    Hello everyone,

    i have problem with my Trane chiller RTAC250 that is low evaporator Rfgt Temp - ct1
    and sometimes the same compressor tripped by low suction Rfgt pressure - ct1.so what shall i do?
    Thanks



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Hi Cool King

    Ask an engineer to sort out the problem

    R's chillerman
    Last edited by chillerman2006; 24-09-2011 at 07:38 PM. Reason: too short - not added regards
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane chiller RTAC250

    Hi
    you should takeCM 's advice!
    this problem is something a tech that is qualified will be able yo deal with .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Sep 2009
    Location
    libya
    Age
    41
    Posts
    35
    Rep Power
    0

    Re: Trane chiller RTAC250

    good evening,

    these massages appaer as alarm so i think the unit needs more gas, is that right?

    thanks

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Quote Originally Posted by cool king2007 View Post
    good evening,

    these massages appaer as alarm so i think the unit needs more gas, is that right?

    thanks
    Evening Cool King

    this does not have to be a refrigerant charge issue

    it could quite as easily be a problem with part of the system

    unless you can provide a full list of operating conditions

    temperatures/pressures at various points

    water temperature in/out confirm flow, correct vessel resistance

    Its hard to give you an answer and really needs an engineer to attend to diagnose

    R's chillerman
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    14

    Re: Trane chiller RTAC250

    Hello ,

    As per my experience , i have seen that mostly " low evaporator pressure " is due to low level of refrigerant in the chiller.In addition , there may be some problem in expansion valve.

    Cool king , please provide us various parameters as chillerman said.

    Have a good weekend.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Trane chiller RTAC250

    I can think of at least 6 or 7 other things that will or could give the same fault.
    In fact I have had to remove refrigerant charge from chillers maintained by very experianced engineers,who made the same assumption.
    The advise being given is cautious for a reason, without the correct facts damage could occur.


    Grizzly
    Last edited by Grizzly; 25-09-2011 at 10:06 AM.

  8. #8
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Quote Originally Posted by Grizzly View Post
    I can think of at least 6 or 7 other things that will or could give the same fault.
    In fact I have had to remove refrigerant charge from chillers maintained by very experianced engineers,who made the same assumption.
    The advise being given is cautious for a reason, without the correct facts damage could occur.


    Grizzly
    Hi Grizzly
    You had them too mate,
    last one stuck flow switch, pumps not running(turned off der!)
    and had to drag out over 22kg that had been dumped in
    its quite amazing sometimes how dangerous a little bit of knowledge can be
    & why do companies allow some to work on our kit...beats me
    well with f-gas quals being so hard..things should improve
    R's chillerman
    If the World did not Suck, We would all fall off !

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Trane chiller RTAC250

    Thanks for the input chillerman.
    Yep assuming can be humbling!
    I prefer to say nowadays, "With what I know so far it would be a good starting point."
    We all do it!
    Chillers as you know have lots of reasons for displaying Low Suction or Temps.
    Many times only because it's the first Fault parameter listed.

    I hope coolking has not taken offence and keeps us all informed.
    It would be interesting as what the actual cause of the alarms is.
    Grizzly

  10. #10
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Quote Originally Posted by Grizzly View Post
    Thanks for the input chillerman.
    Yep assuming can be humbling!
    I prefer to say nowadays, "With what I know so far it would be a good starting point."
    We all do it!
    Chillers as you know have lots of reasons for displaying Low Suction or Temps.
    Many times only because it's the first Fault parameter listed.

    I hope coolking has not taken offence and keeps us all informed.
    It would be interesting as what the actual cause of the alarms is.
    Grizzly
    Yeah me too mate
    I was referring to ones who worked on kit prior to me

    If he can start to list the conditions it wont take long to confirm whats going on
    Just did not want him chucking in refrigerant if not needed

    CoolKing we still here for you if we can help mate

    R's chillerman
    If the World did not Suck, We would all fall off !

  11. #11
    Join Date
    Sep 2009
    Location
    libya
    Age
    41
    Posts
    35
    Rep Power
    0

    Re: Trane chiller RTAC250

    Hello everyone,

    Operation conditions for TRANE chiller RTAC250 at different times:
    at 8:00 am (SEP 27,2011)
    Modes
    chiller mode: Running
    circuit 1 mode: Auto
    cprsr1A mode: Auto
    cprsr1B mode: stopped
    circuit2 mode: Running
    cprsr2A mode: Running
    Chiller
    Evap leaving water Temp: -7.2c
    Evap Entering water Temp: -5.7c
    Active chilled water setpoint:-7
    outdoor air temp: 26.9c
    compressor
    1A
    Amps L1 L2 L3 : 0.0 0.0 0.0
    %RLA L1 L2 L3 : 0.0 0.0 0.0
    unit volts : 418
    oil Temp: 28.1c
    Intermediate oil pressure: 127kpag
    suction pressure: 124kpag
    1B
    Stopped Because comm. Loss: Starter 1B
    2A
    Amps L1 L2 L3: 120.0 115.0 113.0
    % RLA L1 L2 L3: 62.6 58.5 55.5
    Oil Temp: 58.9c
    Intermediate oil pressure: 803kpag
    Suction pressure: 104kpag
    Rfgt ckt1 ckt2
    Cond Rfgt pressure: 614 939 kpag
    Sat cond Rfgt Temp: 27.3 41.0 C
    Evap Rfgt pressure: 125 104 kpag
    Sat Evap Rfgt Temp: -6.9 -9.4 C
    Evap Approach Temp: …… 2.7 C
    Rfgt liquid level: -8 -4 mm
    ---------------------------------------------------------------------------------------
    at 10:50 am (SEP 27,2011)
    Modes
    chiller mode: Running
    circuit 1 mode: stopped by Low Evaporator Rfgt Temp-Ckt1 at 10:30AM
    cprsr1A mode: Auto
    cprsr1B mode: stopped (comm. Loss: Starter 1B)
    circuit2 mode: Running
    cprsr2A mode: Running
    Chiller
    Evap leaving water Temp: -6.9c
    Evap Entering water Temp: -5.3c
    outdoor air temp: 29.2c
    compressor
    1A
    Amps L1 L2 L3 : 0.0 0.0 0.0
    %RLA L1 L2 L3 : 0.0 0.0 0.0
    unit volts : 415
    oil Temp: 30.9c
    Intermediate oil pressure: 116kpag
    suction pressure: 113kpag
    2A
    Amps L1 L2 L3: 140.0 135.0 130.0
    % RLA L1 L2 L3: 71.6 69.0 67.0
    Oil Temp: 62.4c
    Intermediate oil pressure: 933kpag
    Suction pressure: 101kpag
    Rfgt ckt1 ckt2
    Cond Rfgt pressure: 669 1021 kpag
    Sat cond Rfgt Temp: 29.9 43.3 C
    Evap Rfgt pressure: 113 102 kpag
    Sat Evap Rfgt Temp: -8.4 -9.7 C
    Evap Approach Temp: …… 2.7 C
    Rfgt liquid level: -15 0 mm
    ---------------------------------------------------------------------------------------
    at 12:04PM (SEP 27,2011)
    Chiller
    Evap leaving water Temp: -6.8c
    Evap Entering water Temp: -4.9c
    outdoor air temp: 28.7c
    compressor
    1A
    Amps L1 L2 L3 : 68.0 64.0 61.0
    %RLA L1 L2 L3 : 50.4 47.6 44.6
    unit volts : 408
    oil Temp: 32.7c
    Intermediate oil pressure: 653kpag
    suction pressure: 70kpag
    2A
    Amps L1 L2 L3: 141.0 135.0 129.0
    % RLA L1 L2 L3: 71.6 68.5 66.2
    Oil Temp: 62.1c
    Intermediate oil pressure: 924kpag
    Suction pressure: 105kpag
    Rfgt ckt1 ckt2
    Cond Rfgt pressure: 708 1009 kpag
    Sat cond Rfgt Temp: 31.7 43.3 C
    Evap Rfgt pressure: 110 105 kpag
    Sat Evap Rfgt Temp: -8.7 -9.3 C
    Evap Approach Temp: 1.8 2.5 C
    Rfgt liquid level: 3 1 mm
    ---------------------------------------------------------------------------------------
    at 12:13PM (SEP 27,2011) circuit 1
    Low Evaporator Rfgt Temp-Ckt1
    1A
    Amps L1 L2 L3 : 0.0 0.0 0.0
    %RLA L1 L2 L3 : 0.0 0.0 0.0
    unit volts : 410
    oil Temp: 51.3c
    Intermediate oil pressure: 50kpag
    suction pressure: 48kpag
    1A at 12:18 PM
    Amps L1 L2 L3 : 68.0 64.0 61.0
    %RLA L1 L2 L3 : 50.5 48.0 44.5
    unit volts : 411
    oil Temp: 58.1c
    Intermediate oil pressure: 676kpag
    suction pressure: 69kpag

    1A at 12:21 PM
    Amps L1 L2 L3 : 67.0 64.0 61.0
    %RLA L1 L2 L3 : 50.3 47.5 44.5
    unit volts : 411
    oil Temp: 60.6c
    Intermediate oil pressure: 651kpag
    suction pressure: 48kpag

    1A at 12:22 PM
    Amps L1 L2 L3 : 68.0 64.0 61.0
    %RLA L1 L2 L3 : 50.8 47.5 44.0
    unit volts : 404
    oil Temp: 61.3c
    Intermediate oil pressure: 680kpag
    suction pressure: 131kpag
    ---------------------------------------------------------------------
    at 2:57 PM (SEP 27,2011)
    Modes
    chiller mode: Running
    circuit 1 mode: stopped by Low Evaporator Rfgt Temp-Ckt1 at 12:41 PM
    cprsr1A mode: Auto
    cprsr1B mode: stopped (comm. Loss: Starter 1B)
    circuit2 mode: Running
    cprsr2A mode: Running
    Chiller
    Evap leaving water Temp: -6.7c
    Evap Entering water Temp: -5.2c
    outdoor air temp: 28.9c
    compressor
    1A
    Amps L1 L2 L3 : 0.0 0.0 0.0
    %RLA L1 L2 L3 : 0.0 0.0 0.0
    unit volts : 407
    oil Temp: 32.3c
    Intermediate oil pressure: 132kpag
    suction pressure: 129kpag
    2A
    Amps L1 L2 L3: 138.0 134.0 129.0
    % RLA L1 L2 L3: 70.2 68.2 65.5
    Oil Temp: 61.2c
    Intermediate oil pressure: 916kpag
    Suction pressure: 105kpag
    Rfgt ckt1 ckt2
    Cond Rfgt pressure: 666 1017 kpag
    Sat cond Rfgt Temp: 29.9 43.6 C
    Evap Rfgt pressure: 127 104 kpag
    Sat Evap Rfgt Temp: -6.7 -9.5 C
    Evap Approach Temp: …… 2.8 C
    Rfgt liquid level: -8 -1 mm
    ---------------------------------------------------------------------------------------

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Hi CoolKing

    lets see if we can diagnose this for you

    All the readings need to be taken manualy and not off the controller

    Need to know what refrigerant first ?

    Then allow chilled water temperature to rise enough to call for compressor to run at full load 100%

    Now at full load (no saturated temperatures - actual real temperatures)

    List the answers to these conditions below

    Water or Air cooled condensor

    If air cooled - air on & air off
    If water cooled - water in & water out

    Ambient temperature

    Discharge pressure
    Discharge temperature
    Condensor outlet temperature
    Liquid line temperature (after the drier)

    Suction pressure
    Suction temperature

    Evaporator temps/pressure taken through binda point

    Water in
    Water out
    Water return pressure
    Water flow pressure

    R's chillerman
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane chiller RTAC250

    could you give me the complete model of the machine? if it's 250TR has two circuits each circuit with a compressor.

  14. #14
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: Trane chiller RTAC250

    you need an engineer there simple

    long list of possible problems. refrigerant is the last thing you want to look at and one of the most expensive.

    no one can actually help without you having the right tools, besides fgas rules

  15. #15
    Join Date
    Sep 2009
    Location
    libya
    Age
    41
    Posts
    35
    Rep Power
    0

    Re: Trane chiller RTAC250

    Quote Originally Posted by serviceman View Post
    could you give me the complete model of the machine? if it's 250TR has two circuits each circuit with a compressor.
    Hi serviceman,
    The machine is Air Cooled Series RTM Helical-Rotary Liquid Chiller, Model RTAC250, Fluid R134a, with two circuits first one has two compressors 1A,1B. Second one has one compressor 2A.
    our problem with the first circuit that is compressor 1B stop by Comm loss: starter 1B and this is ok because we are waiting for STARTER MODULE for this compressor. But compressor 1A trips by Low Evaporator Rfgt Temp-Ckt1 and sometimes by Low suction Rfgt pressure-Ckt1.

    please let me know For further information

    Thanks

  16. #16
    Join Date
    Sep 2009
    Location
    libya
    Age
    41
    Posts
    35
    Rep Power
    0

    Thumbs up Re: Trane chiller RTAC250

    Quote Originally Posted by sweimaker View Post
    you need an engineer there simple

    long list of possible problems. refrigerant is the last thing you want to look at and one of the most expensive.

    no one can actually help without you having the right tools, besides fgas rules
    Thanks for your advice, and i am here trying to solve the problem

  17. #17
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Trane chiller RTAC250

    Quote Originally Posted by chillerman2006 View Post
    Hi CoolKing

    lets see if we can diagnose this for you

    All the readings need to be taken manualy and not off the controller

    Need to know what refrigerant first ? R134a

    Then allow chilled water temperature to rise enough to call for compressor to run at full load 100%

    Now at full load (no saturated temperatures - actual real temperatures)

    List the answers to these conditions below

    Water or Air cooled condensor

    If air cooled - air on & air off
    If water cooled - water in & water out

    Ambient temperature

    Discharge pressure
    Discharge temperature
    Condensor outlet temperature
    Liquid line temperature (after the drier)

    Suction pressure
    Suction temperature

    Evaporator temps/pressure taken through binda point

    Water in
    Water out
    Water return pressure
    Water flow pressure

    R's chillerman
    Quote Originally Posted by cool king2007 View Post
    Thanks for your advice, and i am here trying to solve the problem
    Cool king

    answer all the above questions and first to see it will be able to help you

    am on here most nights myself

    R's chillerman
    If the World did not Suck, We would all fall off !

  18. #18
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane chiller RTAC250

    COOL KING:

    The Starter Module did not receive a transition complete signal in the designated time from its command to transition. The must hold time from the Starter Module transition command is 1 second. The Must trip time from the transition command is 6 seconds. Actual design is 2.5 seconds. This diagnostic is active only for Y-Delta, Auto-Transformer, Primary Reactor, and X-Line Starters.

  19. #19
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Trane chiller RTAC250

    This is a specific starter test where 1M(1K1) is closed first and a check is made to ensure that there are no currents detected by the CT's. If currents are detected when only 1M is closed first at start, then one of the other contactors is shorted.

    LOW TEMP EVAP.


    (calculated from suction pressure transducer dropped below the Low Refrigerant Temperature Cutout Setpoint for 1125°F-sec with a 8°F-sec/sec max integral rate applied during circuit startup transient (or 4ºF-s/s if manifolded and only one cprsr running) while the circuit was running early in the circuit’s cycle. The minimum LRTC setpoint is -5°F (18.7 Psia) the point at which oil separates from the refrigerant. During the time that the trip integral is non zero, the unload solenoid(s) of the running compressors on the circuit, shall be energized continuously and the load solenoid shall be off. Normal load/unload operation will be resumed if the trip integral decays to zero by temps above the cutout setpoint. The integral is held nonvolatily though power down, is continuously calculated, and can decay during the circuit’s off cycle as conditions warrant.

    LOW PRESS EVAP:


    a. The Suction Refrigerant Pressure (or either of the compressor suction pressures) dropped below 10 Psia just prior to compressor start (after EXV preposition). b. The pressure fell below 16 Psia while running after the ignore time had expired, or fell below 10 Psia (or 5 Psia in sftw prior to Oct’02) before the ignore time had expired. The ignore time is function of outdoor air temperature. Note: Part b. is identical to Low Evaporator Refrigerant Temperature diagnostic except for the trip integral and trip point settings.

    QUESTION:

    have changed the initial charge of oil?