Results 1 to 50 of 135

Hybrid View

  1. #1
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: How to assign thermodynamic properties after splitting two phase into gas and liq

    Quote Originally Posted by Chef View Post
    Maybe you missed my point so I will try again. We have removed gas at the 8 bar line and so this gas is no longer cooled by flashing liquid, similarly the gas at 4 and 2 bar are seperated and they also need no further cooling. In a standard TXV system all the gas is cooled to the evap temp so we have saved some energy here. The question is - is it enough to help and then we have the side streams of gas.

    Got to replace the mainsail so the diagram will come later.

    Chef
    I'm confused. Does the liquid cool the gas?... or does the gas cool the liquid?

  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: How to assign thermodynamic properties after splitting two phase into gas and liq

    Quote Originally Posted by Gary View Post
    I'm confused. Does the liquid cool the gas?... or does the gas cool the liquid?
    Hi Gary

    If I have followed properly, the liquid is cooled by the drop in pressure after the condensor, before the vessel, (constant pressure valve) the flash gas removal, does not affect 'p' or 't' but increase's mass to txv

    Regards Chillerman
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: How to assign thermodynamic properties after splitting two phase into gas and liq

    Quote Originally Posted by chillerman2006 View Post
    Hi Gary

    If I have followed properly, the liquid is cooled by the drop in pressure after the condensor, before the vessel, (constant pressure valve) the flash gas removal, does not affect 'p' or 't' but increase's mass to txv

    Regards Chillerman
    Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: How to assign thermodynamic properties after splitting two phase into gas and liq

    Quote Originally Posted by Gary View Post
    Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.
    Hi Gary

    Thankyou Sir,

    Dont know what I was thinking trying to educate you, duh!

    The info hit a reverse cycle valve & miss-directed

    But still got you thinking, mate & now we both understand,

    R's chillerman
    If the World did not Suck, We would all fall off !

  5. #5
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: How to assign thermodynamic properties after splitting two phase into gas and liq

    Quote Originally Posted by Gary View Post
    Actually, on a drop in pressure part of the liquid flashes into vapor and heat from the liquid is transferred to that vapor... the gas cools the liquid.
    So a small experiment is due here I feel. I pour lighter fuel on my hand and as it evaporates it gets cold, if I blow on it it gets even colder as more evaporation takes place. So you are telling me that the gas after evaporation is cold and in the time available before it disperses in the atmosphere it has time to transfer it coldness to the liquid. Yeah right I beleive that. If you wish you could provide a useful referance to support your comments.

    In the PH diagram I posted there are 3 places where we propose to strip the gas away and pipe it off for its own process. The first split is at 8 bar which is 31.4C so the gas remains at that temp in its side pipe.

    If we had left that gas with the rest of the refrigerant as in a standard TXV system it would need to be cooled down to -26C which is the evap temp in this case.

    So we are going to need to cool that gas and the only source of 'cold' is the liquid hence my comment the liquid will cool the gas. The JT effect is not enough on its own. It is the phase transition that does the cooling.

    But you say the gas cools the liquid so by dropping some gas from 8 bar to 1 bar it will cool in a process that not not only cools itself but has enough (negative) energy to also cool some of the liquid. ????

    Chef
    Last edited by Chef; 23-08-2011 at 09:47 PM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •