    3,356
    Low pressure drop non return valves screw compressor
    Has anyone a recommendation for a proven suction check valve on a screw compressor.
    Needs to have smallest possible pressure drop across it.
    Sizes approx 125-300 mm in size.
    Can also be a stop check valve
    Thanks Ranger
    Auckland
    74
    3,357
    37
    Re: Low pressure drop non return valves screw compressor
    Hi Ranger1,
    generally have those double plate spring loaded things, but they can generate 1 degree loss at super low suction. Concider a stop check flapper vav straight after the compressor in discharge line between comp and separator.
    magoo
    Jul 2007
    Czech
    61
    373
    If there is no escape from the pressure separator to the intake valve is OK.
    Auckland
    74
    3,357
    37
    Hi Ranger.
    how did you get on with check vav.
    magoo
    3,356
    Magoo,
    Just curious really as everyone talks about penalties/efficiency etc etc.
    You/I know about discharge check benefits but only a few companies doing it like Bitzer
    that I know of.
    Have seen a few with I think Grasso stop/checks, but don't know how good they are
    compared to Duo checks.
    Auckland
    74
    3,357
    37
    Hi Ranger,
    The duo stop checks are reasonable high pd on suction add the strainer and several degree losses.
    I have had a Bitzer discharge check let go, the shaft separated from head [ a friction fit ] and sucked the spring back into screws, not a pretty site.
    Dec 2008
    Portugal
    48
    1,020
    Magoo,
    that I know of.
    Yes. Bitzer screws have a discharge check valve integrated on the screws compressors. Attention: if using ECO you should to use a suction electric valve at the ECO port so preventing the gas flow from the ECO to the main suction.