    Nov 2008
    canada
    64
    Plate freezer tunnel requirments
    Looking into putting in a plate freezer does anyone know of any links that show examples of piping designs and equipment requirments for such a project? Medium would be ammonia thanx for your time.
    Auckland
    74
    3,357
    37
    Re: Plate freezer tunnel requirments
    more info required, is it a tunnel or a plate freezer, liquid overfeed etc.,
    Dec 2011
    Spain
    22
    Quote Originally Posted by nanuuk View Post
    Are you referring to horizontal Plate Freezer or Vertical Plate Freezers?
    If you are going to install Horizontal plate freezers, you can forget about defrosting system. It would simplify a lot your installation and avoid a lot of problems that can come across with hot gas line (even with a good design). Then, the unit is a typical pump recirculation system evaporating at -35 ºC or -45ºC and with ECO. I suggest not going into a flooded installation. The system has a lot of changes in evap temp from the cycle start to the cycle end.
    If the plate freezer is a vertical one, you have to go for a pump recirculation system and hot gas defrosting. This is mandatory. There are many options for the defrost but, if you contact the plate freezer manufacturers, maybe they can supply the valves assembled from factory. See the pic I found in the internet as an example. If they install the valves .... they have to explain how to regulate them
    I know I didn't give you so much information, but I hope I could help. A refrigerant unit for plate freezers is no so different. The difference come from the ammonia more than from the plate freezer and I assume you are experienced on that. Otherwise, be careful with the links on the web.