Thread: VRV / VRF Set Free
-
13-10-2005, 09:17 PM #1
VRV / VRF Set Free
Just help commision a vrv this week
its been a long time since i had a play with these machines but i was quite impressed with 410a
system
what a pleasure it was
starting a project next week and ive been told its an hitatchi set free vrf system anyone commisioned one of these are the similair to daikin and fujitsu
(then again i suppose they are all similar exept for the wiring)
Don't promise What you CAN'T DELIVER
-
14-10-2005, 12:04 AM #2
Re: VRV / VRF Set Free
Hi Terrie,
just be sure all dip switch settings are correct before commencing with initial start up of the system(s).
Once all is confirmed the system(s) should operate satisfactory.
BTW there is a nice test function facility on the pcb of the outdoor unit which will save you going around and switching on all the remote controllers.If my memory serves me right the setting for test is on dip switch 4- 1 on (cool test) & both 1 & 2 on for heat test.
Happy commissioning
regards
Jase