Results 1 to 9 of 9
Thread: trane rtad108
05-09-2011, 11:38 PM #1
trane rtad108
evening guru's a customer wants his r22 chiller decomissioning due to the site is being vacated .currently it has 30kg r22r in since a recent repair to a fractured 1/4 line. the customer may want this chiller reinstating in a few years, what r22 replacement do trane recommend? is isceon 59 ok and will i need an oil change/flushing/new driers and oil filter??
please advise ta
06-09-2011, 10:19 PM #2
Re: trane rtad108
hello!! 23hrs and not 1 reply!! i do have my 2079!!
06-09-2011, 10:34 PM #3
Re: trane rtad108
Hi Mr 2079,
do you have to pull the charge from it .... no (can be craned off site still)
pull the fuses in the panel give to customer for safe keeping (he will loose them ! So you can charge when recommisioned for new) You can buy lock-out kit for chillers isolator & lock it out, fill in your details, include contact details,
Trip supply breakers at distribution board, Tape up & mark do not run/electrical fault Isolation required
Job done mate
R's chillermanIf the World did not Suck, We would all fall off !
06-09-2011, 10:44 PM #4
Re: trane rtad108
hello cm -are you qualified in giving me relevent information?? do you have a gold blue peter badge or your 200mtr swimming or any other achievment? the chiller in question has had leaks on the oil cooler section of the condenser,bellows on the oil pressure switch, 1/4 line to pressure switch to start up the fans, so customer wants it degassing,i recommended adding a sniff of nitro to 3psi to keep everything sweet.
the college may reopen in 12mths time or 5yr time.
air cooled condenser,discharging within a plantroom with a louvred wall 2mtr away!! used to trip out on hp in summer,customer eventually had discharge air ducted to outside,theres loads of lil defects on this ,ill take photos of it tomoz and e mail u.obviously i will be locking off the isolator labelling the system of work done,ammending the
F GAS sheet and draining the evap, buffer tank,fan coils etc,got a busy week!!
06-09-2011, 10:49 PM #5
Re: trane rtad108
you said you repaired it .... dodgy trader .... tell him to call an engineer
& reason behind leaving charge in it was so as per f-gas, you can charge to do regular checks on it still
there was no mention its low - scrap it or go R422d then !
Your interupting my 'shameless' with all these questions you should know
Stop pulling my plonker ! or I will inform RB you bought that 2079If the World did not Suck, We would all fall off !
06-09-2011, 10:57 PM #6
Re: trane rtad108
i did this is over a 7 yr period and there is 2 chillers on site, 1 currently has dropped its gas- again leak on oil cooler sectiond=s of the cond but when u see how many startups compared to run hrs!!! its a croc of ****e,1 chiller was dropped on installation, 1 inch flow switches in a 1 inch pocket so the paddle catches on the sides, no balance valve to evenly distribute flow rates through evaps,undersized circ pumps.
06-09-2011, 11:06 PM #7
Re: trane rtad108
Well do as discussed & fill out full dilapidation on units & water circuits .... so they know what to expect when/if they ask for recomissioning, that way they will not think your having them over ... thats then your chance to do it right
If I find numerous faults on site like that .... I list them all on every visit, if they have money for repairs or not they still need regular highlighting .... so when the one working system falls over you have paper trail to say - you have told them all along
but again your still pulling me plonker if you all ready know this
is there anything you DO need answering ?If the World did not Suck, We would all fall off !
06-09-2011, 11:08 PM #8
Re: trane rtad108
how can this thread go off topic??
06-09-2011, 11:25 PM #9
Re: trane rtad108
It can't it's your thread your topics
speaking of which can we add some pictures now, something a bit more interesting than RTAD though ?
can we Mesiah --- a bit of fluff http://www.youtube.com/watch?v=NquFVO44lvg
R's chillermanLast edited by chillerman2006; 06-09-2011 at 11:29 PM.