    killing our scrolls? help



    i really need help with a 4 year old modular chiller set up that has killed 4 out of 8 scroll compressors. r-22 . air cooled condenser and chiller not from same company. high side runs 350 to 380 psi while low side is mid to low 50's psi. 375psi vapor into condenser 345psi leaving condenser going into an 80lb receiver . any ideas.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: killing our scrolls? help

    how long is the delay from stopping to starting,should be at least 3mins to allow for pressures to equalise.-is it a mercury climatic? by any chance?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: killing our scrolls? help

    High side pressures seem overly high, what is the ambient temperature?

    What is the state of the condenser?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Simply your head pressure is to high, and is a good chance is outside the operating range of the compressor. I bet the discharge line is glowing red (joke) but is very hot.
    Why is it so high, what is your air "on" temp to the cond, what are cooling.
    Making a guess, i would say that your system has air in it.

  5. #5
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: killing our scrolls? help

    as the other guys have said yr head way to high for a scroll to handle on 22 they will run but fail very quick check for non condensables and get yr failed units replaced so it can handle the load check the rotation of the comps if they going wrong way they sound like a bag of spanners and dont work very well then overheat best way to see if you had phase rotation see if yr condenser fans running the correct way an check yr oil levels that buggers them up as well good luck with that one

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: killing our scrolls? help

    Other faults that may give the symptoms you have.
    Overcharged?
    Chocked liquid Strainer?
    Moisture in the system?
    Given the issues you mention.
    I would reclaim the refrigerant and recharge with fresh or at least . Do a pressure temp comparison to confirm you have R22 in the system and that it is not contaminated.
    Grizzly

  7. #7
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    it does have 3min delay timer.

  8. #8
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    rotation is correct. we have made shure there is no non-condensables, by starting over on one of them ,pulling a good long vaccume on system all over (each side of check valves) .not shure about chocked liquid strainer? we have put in new filter dryer just before expantion valve.outside temp under 100f

  9. #9
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: killing our scrolls? help

    another thing to check if system cycling down ok ,ht scrolls throw out alot(all) of oil as they approach vacuum

  10. #10
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    yes we have had that problem with short on and off times when cold out and oil leaving compressor. but we are not going to run them under 40 degrees anymore and we also have better control of condenser fans. we also have a very low delta-t at about 4 degrees f. im told it needs to be around 10 . so does that mean refridgeration valve is staying almost closed making low pressure? rember also i have 30# pressure drop on high side through condenser.

  11. #11
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: killing our scrolls? help

    Do they pump down when they stop? If yes, do not let them go below 20psi.

    The pressure should not change through the condenser. Sounds like it is partially clogged.

    Are there NRV's on each discharge?

    Check expansion device, high head pressure can indicate problems with it at times.

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: killing our scrolls? help

    Is the high head pressure a new problem or has it always been there?
    Mostly found in Oxfordshire, UK :)

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    At 350-380psi, your saturated condensing temp (SCT) is 144-150F. SCT should be no more than 30-35F above ambient temp. In other words, if the ambient temp is 100F, the SCT should be no more than 130-135F, which translates to 296-315psi. 350-380psi is way too high.

    If it isn't a condenser airflow problem, then the system is very probably overcharged.

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Start with air flow and water flow. What is the temperature of the air entering the condenser and the air leaving the condenser? What is the temperature of the water entering the evaporator and the water leaving the evaporator?

  15. #15
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    the compressors do not pump down. there is a 24volt solinoid that opens and closes directly with compressor contactor. they are 25 ton scrolls. this modular chiller set up has never been right. i remember the start up guys from each company (one with the chiller and the other with the condenser) fighting during start up. one was saying he did not like the pressures at all ,he said it looks like you have non condensables.
    since then we have had two different factory reps and several different chiller guys here and try to get set up right. obviously from most of the response iv been getting 350-380 psi is too much for a scroll. i agree. i will get more temp readings across condenser. entering water is 46deg f and leaving is 42degf thanks for the help i really hope we can get to the bottom of this

  16. #16
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Measure the temp of the refrigerant leaving the cond and the temp leaving the reciever.
    Measure the liquid pressure leaving the reciever.
    One has to presume that the cond has been sized correctlly
    Are you cond fans 3 phase, check rotation of each fan, also check that all fans have the same blade and are fitted correctlly.
    If your head pressure is so high, I can not see how you would know if your cond fans set up is OK (what pressures are these set to?), unless this is set up with the wrong pressures.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Quote Originally Posted by ENERGY KNIGHT View Post
    entering water is 46deg f and leaving is 42degf
    On the evaporator, the water should enter the bottom and exit the top. The refrigerant should enter the top and exit the bottom.

    At 4F, the delta-T is low. It should be about 10F. Either the evap outlet superheat is too high or there is too much water flow.

    I'm thinking there is a combination of several problems... and we need to track them down one at a time.

  18. #18
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Quote Originally Posted by Gary View Post
    On the evaporator, the water should enter the bottom and exit the top. The refrigerant should enter the top and exit the bottom.

    At 4F, the delta-T is low. It should be about 10F. Either the evap outlet superheat is too high or there is too much water flow.

    I'm thinking there is a combination of several problems... and we need to track them down one at a time.
    Nett refrigeration effect will be low due to high discharge pressures

  19. #19
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Given the low side pressure, excessive water flow is unlikely. Once the high side pressure is reduced (probable overcharge), the low side pressure is going to drop even further. This all adds up to high evap outlet superheat, which points to liquid restriction. Given the fact that it was like this new, I would suspect undersized TXV orifice and/or undersized liquid line, drier, etc... but we need more information to confirm all of this.
    Last edited by Gary; 29-06-2011 at 12:19 AM.

  20. #20
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Reading between the lines, the OP said that there had been a few engineers on site and from different companies, It would suprise me that at least one of the engineers would have picked up the basic problem. Could it be that the cond has just been incorrectly sized, and someone/company is just trying to protect their arse

  21. #21
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Quote Originally Posted by mad fridgie View Post
    Reading between the lines, the OP said that there had been a few engineers on site and from different companies, It would suprise me that at least one of the engineers would have picked up the basic problem. Could it be that the cond has just been incorrectly sized, and someone/company is just trying to protect their arse
    If the condenser were undersized, the suction pressure would be high. If the condenser were oversized, the head pressure would be low. But then... who knows what they might have done to cover their tracks?

  22. #22
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    If the cond was undersized and 100% cond was not achieved (vapour and liquid in the liquid line), then you would have lower suction, due to the a reduced mass flow through the expansion device, you normally see high superheat, but on rare occassions you do not because of the increased pressure drop through the evap, where little heat transfer occurs at the beginning of the evap.
    Last edited by mad fridgie; 29-06-2011 at 01:13 AM.

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: killing our scrolls? help

    What is compressor make and model?
    What is chiller make and model?
    What is condenser make and model?
    Last edited by nike123; 29-06-2011 at 10:41 AM.

  24. #24
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    the part i just read about vapor and liquid in the liquid line is what is hapening. the sight glass just before the expantion valve is full of bubbles. i mean FULL of bubbles! i heard that in some systems a little bit of bubbles is ok but im shure not like we have. story goes like this when start up was done they filled system until sight glass was clear. when it stared to get hot outside the discharge elbows right off the compressors started breaking so they sent up a different person and he took out enought r-22 from a full unit to re-fill one that lost charge from broke elbow. Im told original charge was 100# of r-22. these chillers have an 80# receiver just before the expansion valve. right now the one we are working on has a new compressor and 50# of r-22 it was arround 70deg outside and i set fans to 30hertz and the pressere just off compressor was 275 and the same 275psi right before going into condenser. just leaving condensor we had 220psi the low side just before going into compressor was maby 50psi . about this condenser i have looked at other ones and they all have two big long tubes on the end that the small tubes conect too and the incoming vapor hooks too one and the leaving liquid hooks to the other one. our condenser has the two big tubes and one realy short one at bottom the vapor hooks to one big tube and the leaving liquid hooks to that short tube not the other gig tube . im not shure what that is i read somewhere about a sbcooling circuit? if that is what it is is it piped corectly? we only have two pipes coming from chiller to condenser.

  25. #25
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Good info,
    It sounds like your reciever is piped incorrectly, it sounds like your reciever is piped for a free draining cond, and not a cond with a dedicated sub cooling circuit.
    Possible fix. (change from flow reciever to surge reciever)
    The liquid drain from the cond, needs to feed the liquid line directly. (an not to the reciever inlet) The liquid line is still connected to the reciever outlet and open. The reciever inlet is not in use (blanked off).
    Your fan speed is still to low (head pressure still to high), at 70F ambient you should be looking at pressure of around 200 psi.
    This does depend upon on your expansion device and your compressor capacity control method.
    You also need to look at your control loop for the fan speed control, "PID"
    Last edited by mad fridgie; 29-06-2011 at 10:49 PM.

  26. #26
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: killing our scrolls? help

    I have read about condensers eing piped wrong, the only way the would have liquid exiting them was if they had filled right up with liquid.

    If i was you i would stand by the chiller and imagine i was some refrigerant and follow the path i would take all round the system as if the system was running, noting what state i would be in in various parts of the system as i went, and see if i could make that journey (path not blocked or restricted) and be in the right state at the right time (superheated vapour, saturated vapour, saturated liquid, subcooled liquid, saturated liquid, saturated vapour, superheated vapour, etc) take temperature and pressure readings if needed and see if this shows up anything.

    Jon
    Mostly found in Oxfordshire, UK :)

  27. #27
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    sorry you lost me on the flow reciever vs surge receiver. it shure looks like there is a ton of knowledge out there i will get any information you guys need to figure this out its probly simple to someone if i can just get them the info they need please help and thanks to all for getting involved.

  28. #28
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Did you get the condenser air in and air out temperatures, yet?

  29. #29
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    sorry not yet i will get that tomorrow anything else that might be helpful it is suposed to be in the upper 90s here tomorrow

  30. #30
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    A normal reciever all the refrigerant flows through the reciever, a surge reciever is like an expansion tank on a water system, The main flow effectively by-passes the reciever, when things change as they do, the level of the refrigerant in the reciever goes up and down.
    Your problem is more than likely to be simple, but somes times you "can not see the wood for the trees"
    Do you know another engineer who has NOT worked on the plant, if so I would bring him in for a quick look. Some fresh eyes and thinking

  31. #31
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Draw a picture of the system and indicate all working pressures and temps, also note the load if possible and the number of compressors running along with speed of the cond fan

  32. #32
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    can you explain a little more on the reciever im still trying to understand how that works sounds interesting im just a little slow.

  33. #33
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    keeping it simple, a normal reciever ALL the flow for arguments sake enters the top and leaves the bottom. OK so far?

  34. #34
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    ok i understand that

  35. #35
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Now lets remove the reciever completely, liquid form cond goes straight to TEV and evap. (very common and often called a critical charge system) In your case the liquid/vapour mix leave the cond and enter the sub cooling circuit.
    At this stage any supercooled vapour and liquid should get sub cooled further, and you should have basically a clear sight glass at the TEV. OK so far?

  36. #36
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    ok im with you so far

  37. #37
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    So the above is great good condensing and proper sub cooling, but what if the system has massive changes (load, mass flow ambient) The density of the refrigerant would change and where its location would change with in the system, agree? OK

  38. #38
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    ok i think im with ya

  39. #39
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    So we do not want to flood the condensor with refrigerant (drives up head pressure) and we still proper subcooling.
    So we need to be able to store some refrigerant to allow for the changes in a system. (simple again) If I inserted a "T" in the liquid line with a pipe raising up and blanked at the top. When I charged the system I would fill until this pipe was half full. When TEV closes the pipe will fill and when the TEV opens the pipe will empty (this happens before chages occur in the cond/sub cooler). Only the changes moves through the pipe, not all the refrigerant. OK

  40. #40
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    If we change this pipe into a vessel, we have greater room for change "surge reciever"
    It is the dedicated sub cooling circuit which determines this method or a subcooler can be used after a standard reciever, but before the TEV

  41. #41
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    It might be very helpful to know the surface temperatures at various points along the liquid line, from the condenser outlet to the TXV inlet, particularly the entering and leaving temperature of each component in that line.

    If this is in fact a subcooling circuit, then the receiver is not needed at all, and could simply be eliminated.

  42. #42
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Quote Originally Posted by Gary View Post
    It might be very helpful to know the surface temperatures at various points along the liquid line, from the condenser outlet to the TXV inlet, particularly the entering and leaving temperature of each component in that line.

    Pressure at each measuring point would also be nice (MF)

    If this is in fact a subcooling circuit, then the receiver is not needed at all, and could simply be eliminated.
    Yes and no, by having a surge reciever you do remove some of the critical charge requirements

  43. #43
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    ok im listening but dont get it why is my sight glass so full of vapor.

  44. #44
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Quote Originally Posted by mad fridgie View Post
    Yes and no, by having a surge reciever you do remove some of the critical charge requirements
    As does the subcooler circuit.

  45. #45
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    Quote Originally Posted by Gary View Post
    As does the subcooler circuit.
    Maybe, maybe not, it is all system specific.

  46. #46
    Join Date
    Jun 2011
    Location
    usa
    Age
    47
    Posts
    69
    Rep Power
    13

    Re: killing our scrolls? help

    what do you guys think about all the bubbles at expantion valve

  47. #47
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Quote Originally Posted by ENERGY KNIGHT View Post
    what do you guys think about all the bubbles at expantion valve
    The flow of liquid is restricted somewhere between the condenser outlet and the point where you are seeing these bubbles. At the point of restriction, there will be a drop in pressure and a drop in temperature. We need to find that choke point.

  48. #48
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: killing our scrolls? help

    Is there a difference in elevation between the condenser and the receiver? Is the condenser higher than the receiver? Is the condenser lower than the receiver?

    Is the condenser outdoors and the receiver indoors?... or are they both outdoors?

  49. #49
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: killing our scrolls? help

    I have to agree with gary, information is required.
    You may also have more than one problem. (one masking the other)
    For example lets say the drier is partially blocked, reducing flow, so you add more refrigerant to increase the pressure, to drive more refrigerant through the restriction. As the cond becomes full of liquid, more sub cooling occurs, so less flashing would occur through the restriction and the sight glass would look clear. You still have high head pressure. The flashing in the sightglass is an affect not the cause.

  50. #50
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: killing our scrolls? help

    Quote Originally Posted by Gary View Post
    If the condenser were undersized, the suction pressure would be high. If the condenser were oversized, the head pressure would be low. But then... who knows what they might have done to cover their tracks?
    Hey Gary, something here troubles me. O.P. says he has 30 psi drop through condenser and with 345 psi leaving the condenser, would you not consider the possibility of undersized condenser or short cycling air even with 50 psi suction pressure? Taking into account that he does not have liquid to tx but liquid/ vapour mix, this would allow valve to starve enough to keep suction pressure low? I see we don't have air on/off temps yet.. Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.