    May 2008
    malaysia
    40
    82
    expansion valve sizing
    hi everybody, i m new to refrigeration engineering, hope can get some help, my question is...
    for sizing, i need the following data
    - pressure drop ( the pressure between TEV and compressor suction? )
    - capacity ( compressor capacity? )
    - evaporating temperature ( i have no idea for this )
    for example.. if i have a 37kw compressor
    Sep 2009
    Iran
    66
    672
    1
    Re: expansion valve sizing
    first you have to learn how TEV is works,
    2nd you need these information ,discharge & suction pressure - Room temperature-Evaporator temperature - Evaporator Capacity - and ....
    3rd in table you chose your TEY.
    Sep 2003
    ISRAEL
    72
    4,248
    First you need to choose the right size evaporator for your job, above or below zero, kind of defrost if any, Humidity required in the cold room, etc. etc.
    Choosing the TXV depends of evaporating temp, refrigerant to be used.
    Last comes condensing unit to fit the chosen capacity and ambient temp.
    May 2006
    India
    399
    Pls go through sporlan , danfoss , alco ,catalogs ......... Selection procedures are well explained therein
    11,025
    Try this Sporlan Literature site, it has just about everything that you need to know.
    http://www.sporlanonline.com/literature.shtml
    May 2008
    malaysia
    40
    82
    thanks for your reply, i think i need some time to check it..