    Vrv Refrigerant metering in heating mode



    On a vrv system on heating mode is refrigerant metered at the indoor unit? And
    The high pressure liquid line is now a low pressure/low temperature line. Or is the metering device at the indoor bypassed and metered at the outdoor coil and the liquid line is always a high pressure liquid line. Just came to mind when i had trouble insulating some pipe confined to a tight space and wondering if it was
    Necessary to be insulated? Cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Vrv Refrigerant metering in heating mode

    Daikin vrv install manual states insulate both lines or all 3 if heat recovery,preferably with 13mm wall armaflex