    Dear Forum
    I like to know up to what temperature can ammonia refrigerant can achieve .
    I like to design for -40 DegC with Ammonia Refrigerant is that possible.
    I came to know that it is possible in two stage system is that true?
    please give me suggestions
    Thank you.
    Auckland
    74
    3,357
    37
    Re: Ammonia Low Temperature Chiller
    Yes they can run down to -50'C air temp., with two stage systems.
    Auckland
    74
    3,357
    37
    Forgot to mention that -40'C temps are quite acheivable with single stage screw compressors with sub-coolers.
    magoo
    Nov 2007
    India
    74
    Yes you can acheive easily with Ammonia using single stage compressor / two stage (booster / high stage) reciprocating compressors.
    Sep 2009
    Iran
    66
    672
    1
    temperature is not very important , main thing is :
    what kind liquid do you want to cool
    Nov 2009
    India
    41
    32
    Thanks for your suggestions
    I like to cool methanol fluid , can any one provide me normal diagram how to design .
    please do me need full.
    Dec 2008
    usa
    83
    34
    Several different basic designs are possible. Depends on the amount of cooling desired, btu per hour? or other measurement in metric units kw per hour etc?. Evaporator can be plate and frame, direct expansion shell and tube, or flooded shell and tube. Compressor can be recip or screw. Condenser can be water cooled, evaporative air/water or even air cooled. Without getting into details there are several pieces of equipment that nay be required such as receiver, economiser, interstage desuperheater to cool discharge from low stage compressor.
    Methanol a fairly good choice for the fluid. Low cost, low viscosity, low freezing temperature, but poor specific heat and of course, flammability may be an issue depending on the water/methanol concentration.
    If you are trying seriously to design a system you had best have an expert help you out