    Daikin VRV II retrofitting water heat recovery and solar



    chaps

    A client who has a 2x REYQ 26 M8(10+16) stamped 2006 wants to retrofit with solar and hot water heat recovery.

    current capacity

    indoor 84kw
    outdoor 71kw

    Are there any Daikin bod's here who know if this can be done or not?

    TIA

    Richard
    ( I am assuming it's VRVII BTW :-)
    units are 2 x REYQ16M8W1B + 10
    Last edited by r.bartlett; 10-09-2011 at 03:18 PM.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV II retrofitting water heat recovery and solar

    is it wII watercooled condensers,if so with the heat recovery are u intending to heat a dhw cylinder?

  3. #3
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Good After RB

    have you rtfm spoken to a Daikin dealer & we do not want to helping those not competent, as they may hurt themselves, so are you & have you got your f-gas

    Sorry mate ....... you left yourself wide open to them few

    I will remember to duck when passing through your way next,

    R's chillerman
    If the World did not Suck, We would all fall off !

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by chillerman2006 View Post
    Good After RB

    have you rtfm spoken to a Daikin dealer & we do not want to helping those not competent, as they may hurt themselves, so are you & have you got your f-gas

    Sorry mate ....... you left yourself wide open to them few

    I will remember to duck when passing through your way next,

    R's chillerman

    Sadly DUk do not open on the weekends so that's a problem hence why I came here. For our F-Gas certificate please see our website

    http://www.ambientcontrol.co.uk/pdfs...fullstatus.pdf

    My own is available on request. As regards competent then you've got me banged to rights!
    Last edited by r.bartlett; 10-09-2011 at 04:00 PM.

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by install monkey View Post
    is it wII watercooled condensers,if so with the heat recovery are u intending to heat a dhw cylinder?
    No std VRV air condensers... The client has all sorts of idea's most are valid and interesting but we're on a real tight frame. Job is due to start 17th and he bombarded me with all sorts of requests. First time I met him though and a decent knowlegable chap so we are investigating options..

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by r.bartlett View Post
    Sadly DUk do not open on the weekends so that's a problem hence why I came here. For our F-Gas certificate please see our website

    http://www.ambientcontrol.co.uk/pdfs...fullstatus.pdf

    My own is available on request. As regards competent then you've got me banged to rights!
    Well that was good justification, on its own
    My a/c let alone vrv knowledge can be written on back of stamp, not much help to you there, mate

    But will keep thread alive during the night, so our friends over the ponds see it aswell

    Maybe its about time all Manufacturers provided 24/7 support ... which could be implemented here ... it would not just provide the support when needed but also, would stand them in good light fo sales ... and of course up site attendance/membership & in turn site adverts/revenue ...... yeah ok 'Install' before you tell me again today 'Isa creep' !

    R's chillerman
    If the World did not Suck, We would all fall off !

  7. #7
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by chillerman2006 View Post
    Well that was good justification, on its own
    My a/c let alone vrv knowledge can be written on back of stamp, not much help to you there, mate

    But will keep thread alive during the night, so our friends over the ponds see it aswell

    Maybe its about time all Manufacturers provided 24/7 support ... which could be implemented here ... it would not just provide the support when needed but also, would stand them in good light fo sales ... and of course up site attendance/membership & in turn site adverts/revenue ...... yeah ok 'Install' before you tell me again today 'Isa creep' !

    R's chillerman
    Toshiba provide the best tech support in the UK and is 24/7 direct to an engineer. The others should take note instead of scrimping on their call centre

  8. #8
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Richard

    Where in the process does he want to add the solar, does the existing VRV provide water heating?

    Are you looking at adding an Altherma set up or similar?

    Just curious as to where the vrv comes in (other than hacking the discharge through a plate heat exchanger?)

    Other wise it's a question of DHW tank selection etc

    Alec
    Mostly found in the southern part of this green and pleasant land.

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by al View Post
    Richard

    Where in the process does he want to add the solar, does the existing VRV provide water heating?

    Are you looking at adding an Altherma set up or similar?

    Just curious as to where the vrv comes in (other than hacking the discharge through a plate heat exchanger?)

    Other wise it's a question of DHW tank selection etc

    Alec
    Daikin VRV can incorporate heat recovery into water as part of the system.
    http://www.daikin.co.uk/heat-recover...ry/default.jsp

    I worry that in winter there will be little heat left to heat water but my client suggest it will switch over to the imersion heater for those few days..

    i believe it's only available for VRV III but need this confirmed

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Can u not persuade him into photovoltaic solar panels,as the downtime of the vrv,s being hacked repiped etc is going to affect the staff.and more energy efficient lighting?

  11. #11
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Richard

    Going on the capacities you give, the outdoor is already undersized compared to the indoors (71inside to 84kw out), would adding heat recovery not put you under extreme pressure if we have a winter repeating like last year? Although a smart ambient control could solve this, ie switch off heat recovery when ambient is below zero or so?

    Good suggestions from IM there too.

    alec
    Mostly found in the southern part of this green and pleasant land.

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Diversity of 130% is normal for a vrv,as generally not all the indoors have 100% demand. I personally don't think it's worth mauling with some kit that's 5yr old,also in winter when ur in full heating mode ur not gonna be able to generate any heat reclaim,the money ur customer is saving by not mauling with the kit would enable him to spend on more panels,maybe an altherma system to heat his water or solar for hot water generation.collecting rain water for toilet flushing,biomass boilers for waste incineration,mixers on taps,pirs on lighting,skylight domes for free lighting.inverter drives on ventilation fans,pumps-look at me mr Eco monkey!!!!

  13. #13
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by install monkey View Post
    Can u not persuade him into photovoltaic solar panels,as the downtime of the vrv,s being hacked repiped etc is going to affect the staff.and more energy efficient lighting?

    Ironically he has pencilled offf 70% of the flat roof for PV. I'm no fan of them but he is and that is what counts!

    Let's nail this one :
    The VRV won't be hacked or ripped as it's only going to be fitted if it can be normally incorporated into the system .Which can be done to VRV depending upon certain criteria which i am trying to find out
    Last edited by r.bartlett; 10-09-2011 at 07:01 PM.

  14. #14
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin VRV II retrofitting water heat recovery and solar

    That would be my worry too mr eco monkey!! A system already under pressure being asked to heat water too could be asking for trouble.

    alec
    Mostly found in the southern part of this green and pleasant land.

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by r.bartlett View Post
    Ironically he has pencilled offf 70% of the flat roof for PV.
    RB

    If you are going to be involved in this side of it mate, MikeHolm is the man for pv.
    http://www.refrigeration-engineer.co...52492-MikeHolm

    worth dropping him a line, quite often about around now

    R's chillerman
    If the World did not Suck, We would all fall off !

  16. #16
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by r.bartlett View Post
    Toshiba provide the best tech support in the UK and is 24/7 direct to an engineer. The others should take note instead of scrimping on their call centre
    Well that should help Toshiba sales,

    Just got back online, have you's worked out if this equipment can do the job ?

    Has Mr holm put in an appearance & seen this or did you pm him

    R's chillerman
    If the World did not Suck, We would all fall off !

  17. #17
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by chillerman2006 View Post
    RB

    If you are going to be involved in this side of it mate, MikeHolm is the man for pv.
    http://www.refrigeration-engineer.co...52492-MikeHolm

    worth dropping him a line, quite often about around now

    R's chillerman
    The whole building is being done but in stages. PV is something like stage 15 and we haven't started yet

  18. #18
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by al View Post
    That would be my worry too mr eco monkey!! A system already under pressure being asked to heat water too could be asking for trouble.

    alec
    We suspected it would be over indexed so he has already suggested swapping the 10's for another 16 to make it 2 x 32. Then we would use the two 10's on another part of the building. Most of these idea's won't get the go-ahead but he wants all the alternatives before he green lights the way he wants to go forward

    Personally I would prefer he sticks with the current set up and leaves the water side till the next floor is done.

  19. #19
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV II retrofitting water heat recovery and solar

    best to get a daikin rep to site to survey and do the donkey work to ensure any plans are viable then youve covered ur butt if there is any performance issues

  20. #20
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Quote Originally Posted by install monkey View Post
    best to get a daikin rep to site to survey and do the donkey work to ensure any plans are viable then youve covered ur butt if there is any performance issues
    I have already emailed DUK but as you probably know they work at their own pace..

  21. #21
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV II retrofitting water heat recovery and solar

    mention that the customer has had mitsi knocking at his door, ring neil foley or the fqs team

  22. #22
    c4ble's Avatar
    c4ble Guest

    Re: Daikin VRV II retrofitting water heat recovery and solar

    Are you looking for this types?