    Mitsubishi over door heater



    Hi all
    Was wondering if you could point me in the right direction. I have been working on a vrf system with 6 normal indoor Ac units and one thermoscreens door heater. All units have a par27 remote except the door Heater which has a par21. I have addressed and ran up all units and are all working correctly accept the door heater. This runs in cool/heat mode with good air offs then cuts out with error 6607. I have checked the mnet and am happy it's all ok. I know it's addressed correctly as it's seems on te centralised controller and can run for short period.


    Any ideas?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi over door heater

    any loose connections on the power 240v to the heater or in the isolator. test u have 30vdc on the mnet,have u checked the address on the par21.
    disconnect the local controller and test operation on the g50/central controller

  3. #3
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Mitsubishi over door heater

    I have Done the following with no success. It's addressed as unit 02 wasn't sure if it is the par21 causing the problem.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi over door heater

    ive checked mitsi website and theres only dimensinal drawings for the thermoscreen no installation/service info

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Mitsubishi over door heater

    Thermatech is you're man for this..

  6. #6
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Mitsubishi over door heater

    It's a weird one. Got mnet voltage in and out. Power in the right places etc.. Just runs and goes out. I'm not to familiar with Mitsi but it's addressed 02 on system. 01 works fine and so do the units after it. The only thing I did pick up on was that when first turning the door heater on he controller was locked under centralised control. For which I'm not sure why? No unlocked and works for short time before going out on 6607 error.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi over door heater

    does the par21 need addressing? i'll send u a manual for the par21

  8. #8
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi over door heater

    With the thermoscreen being address no.2 and connected to a par 21 has someone programmed the central controller to tell it unit address 002 is connected to controller 102 which does not exist ,so it drops out on 6607 (no ack) as it can't find controller 102.
    Check the central controller to make sure IC 002 has no controller address assigned
    I may be wrong but should a par 21 be connected to the M-Net at all ,some thing is telling me it should be on the 12v circuit.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi over door heater

    par 21 is a ma controller so connects on tb15 not the m net and doesnt need addressing
    M-NET Address settings

    (1) Address settings table

    The need for address settings and the range of address setting depend on the configuration of the system.

    *1. Address setting is not required for a City Multi system that consists of a single refrigerant circuit (with some exceptions).

    *2. To set the ME remote controller address to "200", set the rotary switches to "00".

    *3. To set the outdoor unit address to "100," set the rotary switches to "50."

    *4. Some indoor units have 2 or 3 controller boards that require address settings.

    No. 2 controller board address must be equal to the sum of the No. 1 controller board address and 1, and the No.3

    controller board address must equal to the No. 1 controller address and 2.

    *5. The outdoor units in the same refrigerant circuit are automatically designated as OC, OS1, and OS2 in the order of

    capacity from large to small (if two or more units have the same capacity, in the order of address from small to large).

    Unit or controller Address setting

    range

    Setting method Factory

    setting

    CITY MULTI indoor

    unit

    Main/sub unit 00,

    01 to 50

    *1

    Assign the smallest address to the main indoor unit in the

    group, and assign sequential address numbers to the rest

    of the indoor units in the same group.

    *4

    00

    M-NET adapter

    M-NET control interface

    Free Plan adapter

    LOSSNAY, OA processing unit

    Air handling kit

    00,

    01 to 50

    *1

    Assign an arbitrary but unique address to each of

    these units after assigning an address to all indoor

    units.

    00

    ME remote controller

    Main remote

    controller

    101 to 150 Add 100 to the smallest address of all the indoor units

    in the same group.

    101

    Sub remote

    controller

    151 to 200

    *2 Add 150 to the smallest address of all the indoor units

    in the same group.

    MA remote controller No address settings required. (The main/sub setting must be made if 2

    remote controllers are connected to the system.)

    Main

  10. #10
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi over door heater

    I found this but you probably have it all ready.
    It's all a bit involved for an air curtain if you ask me
    http://www.thermoscreens.com/en/down...035-2%20UK.pdf (taken from thermoscreens website)
    Cheers
    Stu
    Last edited by stufus; 11-09-2011 at 12:31 PM. Reason: Nod to info owner (just in case);-)
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  11. #11
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Mitsubishi over door heater

    Hey Weidit
    Did you figure this one out????
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  12. #12
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi over door heater

    ME and MA remote controller should not be used together in a system without system controller or centralized controller.
    Weidit, any system controller in your system?