    Compressor room ventilation requirements for compressor racks??



    Hi Folks,

    I have a 100 horsepower compressor rack fitted with 4 x Copeland 25 HP compressors operating on R22 refrigerant that is cooking in a sauna of a plant room/compressor room because there is no ventilation installed, its + 41 degrees Centigrade!

    The customer is being cooperative and will install cross flow ventilation in the compressor room.

    However he has asked me for the technical ventilation data so he can instruct the ducting company to install it and this has stumped me.

    I have already asked Copeland what the minimum ventilation requirements are and I didn't get a satisfactory answer.

    Question?

    In my application described above would the minimum ventilation requirement be based on volume air changes per hour?, velocity per Compressor horsepower?, heat rejection of compressors?, what is the criteria??

    Is there also a rule of thumb calculation that the ventilation industry uses for compressor racks/Compressor rooms or is it a more complicated calculation?

    Your help would be most appreciated.

    best regards


    buddy

  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Buddy

    not my area mate.... but would be presumptious in thinking it will be based on your heat load & then there will be a calculation as to the air volume you would need to move, to reject the heat

    I know quite a few of the designers use programmes for calcs, try this one it seems popular

    http://www.et.web.mek.dtu.dk/coolpack/uk/download.html

    R's chillerman
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Chillerman3006,

    Thanks for your input and the link.

    I know that it would be based on the heat load but what is the actual criteria as I mentioned on my OP?

    Air Velocity?...Air changes per hour? etc etc etc?

    There must be a minimum ventilation requirement...other wise all compressor rooms would not have ventilation fans fitted just to save on cost.

    best regards


    best regards
    buddy

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Buddy

    was just thinking out loud mate....not my area so sorry can not give a good answer for you

    there are a number on here that would know how to do this..... a few off the top my head

    Peter_1, Magoo, Mad Fridgie, DesA, Tesla,

    If you dont get a response, you could drop them a pm

    am sure they would be happy to help

    Peter & DesA are about in the evening & the others after 21:00 normaly

    R's chillerman
    If the World did not Suck, We would all fall off !

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor room ventilation requirements for compressor racks??

    Not certain of these things but with Gas regulations there are minimum ventilation requirements based on boiler sizes (kW).

    Also the maximum temperature allowed in the UK for boilers houses is 30°C to protect electrical services which should not be above that temperature.

    Different equipment maybe but the electrics are the same.

    [edit]
    Came across this document, albeit American, that details the different calculations required depending on what sort of ventilation you are aiming for. Obviously Imperial units used, sory.

    http://www.reta.com/convention/2008/...tech-paper.pdf
    Last edited by Brian_UK; 12-09-2011 at 11:45 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Brian_UK,

    Yes picked that up myself from the internet, however RETA is an Ammonia organisation so I would think the ventilation requirements are completely different than what is required for a 100 HP compressor rack operating on R22 refrigerant.

    I,m thinking safety, fast evacuation etc

    Thanks for searching though much appreciated.
    buddy

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Buddy

    I have thought how to work this out... maybe its just magic

    Regards Chillerman
    Last edited by chillerman2006; 14-09-2011 at 06:18 AM.
    If the World did not Suck, We would all fall off !

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Compressor room ventilation requirements for compressor racks??

    Buddy

    One way i would do it, and have done so for applications here, is data log the room for 7 days, place temperature monitors at high and low level and then "map" this, you now have a base line temperature load to go off.

    So from there work out what temperature the room needs to be and the air changes needed, use this and go off transformer room which is probably the closest match.

    http://www.alpinefan.com/alpineair_vent_calc.php

    to be honest most are sized on the biggest extract that the room can take, hence the lack of calculations!!

    al
    Mostly found in the southern part of this green and pleasant land.

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Compressor room ventilation requirements for compressor racks??

    Nice one Al

    everyone has missed these posts and buddy & I was wondering if anyone will actually reply

    Regards Chillerman
    Last edited by chillerman2006; 14-09-2011 at 11:31 PM. Reason: No Edit
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Red face Re: Compressor room ventilation requirements for compressor racks??

    its best to cover ur arse, get a rep fr venilation wholesaler,explan the fact that the compressors dont run 24 7 let him size the fans and ductwork, that way your covered when a comp fails and the customer tells u that u designed the ventilation,obviously it was undersized!!.
    Its all a blame game,so if u can deflect the blame u still smell of roses,also were fridgies not duct/ventilation gimps!!!!

  11. #11
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by al View Post
    Buddy

    One way i would do it, and have done so for applications here, is data log the room for 7 days, place temperature monitors at high and low level and then "map" this, you now have a base line temperature load to go off.

    So from there work out what temperature the room needs to be and the air changes needed, use this and go off transformer room which is probably the closest match.

    http://www.alpinefan.com/alpineair_vent_calc.php

    to be honest most are sized on the biggest extract that the room can take, hence the lack of calculations!!

    al
    Hi Al,

    Thanks for your input,

    Good idea about the temp measurements etc, however how would I know what air changes are needed, 5, 10 30??..where would I get this information from for a 100 HP compressor rack?

    And what about the ventilation calcs for a new compressor room?

    Thanks for the link as well.

    best regards

    ,
    buddy

  12. #12
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by al View Post
    Buddy

    One way i would do it, and have done so for applications here, is data log the room for 7 days, place temperature monitors at high and low level and then "map" this, you now have a base line temperature load to go off.

    So from there work out what temperature the room needs to be and the air changes needed, use this and go off transformer room which is probably the closest match.

    http://www.alpinefan.com/alpineair_vent_calc.php

    to be honest most are sized on the biggest extract that the room can take, hence the lack of calculations!!

    al
    Hi Al,

    Thanks for your input,

    Good idea about the temp measurements etc, however how would I know what air changes are needed, 5, 10 30??..where would I get this information from for a 100 HP compressor rack?

    And what about the ventilation calcs for a new compressor room?

    Thanks for the link as well.

    best regards

    ,
    buddy

  13. #13
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Just for your information I emailed a mate of mine who works for Hill-Phoenix in the States and he came back with a figure of 100 CFM per 1 Compressor Horsepower.

    I did ask him where this figure came from and he says he "thinks" its from Copeland, not sure.

    So 10,000 CFM for a 100 HP Compressor rack, but not confirmed?

    I shall contact Copeland/Emerson in the US and see if I can get a straight answer from them and I,ll post the answer on this thread.

    In the mean time anybody else got any ideas/information?...I didnt think it would be so hard to find the information?

    Hey Chllerman2006...Thanks for your support.

    best regards
    buddy

  14. #14
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Install Monkey,

    Good idea always to cover your arse, but where I am working there aint no reps from ventilation wholesalers...and if there was I would not trust them.

    I'm basing that on past experience.

    Thanks for your input.

    best regards
    buddy

  15. #15
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Compressor room ventilation requirements for compressor racks??

    Buddy

    The site i attached has an air change recommendation for an internally positioned transformer, these are normally sited outdoors so i think this would well cover you and you can give the customer this info and get them to sign off on it, ultimately it is the customers instruction that you will be acting on!(that's what i do)

    Al
    Mostly found in the southern part of this green and pleasant land.

  16. #16
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor room ventilation requirements for compressor racks??

    You have 2 issues to look at
    First the compressors are they suction cooled or air cooled, "does the compressor need air flowing over them to keep them cool" This is specific to the compressor make and model. ( not the same as your ventilation) are tech detail will be available. ( Purpose built fans to do the job)

    Depending upon the application ( HT or LT) and operating conditions you can get up to 30% of the electrical input to the compressors reject directly from the compressor so 100Kw rack, say COP of 2, electrical input of 50kw, so compressor heat lost 15Kw, then you consider high losses (oil sep and discharge pipes) very specific, lets 5Kw. are then any other gains, electrical switch boards, VSDs, solar gains, hot water tanks. (assume some) another 5Kw. So total 25Kw.
    Outside air temp 25 C leaving 30C load 25kw, air flow = 4200l/s (will kill it)

  17. #17
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Compressor room ventilation requirements for compressor racks??

    A book on ventilation for mechanical equipment rooms suggests the following :

    8 CFM/BHP combustion air
    2 CFM/ BHP ventilation

  18. #18
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Hi D.D,

    Apologies I don't really understand your post?

    Do you mean 2 CFM per Compressor horsepower for ventilation requirements?
    buddy

  19. #19
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Hi mad fridgie,

    The Compressors are 25 Horsepower Copeland compressors with suction gas cooled motors.

    Copeland Model 6SLW 2500 AW/MD-OOO Compressors both application HT and LT operating on R22 Refrigerant. plus +45 degrees condensing.

    Ambient average +32 degrees Centigrade.
    buddy

  20. #20
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by D.D.KORANNE View Post
    A book on ventilation for mechanical equipment rooms suggests the following :

    8 CFM/BHP combustion air
    2 CFM/ BHP ventilation
    it dont also say you get 100% more use when loss a sqirt of juice does it
    If the World did not Suck, We would all fall off !

  21. #21
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Compressor room ventilation requirements for compressor racks??

    Hi Buddy.
    To get back to your original question.
    Plant room or "specialized Machinery space" layouts and ventilation Requirements are given in EN378.
    I believe the 2008 version gives a lot more detail, as historically certain companies went around installing
    nothing more than corrugated steel bike sheds or lean To's with 4 walls.
    I would not be surprised if this is not what you are referring too?
    It is quite detailed and even refrigerant specific!

    Any respectable company should be able to advise.
    From memory there minimum louvered grill sizes, door details and sizes. Even down to refrigerant alarm and ventilation requirements.
    Another consideration is if the refrigerant leaked out and went "Bang". Would the fabric of the building the plant is in.
    Provide a safe controlled blast area or would you have sheet steel flying around. Possibly in a public car park.
    Obviously the main consideration is the safety of individuals but if applied properly the plant ability to "Breath" is enhanced also!

    You have raised a good point with your customer, where if remedied everyone wins.
    By the way EN378 is Law!

    Grizzly

  22. #22
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by buddy View Post
    Just for your information I emailed a mate of mine who works for Hill-Phoenix in the States and he came back with a figure of 100 CFM per 1 Compressor Horsepower.

    I did ask him where this figure came from and he says he "thinks" its from Copeland, not sure.

    So 10,000 CFM for a 100 HP Compressor rack, but not confirmed?

    I shall contact Copeland/Emerson in the US and see if I can get a straight answer from them and I,ll post the answer on this thread.

    In the mean time anybody else got any ideas/information?...I didnt think it would be so hard to find the information?

    Hey Chllerman2006...Thanks for your support.

    best regards
    This is copied and pasted from Emerson (Copeland) reply to my enquiry. -

    "Two-stage compressors are equipped with a desuperheating expansion valve for interstage cooling, and no auxiliary cooling is required.
    If compressors or condensing units are located in a machine room, adequate ventilation air must be provided to avoid an excessive temperature rise in the room. To allow for peak summer temperatures a 10°F. temperature rise is recommended, although a 15°F. rise in cooler ambients might be acceptable.

    The most accurate calculation is to determine the total heat to be rejected by adding the compressor refrigerating
    capacity at the design operating condition to the heat equivalent of the motor input. The CFM can then
    be calculated by the formula…
    BTU/HR
    CMF = ºTD
    For example, determine the machine room ventilation for an air cooled condensing unit operating at -25°F.
    evaporator, 120°F. condensing with a net refrigeration capacity of 23,000 BTU/HR, 6,400 watts input to the
    compressor motor, and a 1 H.P. condenser fan motor.

    Compressor capacity 23,000 BTU/HR
    Heat equivalent 6400 watts x 3.413 21,843 BTU/HR
    Heat equivalent 1 H.P. fan motor 3,700 BTU/HR
    Total Heat to be Rejected 48,543 BTU/HR
    48,543 BTU/HR
    CMF = 10º TD = 4.854 CFM
    With remote condensers, approximately 10% of the heat rejected is given off by the compressor casting and the
    discharge tubing, and the ventilation can be calculated accordingly.
    For convenience, table 20A gives a quick estimate of
    the ventilation air requirement if only the compressor
    capacity is known.

    COMPRESSOR LUBRICATION
    An adequate supply of oil must be maintained in the crankcase at all times to insure continuous lubrication.
    The normal oil level should be maintained at or slightly above the center of the sight glass while operating.
    An excessive amount of oil must not be allowed in the system as it may result in slugging and possible damage
    to the compressor valves.

    Compressors leaving the factory are charged with naphthenic refrigerant oils. A complete list of acceptable
    refrigerants and lubricants are listed on form #93-11.
    The use of any other oil must be specifically cleared with the Emerson Climate Technologies, Inc. Application
    Engineering Department. The naphthenic base oil has definite advantages over paraffinic base oils because
    separation of refrigerant from paraffinic oils occurs at substantially higher temperatures with the same oilrefrigerant
    concentration.
    When this separation or two phase condition exists the oil floats on top of the refrigerant and the oil pump inlet at the bottom of the sump is fed almost pure refrigerant at start up. The resulting improper lubrication can result in bearing failure. Because
    of the lower separating temperature of naphthenic oil, the possibility of two-phasing is greatly reduced.
    Copelametic® compressors are shipped with a generous supply of oil in the crankcase.

    However the system may require more or less oil depending on the refrigerant charge and the system design.
    On field installed systems, after the system stabilizes at its normal operating conditions, it may be necessary to add or remove oil to maintain the desired level.
    OIL PRESSURE SAFETY CONTROL
    A major percentage of all compressor failures are caused by lack of proper lubrication. Improper lubrication or the
    loss of lubrication can be due to a shortage of oil in the system, logging of oil in the evaporator or suction line due
    to insufficient refrigerant velocities, shortage of refrigerant, refrigerant migration or floodback to the compressor
    crankcase, failure of the oil pump, or improper operation of the refrigerant control devices.
    Regardless of the initial source of the difficulty, the great majority of compressor failures due to loss of lubrication
    could have been prevented. Although proper system design, good preventive maintenance, and operation
    within the system’s design limitations are the only cure for most of these problems, actual compressor damage
    usually can be averted by the use of an oil pressure safety control.
    An oil pressure safety control with a time delay of 120 seconds is a mandatory requirement of the Emerson
    Climate Technologies, Inc. warranty on all Copelametic® compressors having an oil pump. "
    buddy

  23. #23
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by buddy View Post
    Just for your information I emailed a mate of mine who works for Hill-Phoenix in the States and he came back with a figure of 100 CFM per 1 Compressor Horsepower.

    I did ask him where this figure came from and he says he "thinks" its from Copeland, not sure.

    So 10,000 CFM for a 100 HP Compressor rack, but not confirmed?

    I shall contact Copeland/Emerson in the US and see if I can get a straight answer from them and I,ll post the answer on this thread.

    In the mean time anybody else got any ideas/information?...I didnt think it would be so hard to find the information?

    Hey Chllerman2006...Thanks for your support.

    best regards
    This is copied and pasted from Emerson (Copeland) reply to my enquiry. -

    "Two-stage compressors are equipped with a desuperheating expansion valve for interstage cooling, and no auxiliary cooling is required.
    If compressors or condensing units are located in a machine room, adequate ventilation air must be provided to avoid an excessive temperature rise in the room. To allow for peak summer temperatures a 10°F. temperature rise is recommended, although a 15°F. rise in cooler ambients might be acceptable.

    The most accurate calculation is to determine the total heat to be rejected by adding the compressor refrigerating
    capacity at the design operating condition to the heat equivalent of the motor input. The CFM can then
    be calculated by the formula…
    BTU/HR
    CMF = ºTD
    For example, determine the machine room ventilation for an air cooled condensing unit operating at -25°F.
    evaporator, 120°F. condensing with a net refrigeration capacity of 23,000 BTU/HR, 6,400 watts input to the
    compressor motor, and a 1 H.P. condenser fan motor.

    Compressor capacity 23,000 BTU/HR
    Heat equivalent 6400 watts x 3.413 21,843 BTU/HR
    Heat equivalent 1 H.P. fan motor 3,700 BTU/HR
    Total Heat to be Rejected 48,543 BTU/HR
    48,543 BTU/HR
    CMF = 10º TD = 4.854 CFM
    With remote condensers, approximately 10% of the heat rejected is given off by the compressor casting and the
    discharge tubing, and the ventilation can be calculated accordingly.
    For convenience, table 20A gives a quick estimate of
    the ventilation air requirement if only the compressor
    capacity is known.

    COMPRESSOR LUBRICATION
    An adequate supply of oil must be maintained in the crankcase at all times to insure continuous lubrication.
    The normal oil level should be maintained at or slightly above the center of the sight glass while operating.
    An excessive amount of oil must not be allowed in the system as it may result in slugging and possible damage
    to the compressor valves.

    Compressors leaving the factory are charged with naphthenic refrigerant oils. A complete list of acceptable
    refrigerants and lubricants are listed on form #93-11.
    The use of any other oil must be specifically cleared with the Emerson Climate Technologies, Inc. Application
    Engineering Department. The naphthenic base oil has definite advantages over paraffinic base oils because
    separation of refrigerant from paraffinic oils occurs at substantially higher temperatures with the same oilrefrigerant
    concentration.
    When this separation or two phase condition exists the oil floats on top of the refrigerant and the oil pump inlet at the bottom of the sump is fed almost pure refrigerant at start up. The resulting improper lubrication can result in bearing failure. Because
    of the lower separating temperature of naphthenic oil, the possibility of two-phasing is greatly reduced.
    Copelametic® compressors are shipped with a generous supply of oil in the crankcase.

    However the system may require more or less oil depending on the refrigerant charge and the system design.
    On field installed systems, after the system stabilizes at its normal operating conditions, it may be necessary to add or remove oil to maintain the desired level.
    OIL PRESSURE SAFETY CONTROL
    A major percentage of all compressor failures are caused by lack of proper lubrication. Improper lubrication or the
    loss of lubrication can be due to a shortage of oil in the system, logging of oil in the evaporator or suction line due
    to insufficient refrigerant velocities, shortage of refrigerant, refrigerant migration or floodback to the compressor
    crankcase, failure of the oil pump, or improper operation of the refrigerant control devices.
    Regardless of the initial source of the difficulty, the great majority of compressor failures due to loss of lubrication
    could have been prevented. Although proper system design, good preventive maintenance, and operation
    within the system’s design limitations are the only cure for most of these problems, actual compressor damage
    usually can be averted by the use of an oil pressure safety control.
    An oil pressure safety control with a time delay of 120 seconds is a mandatory requirement of the Emerson Climate Technologies, Inc. warranty on all Copelametic® compressors having an oil pump. "

    There you go..
    buddy

  24. #24
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    I am still none the wiser.

    Can anybody help in providing a STANDARD calculation for ventilation of Plant rooms with compressor Packs/Racks installed?

    best regards
    buddy

  25. #25
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: Compressor room ventilation requirements for compressor racks??

    Buddy hello
    what size is the compressor room?,
    Rule of thumb Machine room 20 - 30 Air changes per hour,
    Some compressor rooms are small and would not put in a fan with duty of less than 3,000M3/Hr.
    Run the fan of a thermostat.
    You say cross flow ventilation, is that where you put a plate axial fan on one wall and a large grill on the opposite wall, what is the ducting for?
    Last edited by fixit; 05-10-2011 at 09:02 AM. Reason: spelling
    FIXIT............first time every time

  26. #26
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Compressor room ventilation requirements for compressor racks??


  27. #27
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by fixit View Post
    Buddy hello
    what size is the compressor room?,
    Rule of thumb Machine room 20 - 30 Air changes per hour,
    Some compressor rooms are small and would not put in a fan with duty of less than 3,000M3/Hr.
    Run the fan of a thermostat.
    You say cross flow ventilation, is that where you put a plate axial fan on one wall and a large grill on the opposite wall, what is the ducting for?
    Hi Fixit,

    Thank you for your reply.

    The reason why I posted on RE was to hopefully get a straight answer or a calculation formula that may be considered standard vent requirements for compressor packs/racks, but it doesnt look as though it is that simple.

    Where did you get the rule of thumb measurement of 20 - 30 air changes per hour from...what is the source?

    Yes you are correct, cross flow from one end of the plant room to the other on opposite sides.

    Surely the supermarket refrigeration company,s must do this calculation nearly every day, theremust be some communication between the ventilation company, the builder/project manager and the refrigeration compressor pack installer to get the right ventilation installed on a new store?
    buddy

  28. #28
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by Emmett View Post
    Hi Emmett,

    Thanks for the link.

    I am aware of Ashrae standard 15 and also EN378 ventilation requirements for compressor rooms.
    However those ventilation standards are "safety" standards in case of refrigerant leaks and also exposure to hazardous refrigerants, Ammonia, Hydrocarbons etc etc.

    As what I am looking for is standard ventilation requirements for the compressor pack/rack say installed with 4 Bitzer or Copeland 25 Horsepower compressors in Supermarket application?

    Anybody?
    buddy

  29. #29
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by buddy View Post
    Hi Emmett,

    Thanks for the link.

    I am aware of Ashrae standard 15 and also EN378 ventilation requirements for compressor rooms.
    However those ventilation standards are "safety" standards in case of refrigerant leaks and also exposure to hazardous refrigerants, Ammonia, Hydrocarbons etc etc.

    As what I am looking for is standard ventilation requirements for the compressor pack/rack say installed with 4 Bitzer or Copeland 25 Horsepower compressors in Supermarket application?

    Anybody?
    Sorry,
    Thought that is what you were seeking. I have not got a clue what a rule of thumb would be but here is another link you may find helpfull.
    http://www.suncam.com/authors/111Bal...achineRoom.pdf

  30. #30
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by Emmett View Post
    Sorry,
    Thought that is what you were seeking. I have not got a clue what a rule of thumb would be but here is another link you may find helpfull.
    http://www.suncam.com/authors/111Bal...achineRoom.pdf
    Hi Emmett,

    Thanks again for the link.

    On the document it says "2009 International code"

    What code does this refer to, do you know?
    buddy

  31. #31
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Compressor room ventilation requirements for compressor racks??

    It is a code which has been adopted in nearly all of the United States.
    http://en.wikipedia.org/wiki/Interna..._Building_Code

  32. #32
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Compressor room ventilation requirements for compressor racks??

    I have given you the method of calculation, I do mind checking your results, but giving you the answer does not help you learn.
    Break down each section showing your calculation method.

  33. #33
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by mad fridgie View Post
    I have given you the method of calculation, I do mind checking your results, but giving you the answer does not help you learn.
    Break down each section showing your calculation method.
    Dear mad fridgie,

    You are right of coarse so apologies for ignoring your previous post but it is so confusing with which method/formula do you calculate with as there seems to be so many out there and no set standard?

    For my knowledge I shall try to work out the calculation on a separate post and kindly request your assistance as this will be my first attempt at this type of calculation.

    This is exactly why I love RE, its such a great source of knowledge.

    best regards
    buddy

  34. #34
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by Emmett View Post
    It is a code which has been adopted in nearly all of the United States.
    http://en.wikipedia.org/wiki/Interna..._Building_Code
    Hi Emmett,

    Thank you for the information on the International building Code.

    One question?

    Where did you get the form from that you posted?

    best regards
    buddy

  35. #35
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by mad fridgie View Post
    You have 2 issues to look at
    First the compressors are they suction cooled or air cooled, "does the compressor need air flowing over them to keep them cool" This is specific to the compressor make and model. ( not the same as your ventilation) are tech detail will be available. ( Purpose built fans to do the job)

    Depending upon the application ( HT or LT) and operating conditions you can get up to 30% of the electrical input to the compressors reject directly from the compressor so 100Kw rack, say COP of 2, electrical input of 50kw, so compressor heat lost 15Kw, then you consider high losses (oil sep and discharge pipes) very specific, lets 5Kw. are then any other gains, electrical switch boards, VSDs, solar gains, hot water tanks. (assume some) another 5Kw. So total 25Kw.
    Outside air temp 25 C leaving 30C load 25kw, air flow = 4200l/s (will kill it)
    Dear mad fridgie,

    I have more information that may help me understand the calculation method (in blue font below).


    Previous post –

    You have 2 issues to look at
    1) First the compressors are they suction cooled or air cooled = Suction gas cooled operating on R22 refrigerant.
    2) "does the compressor need air flowing over them to keep them cool" = Yes (have posted Bitzer and Copeland calculation method).

    This is specific to the compressor make and model. ( not the same as your ventilation) are tech detail will be available. ( Purpose built fans to do the job)

    3) Depending upon the application ( HT or LT) = Have 2 compressor racks, 1 x LT and 1 x MT.
    LT evaporating temp -35 Centigrade, MT evaporating at -15 Centigrade, Condensing both at +45 Centigrade

    This where you lose me -
    “ and operating conditions you can get up to 30% of the electrical input to the compressors reject directly from the compressor
    For my knowledge where is this information from?

    so 100Kw rack, say COP of 2, electrical input of 50kw, so compressor heat lost 15Kw, then you consider high losses (oil sep and discharge pipes) very specific, lets 5Kw.

    For my knowledge where is this information from?

    are then any other gains, electrical switch boards, VSDs, solar gains, hot water tanks. (assume some, no hot water tanks) another 5Kw. So total 25Kw.
    Outside air temp 25 C leaving 30C

    Outside air temp based on 40 C leaving 45 C

    load 25kw, air flow = 4200l/s (will kill it)

    For my knowledge how do you come to this result?

    Best regards
    buddy

  36. #36
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Sorry Chaps,

    I noticed I hadnt posted the Bitzer vent calculation....please see note below -

    "If 4 x compressors, then if it is MT, you use 10% of condensing capacity
    ( this you need to calculate from our software),

    Can you at least tell this is 4 cylinders or 6 cylinders compressors?

    If it is 4 cylinder, 4H-25.2, estimate heat is 16.2kW, base on 10% of condensing capacity
    (40.5kw x 4 = 162kW)"

    best regards
    buddy

  37. #37
    Join Date
    Nov 2011
    Location
    US
    Age
    52
    Posts
    1
    Rep Power
    0

    Re: Compressor room ventilation requirements for compressor racks??

    buddy,
    Search for "Tyler System Installation Manual", it shows Machine Room Ventilation Requirements of 100 CFM / HP
    for compressor rack system with remote air-cooled condenser (page 1-1).

    Search for "Kysor Warren - Installation & Operation Manual", it shows "40 to 100 CFM per compressor horsepower depending on the ambient temperature" (page 29).

    Search for 6.2.5.5.2 Minimum Ventilation in Canada B52, it shows "Whenever the refrigeration system is operating or whenever the room is occupied, a sufficient part of the
    mechanical ventilation shall be operated to provide normal volumes equal to the greater of the following:
    (a) 2.54 L/s/m2 (0.5 cfm/ft2) of machinery room area; or
    (b) the volume required to prevent a maximum temperature rise above ambient greater than 10 ºC
    (18ºF), based on all of the heat-producing machinery in the room".

    For a rule of thumb, i would use 60 - 80 CFM / compressor HP.

  38. #38
    Join Date
    Jan 2004
    Location
    England
    Posts
    136
    Rep Power
    21

    Re: Compressor room ventilation requirements for compressor racks??

    Quote Originally Posted by tl1972 View Post
    buddy,
    Search for "Tyler System Installation Manual", it shows Machine Room Ventilation Requirements of 100 CFM / HP
    for compressor rack system with remote air-cooled condenser (page 1-1).

    Search for "Kysor Warren - Installation & Operation Manual", it shows "40 to 100 CFM per compressor horsepower depending on the ambient temperature" (page 29).

    Search for 6.2.5.5.2 Minimum Ventilation in Canada B52, it shows "Whenever the refrigeration system is operating or whenever the room is occupied, a sufficient part of the
    mechanical ventilation shall be operated to provide normal volumes equal to the greater of the following:
    (a) 2.54 L/s/m2 (0.5 cfm/ft2) of machinery room area; or
    (b) the volume required to prevent a maximum temperature rise above ambient greater than 10 ºC
    (18ºF), based on all of the heat-producing machinery in the room".

    For a rule of thumb, i would use 60 - 80 CFM / compressor HP.
    Hi tl1972,

    Lots of information there.

    Thank you very much.

    best regards
    buddy