I know they have a fresh air in spigot but does anyone know if you can take a spigot (or two) off the side of Daikin cassettes (not roundflow) as we have an office which is being split into 3 and they want to take off from the cassette to feed each side office,we know they won't have control but it's better than nothing and it reduces capacity from the cassette in the reduced office.
TIA
-
17-09-2011, 05:08 PM #2
Re: taking spigots off daikin cassettes
I have done this in the past on mitsu cassettes for similar reasons ,block the outlet in the grille on the side you are taking the spigots off.
Not great but sometimes you just got to do what you can.
cheers
StuTool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
17-09-2011, 06:14 PM #3
Re: taking spigots off daikin cassettes
rb yep u can,on a cassette on the 3 sides there is a rectanglar cutout,use tinsnips and a stanley knife to carefully cut the polysytrene then get a sq to round fitting and insulate it!,as a cheaper option get a 200mm od spigot and get a 200mm od starret cutter and cut the hole first then mount the spigot.
as stufus says gat some 5/8 armaflex and block the outlet on that perticular side,oh and use insulated flexi duct.
i use the white air valves as outlet grilles as its cheaper,for increased performance fit an inline fan with speed controller to give some control.
-
17-09-2011, 06:21 PM #4
Re: taking spigots off daikin cassettes
I saw the rectangle cut outs but couldn't find any details . I will use our nibbler and a 200 dia spigot exactly the same as you. I will offer them the additional fan upgrade but I doubt they will take it as it adds a few hundred to each take off because I wont use those cheap round inline fans as they are far too noisy...
-
17-09-2011, 06:25 PM #5
Re: taking spigots off daikin cassettes
-
17-09-2011, 06:30 PM #6
Re: taking spigots off daikin cassettes
-
17-09-2011, 06:41 PM #7
Re: taking spigots off daikin cassettes
its due to lateral compression-i think desa or mad fridgie can explain how- as for copper pipe only worry when theres a 30mtr coil and its a 6 mtr run-in that case you have pykies on site!