    old Manitowoc blowing control fuse



    I have a Manitowoc m#GRO600A that keeps blowing glass fuse on control board. When toggle switch is put in water circulation position, unit runs fine. When toggle switch is put in ice position, there is a loud pop and a blown fuse instantly. Cannot find anything grounded or shorted. Ice sensor relay looked burnt. Installed new unitary board/sensor relay assembly. Installed inline fuse before terminal #4 on board. Same problem. Tried disconnecting condenser fan motor (even though fan cycle should isolate). Same problem. Checked voltage rating on solenoid coils - both coils ok. Found about 500 ohmes through hot gas solenoid coil and dump valve solenoid coil. Voltage supplied to unit is 247v. Checked to make sure all wiring is in the correct place. Suspect there is a short between L1 and L2 somewhere. Breaker hasn't tripped yet. Any ideas?



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: old Manitowoc blowing control fuse

    There's not much on these units, disconnect all solenoids, have you checked contactor feeding compressor?

    al
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    May 2009
    Location
    USA
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: old Manitowoc blowing control fuse

    Al, I have replaced the compressor contactor due to pitting and to eliminate one more component.

  4. #4
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: old Manitowoc blowing control fuse

    I would start by disconnecting things one by one until I isolate the problem. Start with the compressor.

  5. #5
    Join Date
    May 2009
    Location
    USA
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: old Manitowoc blowing control fuse

    I have it repaired now. it was shorted condenser fan wire (dry rotted). Thanks for your help.