    compressor is burning



    Need your help? please
    We have 40 hp DWM Discus compressors 6 month old.
    It woks 4 month well , but in power station we had electric shock , and compressor is burned and we repaired it in 2 month Compressor is burned 3 times,
    Room temperature = -18
    Outside temperature = +30
    We have control phase in system and delay time for stating and after defrosting system and over load, I checked electric panel 2 times nothing wrong .
    All pressure are good and current is good about 38 A and Mechanical parts compressor is good
    But we did not change gas (R22) or drier after burning of gas,
    Reason of burning could be from of acidity of gas or not?



  2. #2
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: compressor is burning

    Hi MBC,

    Gas is not acidic, it is oil which could be acidic and damaging your compressors. If you haven't changed the oil, nor filters, you still have a corrosive ambient in the circuit. It is not necessary to replace the oil, as long as you are able to recycle it. Check the oil pH.

    Regards,

    Nando.

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: compressor is burning

    Quote Originally Posted by mbc View Post
    Need your help? please


    We have 40 hp DWM Discus compressors 6 month old.

    It woks 4 month well , but in power station we had electric shock , and compressor is burned and we repaired it in 2 month Compressor is burned 3 times,


    Room temperature = -18

    Outside temperature = +30

    We have control phase in system and delay time for stating and after defrosting system and over load, I checked electric panel 2 times nothing wrong .

    All pressure are good and current is good about 38 A and Mechanical parts compressor is good

    But we did not change gas (R22) or drier after burning of gas,


    Reason of burning could be from of acidity of gas or not?
    Hello.

    You say you had a power failure and that caused the first comp to fail?
    and only after a few months others have failed?

    Check all the electrics.

    Check the oil pressure switch and the main contactors.

    If there is a problem with the supply and the comp is stopping and
    starting it will fail.

    If the comp failed because of a electrical fault (power surge) then that
    should not burn the gas or the oil. But if you suspect the oil you can put
    burn out dryers into the system to help remove any acids that may be there.

    All the best

    taz

    .

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: compressor is burning

    dear sir
    every times after burning compressor I changed the oil and put new oil (suniso 3 GS) .
    I checked all pressure and oil pressure .
    oil pressure comes off after 120 sec. high is set for 20 Bars , low about 0.3 bars,

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: compressor is burning

    Check this Copeland directions and comply in full at what is stated there and you shold be safe that compressor will not burn again because of previous burnings.
    http://www.hvacrinfo.com/cope_ae_bulletins/TAE1105.PDF

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: compressor is burning

    fit suction burn out driers,regularly check pressure drop accross as they are not meant to be left in- also i recommend testing the oil ph level and maybe use acid away-neutraliser-did u change the contactor,liq drier from last time

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: compressor is burning

    Has it got head cooling fan and liquid injection ?

  8. #8
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: compressor is burning

    Along with finding the root cause of the failure ,the compressor protection devices need to be checked ,i assume a compressor this size would have thermal , voltage & amps protection that obviously didnt work

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: compressor is burning

    Most compressors burnuot caused by electrical problems, so unless it has some mechanical problem, I'd check the electrical system real good.

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: compressor is burning

    Does system have crankcase pressure regulator, to protect compressor from high current draw after defrost.

  11. #11
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: compressor is burning

    dear magoo.
    No I did not put crankcase pressure regulator (CPR) , but I put this system.
    after finishing defrost system does not works for 4 minutes and then fans come on and after 90 second compressor comes on , so we have not high pressure in crankcase,
    also I want to recover gas R22 and put new gas on it for more safety side .