    How to set TXV temperature in Brazed Plate Heat Exchanger. I am assembling a chiler for water temperature of 34 degree F. The temperature range printed on TXV is from -49 to +50 F
    Dec 2008
    Portugal
    42
    1,040
    13
    Re: Low Evaporating Temp TXV
    What kind / brand is your TXV?
    Dec 2009
    Pakistan
    55
    12
    It is Danfoss TEX2 for R22
    Dec 2008
    Portugal
    42
    1,040
    13
    What's the evaporating temperature and superheating that is concern to the selection of the plate heat exchanger?
    Dec 2009
    Pakistan
    55
    12
    The target Evaporating temperature is 35 F or 2 C. Not sure about superheat
    What kind of design chanes required for different evaporating temperatur like very low temperature freezers for ice cream hardning
    Dec 2008
    Portugal
    42
    1,040
    13
    Quote Originally Posted by nadeem.usmani View Post
    Please inform about the inlet and outlet water temperature.
    Dec 2009
    Pakistan
    55
    12
    Sorry for late reply The detail of the chiller is as following
    It is a water chiller for a Bakery
    Ref Capacity 10 ton
    Tank Capacity 90 gal
    Water Circulation 30 gal / min
    Delta Temp 10 C
    Required wter temp 2 C
    Water Draw from tank 30 gal after every 20 miniuts
    I think I have made a mista to ask you the design Evap temp of 2 C or 34 F. I think it should be some where minus 5 C (to achive 2 C water)
    Sep 2003
    ISRAEL
    66
    4,152
    38
    What is the PHE capacity?
    The TXV size has to fit that capacity regardless the evaporting temp. When you get this info, you can determine the condensing unit size, Or you can check your 10 ton refrigeration unit capacity at -5C and then work out the TXV size and PHE capacity at your required water flow and leaving temp.
    Remember that water freezez at 0C so you might need to add some glycol but that will decrease the unit capacity.
    Dec 2008
    Portugal
    42
    1,040
    13
    That's right chemi-cool. But you have to keep in mind that the "size" of the TXV is also affected by the evaporating temperature. Lowering the evaporating temperature less capacity it allows considering the same superheat.
    Dec 2009
    Pakistan
    55
    12
    My basic question is still there
    How to lower the evap temp setting of TXV
    The way I understand the factory setting is @ 7 C
    How to make it -5 C
    May 2008
    803
    11
    watch out for the low temps in your plate evap. remember the 4C fase change of water!!
    if yore flow is not strong enough.....sh...t will happen
    Ice
    Dec 2008
    Portugal
    42
    1,040
    13
    How to make it -5 C
    Why do you say it came 7C. The valve adjust itsel to new dynamic conditions. The thing you can some how adjust is the superheat but even so it can vary depending of the moment liquid demand.