Thread: shower switch fault !
-
12-10-2005, 09:28 AM #1
shower switch fault !
sorry didnt knw wher to post this, but as its an electrical issue....
i opened the shower switch up as it jammed in the off position and had a funny fishy smell(cue funny comments....) coming from it....and found it 2 b melted,along with both neutrals
1 of the neutrals popped out very easily....
also the 1 of the live wires has a black burn strip running down it....
but the other live wire is ok...
my question is this....
could the melting of the wiring be caused by the switch heating up n melting, due to the loose connection, in turn leading to the melting of the wiring ?
its 2.5 mm twin and earth...so i would have thought its sufficient enough rite ?
any ideas ? as this is the second time this switch has burned out and im looking for a permanent fix
cheers
-
12-10-2005, 09:38 AM #2
Re: shower switch fault !
2.5MMM ?????
Youre joking Krupps
Is it a 8KW shower?
I think you need to use ,
Im not sure if its 6mm or 10mm
Ill checkAny opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
-
12-10-2005, 12:15 PM #3
Re: shower switch fault !
I have done a whole house electrics in Scotland,
Used a 10mm wires for the shower water heater.
No problems for the past 6 years.
I agree with Marc, there is nothing like a loose connection for a little fire in the house.
When in doubt about the wires mm, go one or to higher.
Chemi
-
12-10-2005, 03:31 PM #4
Re: shower switch fault !
sorry meant 6 mm lol not 2.5mm i was thinking about something else at same time as writing this.....
its a 10.5kw electrical shower...
think iv sorted it now neways....
gonna run a fresh 10mm cable in and new switch
-
12-10-2005, 05:05 PM #5
Re: shower switch fault !
10.5 kw is fairly large for a shower. is the switch a proper rated double pole isolator or the ceiling mounted pull cord type as it may not be rated high enough {10500w/240v = 43.75a} for full load.
-
12-10-2005, 08:06 PM #6
Re: shower switch fault !
it may not be rated high enough {10500w/240v = 43.75a} for full load.
It is now required to calculate everything in the UK as either 230v or 400v so your calculated running current (for cable sizing purposes) should be 10500w/230v = 45.65A. Cable sizing should then be calculated on the instalation method in accordance with BS7671
-
13-10-2005, 12:41 PM #7
Re: shower switch fault !
Originally Posted by frankTakes a licking, keeps on ticking.
-
13-10-2005, 02:04 PM #8
Re: shower switch fault !
its a 45amp double pole ceiling mounted pull cord type as far as i remember...but dont qoute me on that...
thanks for the info guys...
-
13-10-2005, 08:36 PM #9
Re: shower switch fault !
Obviously you guys are not upto date with current regs
-
14-10-2005, 04:18 PM #10
Re: shower switch fault !
Originally Posted by Krups
then a connection somewhere is loose. maybe in the switch or possibly in the shower. might even be in the dis board. loose connection= higher current draw= toast!Takes a licking, keeps on ticking.
-
19-10-2005, 09:10 PM #11
Re: shower switch fault !
The length of run is also an issue , the longer the run the higher the resistance the bigger the cable needed.Sounds like a loose connection to me, also in respect of the switch you get what you pay for so it is normally senisible to buy a decent make a first, something like crabtree or mk
Steve
Similar Threads
-
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Diplomat 6528 Fault Code
By Targus in forum DomesticReplies: 3Last Post: 31-10-2006, 07:43 PM -
Chiller fault
By iceman007 in forum Trouble ShootingReplies: 9Last Post: 27-06-2006, 06:15 AM -
Shower problems
By pscott898 in forum Chit Chat & Service StoriesReplies: 12Last Post: 23-05-2006, 06:24 PM -
Chiller Fault
By iceman007 in forum Air ConditioningReplies: 2Last Post: 13-05-2006, 07:23 PM