling and rely on fresh air.
    Compressor restart delay is 6 min. These have a recouperator that mixes fresh air and return air and if the temp is still too high/low then the compressors will be brought on. The setpoint for the building is 21/22 degress C so the compressors don't need to be on often....supposedly.

    Quote Originally Posted by install monkey View Post
    are the v belts ok,if fitted,panel filters blocked
    Filter/belts ok

    Quote Originally Posted by install monkey View Post
    alarm history, is there a lp swith on it or transducer, may be sartup of the compressor causing pipework to flex and the lp being auto reset??
    Yes theres an LP switch on it, looked at alarm history and found only the 1 LP fault.
    Compressor flex and reset the LP alarm ?? Can that happen??

    Quote Originally Posted by install monkey View Post
    are the fans inverter driven whats the minimum speed or is it controlled of duct pressure?
    Yes the fans are inverter driven and have been commissioned to run at 50hz

    Quote Originally Posted by install monkey View Post
    i could nip up to site as its in my hood!!haha
    Lol, Nip up to the site to do what?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  37. #87
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Thermal camera? To check what?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  38. #88
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Strage Pipework Configuration

    check the accumulator for a start, also check your 4 way valve and NRV's.

    In fairness this is either the site completely screwing up the units or they have been misapplied or specced?

    al
    Mostly found in the southern part of this green and pleasant land.

  39. #89
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Strage Pipework Configuration

    Copeland say that the scroll is compliant, it can handle liquid flood back ( a slug of liquid), say after defrost, in this case it is the position of the EEV temp and pressure sensor causing prolonged oil dilution,
    Accumulator size, without knowing all the data I would just go for one which is has the same size pipe as the comp inlet. You could even look a suction/liquid line heat exchanger (between the EEV sensor and the comp)

  40. #90
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Strage Pipework Configuration

    MF, i've found scrolls less tolerant of flood back, more inclined to wash oil out and not return it, accumulator would be essential as you say.

    al
    Mostly found in the southern part of this green and pleasant land.

  41. #91
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Thats a good idea al, I may suggest that.

    When i find out more i'll update the thread, thanks for your input. Much appreciated
    The difference between genius and stupidity is that genius has its limits.

    Marc

  42. #92
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    Gents

    just a quick thought as bed time for me

    dont certain copeland scroll models have built in accumalators that allows them to take full liquid and boils it off by compressor heat ???

    R's chillerman
    If the World did not Suck, We would all fall off !

  43. #93
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Strage Pipework Configuration

    Quote Originally Posted by al View Post
    MF, i've found scrolls less tolerant of flood back, more inclined to wash oil out and not return it, accumulator would be essential as you say.

    al
    Before I starting producing my units, I did considerable testing on the scrolls, and found that under certain circumstances liquid return was a problem, so even though the tech data says i do not need a accumulator, I do fit one, in my mind it is cheap protection.

    CM; copeland scrolls do not have a built in Acc, Maneurope recip comps do. (twin shell)

  44. #94
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Strage Pipework Configuration

    Quote Originally Posted by mad fridgie View Post
    Before I starting producing my units, I did considerable testing on the scrolls, and found that under certain circumstances liquid return was a problem, so even though the tech data says i do not need a accumulator, I do fit one, in my mind it is cheap protection.

    CM; copeland scrolls do not have a built in Acc, Maneurope recip comps do. (twin shell)
    Thanks Mad

    Thought I was going 'mad' when the thought appeared in me head, argh so its maneuropes (recips) Cheers for correction

    Also picked up a site with a right mickey mouse abortion of a setup (1st visit today) with 4 copeland scrolls, it looks a right b*tch to change 3 of the four compressors

    Mad, in your eyes, whats the perfect suction superheat for copeland scrolls (as I need them to purr for ever)

    R's chillerman
    Last edited by chillerman2006; 03-10-2011 at 06:24 PM.
    If the World did not Suck, We would all fall off !

  45. #95
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Strage Pipework Configuration

    Is anyone doing a failure test on the failed compressors

  46. #96
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Strage Pipework Configuration

    Can Copeland Scroll compressors handle liquid?
    ANSWER: Scrolls handle liquid better than most other compressor types, but still can require additional accessories for optimal protection. Those accessories include: Accumulators are recommended for systems with large refrigerant charge or those that allow for uncontrolled refrigerant floodback. Crankcase heaters are required for three-phase systems with large refrigerant charge and in/outdoor applications.
    ref copelands website

  47. #97
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Strage Pipework Configuration

    Just to update the thread. The system was found to have a leak on the equalising line. The manufacturers went back to site to repair.
    Thanks to everyone who contributed
    The difference between genius and stupidity is that genius has its limits.

    Marc

  48. #98
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Strage Pipework Configuration

    Nice one Marc, thanks for the closure!!

    al
    Mostly found in the southern part of this green and pleasant land.