    compressor amps mitsii pu-p4yga



    recently fitted a new contactor on a mitsi mr slim pu-p4yga on r407c, faulted by another engineer.put unit in test mode and contactor erratically pull in and out showing uf fault code which is compressor current overload.I checked windings,3 phase balance.Compressor to earth all ok,compressor starting amps 15, running amps between 4-5 but does anyone no if they are the correct amps for that model ?

    Many thanks



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: compressor amps mitsii pu-p4yga

    Hope this helps
    watts/volts = amps
    eg a 415vac compressors with a 100watt motor =4.15 amps
    415/100=4.15

    im guessing your motor is around 1.8kw-1.9kw based on 415 vac and a running current of 4.5 amps
    volts x amps = watts
    Last edited by james10; 13-09-2011 at 08:14 PM.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: compressor amps mitsii pu-p4yga

    Nice formula but id check the service manual!poss outdoor board isnt detecting current

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: compressor amps mitsii pu-p4yga

    me thinks im seeing double on this one

  5. #5
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor amps mitsii pu-p4yga

    yeh that is right amps for running, i kept contactor depressed compressor seemed to run with no undue noise, and discharge was hot so it must be pumping ruling out over current fault due to higher amps pulled if seized. Didn't have time to put on gauges or go more in depth but tommorow i will do the same whilst checking low and high side pressures just to prove compressor working leaving the assumption pcb is fault.

    Cheers for replies

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: compressor amps mitsii pu-p4yga

    clip te whie wire,check the compressor spade connection is ok,ring kooltech for comfirmation i can pm u the number if u want

  7. #7
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor amps mitsii pu-p4yga

    ok will do mate cheers i got number for mitsi anyway il give em a ring to confirm amperage