    Heat star super plus 2000



    Hi every one has any one out there had to change the water temp control mc12 , we have a faulty one ordered new control was told that they have replace the mc12 with AC1-5 which is not them same at all . Has any one carried this out thanks Paul



  2. #2
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Heat star super plus 2000

    yes we did but gave up trying to configure the AC1-5 and used a Technologic controller instead. Basically the water controller is only a single stage stat so you could use more or less any similar device, Eliwell, carel, etc.
    Last edited by nevgee; 22-09-2011 at 11:08 PM. Reason: grammar
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  3. #3
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Heat star super plus 2000

    Hi guys fitted the new control today found out that old mc12 is 12v and the new ac1-5 is 240 v . Just changed feed over on transformer ran up all running correctly now