    Re: tx valve bulb location

    Dear All

    Let's clearly define the purpose of having a HE in a system:
    1. To acheive high refrigeration capacity in evaporator.
    2. Maximize utilisation of evaporator on setting the thermostatic expansion valve for minimum superheat.
    3. To prevent sweating and iced-up of suction lines.

    If the bulb is placed after the HE:
    * Suction line will be iced-up
    * More non-useful superheat will be pick up along the suction line outside the refrigerated box(higher TD between ambient & suction line)
    * The net refrigerating effect will be decrease
    * Higher risk of liquid flooding back

    Please correct me if I am wrong.
    Cheers
    Freddy

  2. #2
    Join Date
    Oct 2002
    Location
    australia
    Posts
    28
    Rep Power
    0

    Re: tx valve bulb location

    Quote Originally Posted by freddyng
    Dear All

    Let's clearly define the purpose of having a HE in a system:
    1. To acheive high refrigeration capacity in evaporator.
    2. Maximize utilisation of evaporator on setting the thermostatic expansion valve for minimum superheat.
    3. To prevent sweating and iced-up of suction lines.

    If the bulb is placed after the HE:
    * Suction line will be iced-up
    * More non-useful superheat will be pick up along the suction line outside the refrigerated box(higher TD between ambient & suction line)
    * The net refrigerating effect will be decrease
    * Higher risk of liquid flooding back

    Please correct me if I am wrong.
    Cheers
    Freddy
    i can't see how you could have liquid flooding back if you have measured a superheat of 5k

  3. #3
    Join Date
    Feb 2005
    Location
    Malaysia
    Posts
    7
    Rep Power
    0

    Re: tx valve bulb location

    Hi Adam
    You are absolutely right. There shouldn't be any floodback if you are measuring 5 degree K superheat. But, when during a warm start-up(with sensing bulb located after HE), the evaporator pressure will drop rapidly when the compressor is started and the bulb pressure remains high until the temperature of the bulb is cooled to the normal operating temperature by the suction vapor.
    Naturally, because of the high bulb pressure, the valve will be unbalanced in the open direction during this period and overfeeding of the evaporator will occur until the bulb pressure is reduced. This will eventually cause liquid slugging in the compressor.

    Hope my reply does make sense.

    Cheers
    Freddy

Similar Threads

  1. Whats the prefered solenoid valve location
    By kengineering in forum Commercial
    Replies: 13
    Last Post: 04-02-2006, 12:58 PM
  2. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  3. exp valve location
    By bernard in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 18-08-2005, 10:22 AM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •