Results 1 to 39 of 39
  1. #1
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    foster 2 door freezer



    today i had to change a compressor on a foster 2door upright freezer i reclaimed the gas from it weighed out nearly a kilo of 404a plate says 600grams (wonder why the compressor failed ) so i remomoved old compressor it smelled a bit but it also had the bright green dye in to find leaks what i struggle to understand is with a system that small why add it if you cant find a leak on a system that small its time to become a plumber full time lol fitted new comp changed drier brazed in shrader valve on condenser out let i fitted a flare drier so i could purge nitrogen through capillary for 10mins at about 5psi to make sure it clear of any blockages pressure tested it to 20bar fitted vac pump got 6 torr in 20 min was well impressed 2torr in 45min have worked on all the other units in this kitchen and have had to do triple evac on all of them at least once after changing evaps or capillary or both previous contractor just went along and added gas moisture probs i have had on other cabs are unbelieveable this compressor change went brilliantly and i only put in 600grams of 404a and it came down to temp in an hr amazing you dont have to over charge unit if you do everything by the book and make sure theres no moisture or air in system oh and top tip to any one who works on these and has a leak they cant find change the evap an capillary especially on the old units with hot gas defrost the drier is good idea as well and fit a schrader valve in discharge line how can you vac it out properly if you dont ? oh and a mag lifter on hot gas solanoid makes a good professional touch as well



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    u didnt do an acid test!!! -plumber haha,did u clean the condenser coil?also id change the condenser fan coz for the sake of a 10w multi fit, maybe replace the digi controller too if its a few year old!

  3. #3
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    no no acid test and it had a new motor and i always fit a 16watt multifit have a spare controller but dont tell anyone as we aint allowed to carry spare anything lol

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    ahhh-personnel van stock!! ive got loads of stock of condensate pumps,fixings,core cutters,fuses etc.
    what bosses dont realise is if u have a part in the van it pulls u out the s**t! then u replenish stock at a later date. but they wont splash out on kitting u out with stock,the only problem is the warranty is running out whilst its getting squashed by gas bottles etc.
    oh well done for changing the fan ,youll make a good plumber yet haha
    Quote Originally Posted by simon@parker View Post
    no no acid test and it had a new motor and i always fit a 16watt multifit have a spare controller but dont tell anyone as we aint allowed to carry spare anything lol

  5. #5
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    nah had changed fan 4 weeks ago ish so i knew it was good and really we are not allowed to carry any stock at all nothing only equipment and i have no room for gas bottles but ones i need to do current job have to collect them everytime i need them

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    si has vanstock,si has vanstock-fans,controllers,compressors,fancy driers,horse food and fishing tackle!!!haha

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: foster 2 door freezer

    I got van stock, i got van stock, i got fans, i got driers, i got comps, i got pumps, i got all van stock...

    http://www.youtube.com/watch?v=FX1BPItDcDo

    Wheres my banjer
    Mostly found in Oxfordshire, UK :)

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    Quote Originally Posted by monkey spanners View Post
    I got van stock, i got van stock, i got fans, i got driers, i got comps, i got pumps, i got all van stock...

    http://www.youtube.com/watch?v=FX1BPItDcDo

    Wheres my banjer
    have u got a spare banjo and strings,because uur ****ed if u snap ur banjo!!!!!!!!!!!!!!haha

  9. #9
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: foster 2 door freezer

    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    Quote Originally Posted by mikeref View Post
    mike we both need councilling!,rehab and a bucketfull of red tablets-haha
    Last edited by install monkey; 27-08-2011 at 05:55 PM.

  11. #11
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: foster 2 door freezer

    Hi Simon,

    Is that right that you have to take the charge weight with a pinch of salt?
    I've worked on a couple that initially seem short of charge but weigh out plenty of gas and prior to that would equalise so no obvious blockage. Unless extra refrigerant is added then evaporator is starved although subcooling hovers around 8k at factory charge so it would seem correctly charged.
    I've put it down to either a partial blockage in the cap tube or the wrong weight on the data plate.

    Ironicly I've got one to look at on Tuesday. Another tech has pressure tested it for 24hrs (which held), regassed to the data plate. I was called to it and found no fan output from the controller (another common fault). New controller fitted but evap starved.
    Smelt a rat so checked another Foster freezer. Was running to temperature but suction pressure was 0psig - thought my gauge line wasn't pressing the valve core down to begin with!

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: foster 2 door freezer

    Tayters, seems like some systems need more gas and others do if larger than factory drier is fitted. Has your better half stolen the remote for the T.V?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    also a partial blockage can be overcome by the additional charge with just an slight increase in head pressure

  14. #14
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: foster 2 door freezer

    Hi Mike,

    Thanks for the reply.

    The boss has hit the sack. Even so it wouldn't work from the kitchen.
    I'm multi-tasking doing this and watching Terminator 3.
    When it's finished I'll moonwalk into the bedroom yell 'Get to da chopper!!' in my finest Arnie accent.

    Oh, that was from Predator wasn't it.
    Health and safety first..........unless I'm in a hurry.

  15. #15
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: foster 2 door freezer

    Add 10 hours to your time. wash day today for me, nothing clean right? http://www.youtube.com/watch?v=Jmm3p...eature=related
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  16. #16
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    Quote Originally Posted by Tayters View Post
    Hi Simon,

    Is that right that you have to take the charge weight with a pinch of salt?
    I've worked on a couple that initially seem short of charge but weigh out plenty of gas and prior to that would equalise so no obvious blockage. Unless extra refrigerant is added then evaporator is starved although subcooling hovers around 8k at factory charge so it would seem correctly charged.
    I've put it down to either a partial blockage in the cap tube or the wrong weight on the data plate.

    Ironicly I've got one to look at on Tuesday. Another tech has pressure tested it for 24hrs (which held), regassed to the data plate. I was called to it and found no fan output from the controller (another common fault). New controller fitted but evap starved.
    Smelt a rat so checked another Foster freezer. Was running to temperature but suction pressure was 0psig - thought my gauge line wasn't pressing the valve core down to begin with!

    Cheers,
    Andy.
    when i change drier which i do everytime i break system on these cabs i put a CO32 sporlan 1/4 flare drier in makes it easier to change you also need to look at height and angle of the drier if it to hi conderser has to fill with liquid to that height to keep good flow to cappillary have had to add extra charge to some foster cabs and i dont know why either but i try not to had few in chilled prep areas that struggle to get a warm condenser so have added extra to make sure they work you may want to try just purging nitrogen through yr unit at low pressure for 10 mins this does make a difference to how it vaccs out i have been following up previous contractor on my sites for 2-3yrs now and have had some major probs with some of the foster cabs where they just added a shot of gas got one cab replaced as i had changed capillary 4 times and done numerous gas and drier changes all down to there bad practice when they changed capillary an just cut it and didnt braze ends moisture will kill these cabs and i dont think they owned a vac pump lol good luck with yr cab oh and because it a small system it needs perfect practice every single tme or you will get probs

  17. #17
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    whats a vac pump? haha
    Quote Originally Posted by simon@parker View Post
    when i change drier which i do everytime i break system on these cabs i put a CO32 sporlan 1/4 flare drier in makes it easier to change you also need to look at height and angle of the drier if it to hi conderser has to fill with liquid to that height to keep good flow to cappillary have had to add extra charge to some foster cabs and i dont know why either but i try not to had few in chilled prep areas that struggle to get a warm condenser so have added extra to make sure they work you may want to try just purging nitrogen through yr unit at low pressure for 10 mins this does make a difference to how it vaccs out i have been following up previous contractor on my sites for 2-3yrs now and have had some major probs with some of the foster cabs where they just added a shot of gas got one cab replaced as i had changed capillary 4 times and done numerous gas and drier changes all down to there bad practice when they changed capillary an just cut it and didnt braze ends moisture will kill these cabs and i dont think they owned a vac pump lol good luck with yr cab oh and because it a small system it needs perfect practice every single tme or you will get probs

  18. #18
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    that thing in back of yr van that sucks roflmao

  19. #19
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    fitted a panasonic cassette on saturday! did 4 flares on 4 connections and no f**kups!! i am the flare king!haha
    Quote Originally Posted by simon@parker View Post
    that thing in back of yr van that sucks roflmao

  20. #20
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: foster 2 door freezer

    Quote Originally Posted by simon@parker View Post
    that thing in back of yr van that sucks roflmao
    Speaking of things in the van, do you still keep the naughty mags under the seat?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  21. #21
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    oh yes got them all climate book hrp one fpw screwfix all the very best dirt lmao if yr talkin bout naked ladies dont need a grot mag as i got a phone with massive memory an internet lol

  22. #22
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    ahhhh the mobile phone 10yr ago it was the size of a brick and all u could do is call people. now its compact ,u can watch porn on it save service manuals on it,send piccys,videos,watch porn on it,ring people,watch porn on it,text and e mail,watch porn on it,now all ur soiled chuff mags are recycled into drinking cups etc haha

  23. #23
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: foster 2 door freezer

    Quote Originally Posted by install monkey View Post
    ahhhh the mobile phone 10yr ago it was the size of a brick and all u could do is call people.
    What not like my first posing phone !

    http://www.youtube.com/watch?v=CfYTkruW7iQ
    If the World did not Suck, We would all fall off !

  24. #24
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    haha-bet u still have it for when u go out clubbing.casualty for u if u drop it on ur snakeskin boots!!!! u could use the ariel to whip horses!!!! have u given up on fishing?
    Quote Originally Posted by chillerman2006 View Post
    What not like my first posing phone !

    http://www.youtube.com/watch?v=CfYTkruW7iQ

  25. #25
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: foster 2 door freezer

    Quote Originally Posted by install monkey View Post
    haha-bet u still have it for when u go out clubbing.casualty for u if u drop it on ur snakeskin boots!!!! u could use the ariel to whip horses!!!! have u given up on fishing?
    Nah ! wish I did probaly worth a few quid all up and running plus lets see a company track this mother, its was bad enough trying to make a call they can forget tracking it

    I had a bigger one than this at first, a panasonic, huge battery about 3 times the size of that 8500 and handset sat ontop, cant think of its name to search it though
    May need to start fishing again 2 !!! dinners it's cost me now and not even a good night nosh !
    If the World did not Suck, We would all fall off !

  26. #26
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    haha- i had a sony mars bar phone-with a lil sliding speaker it was small,can find a pic on u tube rented it from martin dawes,£20 per hour for outging calls,that was 18yr ago. was the panasonic the big shoebox with ariel and the phone on top and it had a shoulder strap for the batteries??? get it on mazuma all the lead in them batteries,the acid should of evaporated or leaked by now

  27. #27
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: foster 2 door freezer

    Quote Originally Posted by install monkey View Post
    haha- i had a sony mars bar phone-with a lil sliding speaker it was small,can find a pic on u tube rented it from martin dawes,£20 per hour for outging calls,that was 18yr ago. was the panasonic the big shoebox with ariel and the phone on top and it had a shoulder strap for the batteries??? get it on mazuma all the lead in them batteries,the acid should of evaporated or leaked by now
    Yep ! thats the one - no worries about getting knicked you could give them a ten minute head start & still catch up
    If the World did not Suck, We would all fall off !

  28. #28
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    poor simon was fixing a foster fridge and the thread has evolved from fridges to illegal van stock to porn then mobile/unmobile phones.

  29. #29
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: foster 2 door freezer

    Sorry Si

    Hijacking your thread, mate
    If the World did not Suck, We would all fall off !

  30. #30
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    send him a carrier manual,and a few passwords-haha

  31. #31
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    have a carrier manual on my phone lmao pdf format roflmao dont worry bout the hijacking

  32. #32
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    bet its just a list of fault codes for pro dialogues- or u havent got much porn on ur phone haha

  33. #33
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    nah its a manual for chillers with the liquid pump and as in any manual they have 100pages but theres only one u ever need lmao its just finding it lol

  34. #34
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    u must have a big memory card in it or do u just stream ur porn,get a laptop so u can store more,bigger screen, and u can chat to the mrs whilst spanking the chicken!!

  35. #35
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    32 gig memory on me phone and its practically a laptop do most of this on it

  36. #36
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: foster 2 door freezer

    so u must stream ur porn as opposed to having a stash haha
    Quote Originally Posted by simon@parker View Post
    32 gig memory on me phone and its practically a laptop do most of this on it

  37. #37
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: foster 2 door freezer

    Quote Originally Posted by install monkey View Post
    u must have a big memory card in it or do u just stream ur porn,get a laptop so u can store more,bigger screen, and u can chat to the mrs whilst spanking the chicken!!
    Spanking the chicken eh? You mean recharging the battery http://www.youtube.com/watch?v=hnX6e...eature=related
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  38. #38
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: foster 2 door freezer

    Quote Originally Posted by Tayters View Post
    Hi Simon,

    Ironicly I've got one to look at on Tuesday. Another tech has pressure tested it for 24hrs (which held), regassed to the data plate. I was called to it and found no fan output from the controller (another common fault). New controller fitted but evap starved.
    Smelt a rat so checked another Foster freezer. Was running to temperature but suction pressure was 0psig - thought my gauge line wasn't pressing the valve core down to begin with!
    Just to let you know, reclaime only 300g of the 420g charge, found leak on cap tube where it had rubbed through on compressor (think I made it worse by poking about to find the leak which might explain why it held a previous 25hr test).
    Repaired the tube with a bit of 1/4" pipe, new dryer (copper spun type with HP connection port).
    Regassed with 420g (factory charge) same story with starved evap, suction pressure about 0psig. Subcooling was around 10K but cap tube was clear, condensor blown out, purged whilst brazing and all that jazz.
    Ended up sticking a final charge of 600g. Subcooling now around 15K, SST -30*C S/H still high at 20k.
    Reached -16 downstairs where I did all the work. Wheeled it back upstairs, turned it on, compressor getting red hot but not spinning. Great. Either took a knock on the way up and come off internally or maybe a slug of liquid stuck in there when Iturned it back on. Left it off overnight.
    Back next day, turned on and it fired up, reached setpoint, cycled, worked on defrost etc.
    Maybe it didn't like the bit of extra charge so I took a smidgen out.
    What a rigmorole, but I got there in the end.

    Peace out,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  39. #39
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    295
    Rep Power
    15

    Re: foster 2 door freezer

    Quote Originally Posted by Tayters View Post
    Just to let you know, reclaime only 300g of the 420g charge, found leak on cap tube where it had rubbed through on compressor (think I made it worse by poking about to find the leak which might explain why it held a previous 25hr test).
    Repaired the tube with a bit of 1/4" pipe, new dryer (copper spun type with HP connection port).
    Regassed with 420g (factory charge) same story with starved evap, suction pressure about 0psig. Subcooling was around 10K but cap tube was clear, condensor blown out, purged whilst brazing and all that jazz.
    Ended up sticking a final charge of 600g. Subcooling now around 15K, SST -30*C S/H still high at 20k.
    Reached -16 downstairs where I did all the work. Wheeled it back upstairs, turned it on, compressor getting red hot but not spinning. Great. Either took a knock on the way up and come off internally or maybe a slug of liquid stuck in there when Iturned it back on. Left it off overnight.
    Back next day, turned on and it fired up, reached setpoint, cycled, worked on defrost etc.
    Maybe it didn't like the bit of extra charge so I took a smidgen out.
    What a rigmorole, but I got there in the end.

    Peace out,
    Andy.
    i think the slightly higher pressure from the extra gas can cause problems on start when unit has warmed up have only ever had to overcharge units running in chill rooms so condensers have been always cold next one you do try reposistioning the drier as in slightly lower down condenser before you add extra gas an see if that works
    I can fix broke but I cant fix stupid :)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •