08-09-2011, 10:51 AM #1
Climaveneta CVM 3000 Nascosto Keys
Can someone help with the CVM 3000 Hidden keys for accessing user and Factory Menus. Thank You.
08-09-2011, 02:12 PM #2
Re: Climaveneta CVM 3000 Nascosto Keys
Hi Jomi69
I shall email you the manual
R's CMIf the World did not Suck, We would all fall off !
08-09-2011, 02:18 PM #3
Hi Jomi69
manual sent....but please be careful not to adjust anything that does not need to be
the only thing you should need this access for is to calibrate sensors & transducers
16-01-2012, 10:07 PM #4
Hi Chillerman 2006
I have a manual that tells you details of sensor calibration and so on but it does not give you details of where the hidden keys are and says you should contact climaveneta. I would really appreciate these details if you could email me at tm.edwardmccarthy@gmail.com
Thanks in advance
17-01-2012, 12:20 AM #5
Hi teddymac
its to the left of the screen, just run your fingers over pushing slightly to find it... you then press the hidden key and ice together
chillermanIf the World did not Suck, We would all fall off !
18-01-2012, 03:31 PM #6
Hi Teddymac,
I hope you aren't referring to the procedure identified in the manual as a "Self-Calibration" ......
This will work only connecting a small box called "Self Calibration Kit" to two specific analog inputs of main board.
If you are trying the procedure withouth the "Self Calibration Kit" the final result could be a disaster!
Regards.
18-01-2012, 04:42 PM #7
Hi teddymac
mail me i will send you the manual with directions .
GOOD LUCK
22-01-2012, 09:02 PM #8
Hi Goshen what is your email address ? Mine is tm.edwardmccarthy@gmail.com if you could mail me manual and directions that would be great.
25-01-2012, 04:51 AM #9
did you get it ?
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!