Results 1 to 5 of 5
Thread: condensor screws
-
31-08-2011, 08:18 PM #1
condensor screws
Hello everybody,
We have to make: a central with two srew compressors 134A.
The condensors stay about 6 m lower than the compressors.
Would be that a problem? Is it better to put the receiver as well down together with the condensors?
And the condensor for the olicooler, we have to put this too down, would be that a problem?
Thanks ahead,
Greetings
Nando
-
01-09-2011, 05:36 PM #2
Re: condensor screws
Dear Nando...
This will not be a big problem .
Regards
-
02-09-2011, 09:24 AM #3
Re: condensor screws
Hi Nando, generally the receiver needs to be below the condenser, so the liquid can drain out of the condenser into the receiver. Normal air cooled oil cooler 6m down should be ok.
-
02-09-2011, 06:31 PM #4
Re: condensor screws
thank you all
greetings
-
05-09-2011, 06:09 PM #5
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: condensor screws
main thinks in screw compressor are oil separator and oil cooler, they should be close to compressor as far as we can.
receiver should be lower than condenser