    Ice bulding up in Evaporator's hangers



    Hello!

    I'm having troubles on a Freezer room where two big Evaporators (900kg) are mounted on the ceiling with 8 metal hangers (threaded rods), some of this rods are getting ice build up at the inside of the room, (some not all of them). I've insulated the exterior part of the hangers and worked for a short time but again the ice is coming back.

    Have you deal with this trouble? Do you know if there are non-metal hangers for a 900kg Evaporator?

    Thanks!!



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice bulding up in Evaporator's hangers

    Plastic threaded rods, nuts, washers, etc. are available.

  3. #3
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Ice bulding up in Evaporator's hangers

    Thanks Gary.
    Could you post a manufacturer/dealer website link please? I haven't found long enough rods here in Mexico.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Ice bulding up in Evaporator's hangers

    George

    Have you water leaking in to some of the rods? Plastic can become brittle at low temps, i'd stick with metal.Maybe check the roof first for poor sealing?

    al
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice bulding up in Evaporator's hangers

    Quote Originally Posted by georgedvf View Post
    Thanks Gary.
    Could you post a manufacturer/dealer website link please? I haven't found long enough rods here in Mexico.
    http://www.usplastic.com/

  6. #6
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Ice bulding up in Evaporator's hangers

    Thanks al.

    I didn't see no water on the roof, I already did re-sealing at the rods but the ice is still building up.

  7. #7
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Ice bulding up in Evaporator's hangers

    Quote Originally Posted by Gary View Post
    Thanks, let me check it.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Ice bulding up in Evaporator's hangers

    http://www.bluemay.co.uk/plastic_fas...eaded_rod.html
    technical info states m20 rod rated for 215kg so unless u have 6 rods evenly loaded-u might struggle with the weight-how about a low wattage trace heater tape? usually u bolt the evaps to the ceiling so there is no rod on show

  9. #9
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: Ice bulding up in Evaporator's hangers

    are the evaps opposite each other ? do they go on defrost at seperate times ? if they do one set of rods will be warmed by heat from evaps moisture forms when warm meets cold put them on defrost at same time and check termination temps as they maybe getting to hot on a defrost and being steel they will conduct heat cold either way have a look at RSJ they hanging on see how warm it gets
    I can fix broke but I cant fix stupid :)

  10. #10
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Ice bulding up in Evaporator's hangers

    Quote Originally Posted by simon@parker View Post
    are the evaps opposite each other ?
    Yes, they are.
    do they go on defrost at seperate times ?
    No, they go on defrost at the same time.

    I do will check how hot it gets on defrost, they have electrical defrost heaters.

  11. #11
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Ice bulding up in Evaporator's hangers

    is the connection between the evaps and the rods isolated whit rubbers or silent blocs?
    maybe its capylairy?

    ice