    Process chiller - Typical operating temperatures?



    Hi everyone,

    I have an application where the client wants to dehumidify a process gas stream, using a cold water flow.

    I have two options:
    1. Standard chiller circuit : 7'C delivery, 12'C return.
    2. Antifreeze/water circuit : temps to be determined.

    I have option (1) fairly well covered, it's option (2) where I need a lot more info.

    How low a temp in an antifreeze/water circuit is typical in the industry?
    Which antifreeze is preferable : ethylene-glycol, or propylene-glycol (less toxic), from a performance point of view?

    Are there any particular additional safety features that should be considered for a low-temp chiller, over that of a standard chiller circuit?

    Thanks everyone.
    Last edited by desA; 14-08-2011 at 06:55 PM.


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Process chiller - Typical operating temperatures?

    Hi DesA,
    propylene is the food grade for incidental food contact and more "expensive ", for a 0.0'C water design have a gycol solution mix for at least -10'C. You will get a chiller HX de-rating, and slight water pump Kw increase with the higher spec density. The chiller HX rating will reduce approx 10 > 15 %, suggest having a buffer tank.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Process chiller - Typical operating temperatures?

    Hi Magoo,

    Thanks so much for your applied wisdom. Over here, the ethylene-glycol mix seems to be the main one used, with propylene-glycol a bit of a rarity. The buffer tank makes sense.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Process chiller - Typical operating temperatures?

    We have a similar system with etylene glycol.

    It has a back pressure regulator & compressor unloads as well 100/75/50%.

    Buffer tank is good if you want constant temps as well as to allow for cycling off
    on limit start timer etc.

    We used PHE condensoe & evaporator

  5. #5
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    189
    Rep Power
    15

    Re: Process chiller - Typical operating temperatures?

    If the standard chiller option will get you what you need I would avoid the glycol alltogether. It is less effecient and comes with enviornmental issues.

  6. #6
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Process chiller - Typical operating temperatures?

    Thanks Ranger1.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Process chiller - Typical operating temperatures?

    Quote Originally Posted by Emmett View Post
    If the standard chiller option will get you what you need I would avoid the glycol alltogether. It is less effecient and comes with enviornmental issues.
    Thanks Emmett. I agree on the efficiency reduction for the heat-exchangers in the water-glycol circuit - these are fairly significant.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Process chiller - Typical operating temperatures?

    If anyone perhaps has a simple flow circuit for the chilled-water side, with buffer tank included, I'd be most grateful.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Process chiller - Typical operating temperatures?

    Hi, desA



    Quote Originally Posted by Emmett View Post
    If the standard chiller option will get you what you need I would avoid the glycol alltogether. It is less effecient and comes with enviornmental issues.

    Agree with Emmett... sounds like a petrochemical plant... make it simple and your life easy...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Process chiller - Typical operating temperatures?

    Thanks so much Josip. Much obliged.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  11. #11
    ckgireesh's Avatar
    ckgireesh Guest

    Re: Process chiller - Typical operating temperatures?

    chiller barrel with steel case and copper pipe
    after staring the chiller there is dust in the chilled water......
    from where it is? from the barrel? i mean barrel rusting?
    no chemical in the water...
    this chilled water used for some critical machinaries?
    how we can avoid barrel rusing and cahanging water clour?

    please reply

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Process chiller - Typical operating temperatures?

    Quote Originally Posted by desA View Post
    If anyone perhaps has a simple flow circuit for the chilled-water side, with buffer tank included, I'd be most grateful.
    Hi DesA,

    only just seen this one,

    I dont have any chilled water circuit diagrams sorry, as they are normally pinned to the plant room wall, A3 size as well, but if they are any use I do have a number of chiller flow charts if interest to you, from standard to de-superheaters & full heat recovery, was just thinking with your hot water from thin air, you might want to consider using available wasted energy with your install

    R's chillerman
    If the World did not Suck, We would all fall off !

  13. #13
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Process chiller - Typical operating temperatures?

    Quote Originally Posted by desA View Post
    Are there any particular additional safety features that should be considered for a low-temp chiller, over that of a standard chiller circuit?
    Hi DesA

    a split vessel is a nightmare so as much protection as possible is a must, there is only one thing worse than water in the fridge system and thats glycol, they are both a b*tch to remove

    In addition to flow switch, differential pressure switch (water in/out) plus a must if running 7c setpoint that the lp switch is set to at least 0c preferably 1c, you should get away with 1c without tripping when pulling down, then at least you have backup if flow switch fails + dp & flow switch dont always trip when flow is there but low, the lp will

    below 6c heat transfer as mentioned above deteriates alot as you will need at least 12c protection below setpoint and 20c below setpoint to be safe on R407c

    Hope I am not trying let you know the obvious here mate, but rather look like I am than hear your vessel splits

    R's chillerman
    If the World did not Suck, We would all fall off !

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Process chiller - Typical operating temperatures?

    Does the stream need to be simply dehumidified or dehydrated?

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Process chiller - Typical operating temperatures?

    All comments make sense but for the buffer tank I have some remarks. You only need one if you have a wide varying load and not the possibility to cycle on your compressors (part load ability) If your smallest part load on you chiller matches +/- the smallest load on your system, then you don't need one.
    You can also use a(don't now the correct English name) an equilibrium vessel.
    I scanned some pages from the books of Kotza which I will send you (to big to post here) They're in French, ..sorry.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    189
    Rep Power
    15

    Re: Process chiller - Typical operating temperatures?

    Quote Originally Posted by ckgireesh View Post
    chiller barrel with steel case and copper pipe
    after staring the chiller there is dust in the chilled water......
    from where it is? from the barrel? i mean barrel rusting?
    no chemical in the water...
    this chilled water used for some critical machinaries?
    how we can avoid barrel rusing and cahanging water clour?

    please reply
    ck
    First when you have a specific question you want to ask it is best to start your own thread.
    Second you must add a rust inhibitor or you will continue to degrade the metal in the system and always have discolored water.
    Third to clean up the mess you already have I suggest you install a side stream filter and gradually reduce the microns of the filter until the system is clean.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Process chiller - Typical operating temperatures?

    You can also use a(don't now the correct English name) an equilibrium vessel
    Maybe "hydraulic disconnector"?

  18. #18
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Process chiller - Typical operating temperatures?

    Quote Originally Posted by Peter_1 View Post
    an equilibrium vessel.
    .
    Evening Peter

    have viewed all day on/off waiting for someone to say what this is

    Clues
    1. equilibrium vessel
    2. air vent on top
    3. drain valve at bottom
    4. inlet/outlet x4

    Not seen or heard of one before so don't know what it's called but at the risk of becoming 'your signature' I shall jump in with both feet now....does flow & return run into this vessel where their temperatures equalize...keeping a more constant load on the system ???

    R's chillerman
    If the World did not Suck, We would all fall off !

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •