    Re: Bazed plate heat exchanger and capillary tube

    It works great for me.
    I have bought water chiller but i was told it have 3kW of cooling power... but i does not have, only 1,7kW.
    So i have to build extra 2.0kW chiller to cool water that next will go to my first chiller (with water tank).
    So i can say i builded "pre-cooling" chiller. I always have the same water temperature on inlet to heat exchanger and always the same water capacity (m3/h). And what i can say... few hours of testing, cappilary tube cuting and it works great

    I need no flexibility, in my aplication there will be no changes (It is a testing equipment and i need this extra chiller for testing only one part (out of 20 others)