    mqquay screw LOW DISCHARGE superheat fault



    ok

    gas charge of system is unknown. r134a, it does run and cool (perhaps not efficently) but it works.

    from time to time its constantly tripping on the above fault. ive slowed down fan motor speeds to raise head pressure, did seem to work, but any ambient above 21c she fails on me.

    if i am completly honest the fault baffles me to what its saying..

    any advice or comments on similar issues appreciated. lotsss



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: mqquay screw LOW DISCHARGE superheat fault

    sweimaker could be something to do with oil temp/discharge temp being to close to saturated condensing pressure.
    Normally oil/discharge temp, say on a Bitzer recommend 15 C above SCT to keep refrigerant diluting oil.

    What type of oil cooling does it have, if any?

  3. #3
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    thanks fgor your reply.

    both cirucits are running high oil pressures (oil and filters have been changed a month ago)

    mcqauy say it should run between 1 -1.5 bar

    we are running 2-2.5 (cut outs at 2.5.

    if this helps

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: mqquay screw LOW DISCHARGE superheat fault

    Could it be flooding back causing low discharge temps?

    Have you checked superheat at compressor?

  5. #5
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    hey thanks for response guys...ok

    2 circuit son chiller. circuit 1 is ok..

    circuit 2 has the low discharge super heat fault

    this is how far ive got

    discharge leaving compressor is 55 degrees (at full duty) circuit 1 is 85

    suction is 7 degress on both circuits.

    whats happening is the exv is fully openning!!! 2000 pulses where as on circuit 1 full load is 0800


    if any1 has an answer to why the microtech 2 aka carell controller is demanding the exv to fully open would help.. it was replaced 2 months ago possibly the computer has malfunctioned.?

    same suction temps as the working circuit 1, but liquid is flooding back. i havent actually checked the suction sensor although its reading spot on with circuit 1, even though still no answer for the exv openning to completly open.,

    any help i would love to hear your views

  6. #6
    Join Date
    Feb 2012
    Location
    nigeria
    Age
    51
    Posts
    1
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    Low suction super heat fault occur whenever you have a low super heat temperature, at 100% load your discharge temperature should be arround 85c, and superheat between 30 and 35 degree, lack of rfrigerant can cause a low super heat, also liquid flooding back can cause the low superheat on mcquay chillers with screw compressors. evaporator freezing also cause oil to flood back and cause a low super heat temprature.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: mqquay screw LOW DISCHARGE superheat fault

    Tony.
    Welcome to the forum, Sadly your first post may be up to 4 months to late.
    It is well worth checking the date the post is added.
    But good luck for the future all the same.
    Grizzly.

  8. #8
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: mqquay screw LOW DISCHARGE superheat fault

    Do u have economizer or liquid injection. If yes check them.

  9. #9
    Join Date
    May 2009
    Location
    Portugal
    Age
    60
    Posts
    14
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    Also check your EXV, improper setting of EXV can also cause this issues tipically from units with thermostatic EXpansion Valves.

  10. #10
    Join Date
    Jul 2012
    Location
    Albania
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    Hello, have you resolve that problem? What it was? I have getting the same problem. Thanks

  11. #11
    Join Date
    Jul 2012
    Location
    Albania
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: mqquay screw LOW DISCHARGE superheat fault

    i resolve it , it was the exv sensor on suction pipe :-)