    PHE and Horizontal Surge Drum



    Dear All
    For a Soft Drink planta
    This will be a new installation

    There will be 8 flooded Amoniac Plate Heat Exchanger (PHE) cooling water to 2ºC

    Each PHE have 250 Tr (880 kW) so the installed capacity will be 2000Tr (7040kW)

    The plant woud like to install just one surge drum for all PHE (2 m diameter x 5 m long)

    The surge Drum will be located at 6 m high over the PHE

    The idea is to use just one liquid pipe to feed all PHE(slopped 1%) and one pipe for each PHE to return the two fase ammonia to a main manifold located over the surge drum .
    The Manifold will be 1% slopped down to the surge drum

    The ammonia make up will come from the tank reciever

    The evaporation temperature will be -1ºC


    With all this information I appreciate your very kind expirence to adivice any problem that you could preview

    Thanks
    Gwapa



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    Gwapa,
    We normally use PHE as a pre- cooler for majonier type carbonator.

    Is that what you are doing?

    If flow stops in 1 PHE water will freeze, have you got anything to prevent a freeze up
    in this situation?

  3. #3
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    Ranger1
    Yes They are using amonia in the carbocooler, but the want to elimnate the amonia from the proceses area and locate it in the Room Machineries
    So we will use product vs Chill water in carbocooler and the exiting ammonia PHE will be moved to the room machinery to chill water
    The room is not to big so they want to use just one separator for all PHE
    The freezer point is very good point I think we could have a hot gas line in each PHE and automatic shut off valves
    What do you think??
    Thanks
    Gwapa

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: PHE and Horizontal Surge Drum

    Hi, Gwapa

    Quote Originally Posted by gwapa View Post
    Dear All
    For a Soft Drink planta
    This will be a new installation

    There will be 8 flooded Amoniac Plate Heat Exchanger (PHE) cooling water to 2ºC

    Each PHE have 250 Tr (880 kW) so the installed capacity will be 2000Tr (7040kW)

    The plant woud like to install just one surge drum for all PHE (2 m diameter x 5 m long)

    The surge Drum will be located at 6 m high over the PHE

    The idea is to use just one liquid pipe to feed all PHE(slopped 1%) and one pipe for each PHE to return the two fase ammonia to a main manifold located over the surge drum .
    The Manifold will be 1% slopped down to the surge drum


    The ammonia make up will come from the tank reciever

    The evaporation temperature will be -1ºC


    With all this information I appreciate your very kind expirence to adivice any problem that you could preview

    Thanks
    Gwapa
    What size is that liquid pipe down to feed all PHEs?

    Can you upload a hand drawing with connection of main liquid header to each PHE and return lines connected to main suction header?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Feb 2007
    Location
    ireland
    Age
    43
    Posts
    7
    Rep Power
    0

    Re: PHE and Horizontal Surge Drum

    if you are bringing the water down to -1 i presume there will a gylcol storage tank also your chill water side, the 3 PHEs are they fed off a single primary circulation header or on individual pumpsets.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    Quote Originally Posted by gwapa View Post
    Ranger1
    Yes They are using amonia in the carbocooler, but the want to elimnate the amonia from the proceses area and locate it in the Room Machineries
    So we will use product vs Chill water in carbocooler and the exiting ammonia PHE will be moved to the room machinery to chill water
    The room is not to big so they want to use just one separator for all PHE
    The freezer point is very good point I think we could have a hot gas line in each PHE and automatic shut off valves
    What do you think??
    Thanks
    Gwapa
    Yes you could do that & instal a normally open solonoid for hot gas.

    Have never seen a system on carbo-cooler like this though.

  7. #7
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: PHE and Horizontal Surge Drum

    Quote Originally Posted by gwapa View Post
    ...With all this information I appreciate your very kind expirence to adivice any problem that you could preview

    Thanks
    Gwapa
    "The pressure drop that occurs through a plate heat exchanger is relatively high and the pumping system should be considered". What about PD and pumps?

  8. #8
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    [Josip][/What size is that liquid pipe down to feed all PHEs?]
    We have not select the pipe diameter . I think that it should be selected with a speed of 1 m/s or lower
    I do not know upload the drawing

    [Josei][ I am think that it will work as a thermosiphon but 8 PHE working with one tank. It will work as the oil cooler of compressors]
    gwapa


  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: PHE and Horizontal Surge Drum

    Hi, gwapa

    Quote Originally Posted by gwapa View Post
    [Josip][/What size is that liquid pipe down to feed all PHEs?]
    We have not select the pipe diameter . I think that it should be selected with a speed of 1 m/s or lower
    I do not know upload the drawing

    [Josei][ I am think that it will work as a thermosiphon but 8 PHE working with one tank. It will work as the oil cooler of compressors]
    gwapa
    to upload a drawing (JPG, PDF up to 100Kb) click on attachments (paperclip icon) in the first row ....

    hope this will help

    Best regards, Josip



    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    8 PHE.jpg

    Josip
    The sketch is just the basic idea We have to make some engineering . What do you all could advise?
    The suction temperature will be 0,5ºC. We will have 6 m high so the temperature inside each PHE will be a little higher
    gwapa

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    Gwapa,
    Water at these temps would be very susceptible to instantaneous freezing.
    Suggest to use glycol in this circuit.

    Why do you need so many PHE?

    Could you not have 1 or 2 PHE with a ring main going out to carbocoolers with auto shut off valves,with maybe a mixing 3 way valveto control outgoing temp by bypassing PHE.

  12. #12
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: PHE and Horizontal Surge Drum

    Quote Originally Posted by RANGER1 View Post
    Gwapa,
    Water at these temps would be very susceptible to instantaneous freezing.
    Suggest to use glycol in this circuit.
    With semi welded PHE no damage will be caused if freezing occur.
    Attached Images Attached Images
    Last edited by josei; 20-08-2011 at 01:21 PM.

  13. #13
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    Quote Originally Posted by josei View Post
    With semi welded PHE no damage will be caused if freezing occur.
    josei,
    Loss of production would be a problem though!

  14. #14
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    Dear Friends
    I am wondering how to control the water temperture
    IF you have just one separator tank for each PHE The temperatura water control would be easy
    So how would be the water temperature cotrol with just one tank???
    appreciate tour comments
    GWAPA

  15. #15
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    If you had 1 PHE on surge drum you could use water temp & Back pressure regulator BPR.
    In your case it could only be BPR unless some body has a better idea?

  16. #16
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    Ranger1
    It is not so easy to control 8 PHE with just one BPR
    IF you select a BPR for 8x250=2000TR it will be a big valve
    But what will happen as long one PHE is working? You will need a very small one
    Gwapa

  17. #17
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: PHE and Horizontal Surge Drum

    A proportinal hot gas injection valve on each PHE inlet

  18. #18
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: PHE and Horizontal Surge Drum

    Just read all posts, SST -1C, water required 0.5C,

    Keep the water velocity high, will not freeze.

    Presume comp loads and unloads, so worry is speed of unloading, possible freezing and loading if load is very quick.

    Install large water buffer to take slack in load times

    Install hot gas valve in main suction line, to cover unloading times.

    And for added protection large suction valve, (closes if the pot pressure drops below a pre-determined set point)

    One presumes you have isolation for service or when a PHE is not in service.

  19. #19
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: PHE and Horizontal Surge Drum

    Gwapa,
    Can you explain why you need so many PHE as well as why water not glycol can be used in this system.
    If power failure or pump hicup water mat freeze.

  20. #20
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    [RANGER1]Can you explain why you need so many PHE as well as why water not glycol can be used in this system.
    If power failure or pump hicup water mat freeze.[/]

    As I mentioned before the plant want to get the amoniac rid of production area.
    Existen 5 PHE (amomia flooded) in the carbocooler. We are going to replace those with chill water/ product
    The PHE existing flooded PHE we will move to thr room machinere to generate the chill water.
    Beside that the Soft drink plant produce a lot of other product ,juice,Gatorade etc
    They use in the juice pasteurization system chill water too.
    For the above facts the plant do not want to use water/propelin glycol solution

    Now , in the room machineries there are enought room to install 8 PHE each with its own separation tank. So we thought in use just one tank.

  21. #21
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: PHE and Horizontal Surge Drum

    mad fridgie

    SST -1C, water required 0.5C, May be the best SST=0,5ºC water =2ºC

    Keep the water velocity high, will not freeze. How much is a high speed?

    Presume comp loads and unloads, so worry is speed of unloading, possible freezing and loading if load is very quick.There are a mxture of compresor ,screw and recip

    Install large water buffer to take slack in load times OK

    Install hot gas valve in main suction line, to cover unloading times. could you go deeper ??

    And for added protection large suction valve, (closes if the pot pressure drops below a pre-determined set point)Remember we will have just one pot for all 8 PHE

    One presumes you have isolation for service or when a PHE is not in service.[/QUOTE]

  22. #22
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: PHE and Horizontal Surge Drum

    Quote Originally Posted by gwapa View Post
    mad fridgie

    SST -1C, water required 0.5C, May be the best SST=0,5ºC water =2ºC

    Keep the water velocity high, will not freeze. How much is a high speed?

    Presume comp loads and unloads, so worry is speed of unloading, possible freezing and loading if load is very quick.There are a mxture of compresor ,screw and recip

    Install large water buffer to take slack in load times OK

    Install hot gas valve in main suction line, to cover unloading times. could you go deeper ??

    And for added protection large suction valve, (closes if the pot pressure drops below a pre-determined set point)Remember we will have just one pot for all 8 PHE

    One presumes you have isolation for service or when a PHE is not in service.
    [/QUOTE]

    Water velocity, 2.2m/s, but you take into cosideration the design of the PHE, pump requirements

    Hot gas quite simple, hot gas taken after the oil sep system, in then injected into the main suction stream, to ensure that the hole pot pressure does not fall below a predetermined point. by which time the comps should have unloaded (pressume suction driven unloading)

    Suction safety, is really that sudden, rapid response. So if the whole pot drops in pressure then all 8 PHE can freeze. Think of it this way, your plant is running 100% capacity, you suddenly loose total water flow to all the PHEs, the plant will not respond quickly enough, even with a hot gas valve to stop freezing, shut the main suction. no freeze. Ok plant goes out on LP, but you have a problem any way.

  23. #23
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: PHE and Horizontal Surge Drum

    Make sure the each ammonia Plate heat exchanger should have same pressure drop on liquid as well as wet return circuit.

  24. #24
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: PHE and Horizontal Surge Drum

    8 PHE.jpgThe sketch is just the basic idea We have to make some engineering . What do you all could advise?.The suction temperature will be 0,5ºC. We will have 6 m high so the temperature inside each PHE will be a little higher.gwapa
    gwapa , this kind of systems require some head of liquid above PHE , but 6 m (18 ft) is out of standard of design and operation of a thermosiphon loop . Take a look at attachemnt here that I selected about basic PHE loop from handbook of these systems design and operation. Any add info can contact by PM
    Last edited by josei; 15-09-2011 at 03:17 PM. Reason: attachement

  25. #25
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19
    ...you suddenly loose total water flow to all the PHEs, the plant will not respond quickly enough, even with a hot gas valve to stop freezing, shut the main suction. no freeze. Ok plant goes out on LP, but you have a problem any way.[/QUOTE]

    Economic solution: install water flow switch if the water flow falls the compressors stop. Even during a while it will be evaporation so you always should run with a evaporating temperature inside the plates of 0ºC, 0,5ºC despite the process water could be a +0,5ºC / +1ºC higher.

    To control the water temperature in each evaporator plate you could use in each one an ICS40 or 50, one the feeding liquid line, with a CVT pilot. This pilot measure the the outlet water temperature (more expensive but maybe better it would be you use ICM-motorized with a temperature sensor connect it).
    Because you have a big height of liquid (6 m) so no problems about feeding head loss. In fact you shall have attention not to feed excessively (and the ICS due to its head loss will help not to feed to much) because the excess of liquid have to rise again to the tank. If is to much liquid you will have hydrostatic penalties and the evaporating temperature inside the evaporator will rise and have oscillations.

    As far I understood you have individual water pump systems grouping one or several plate heat exchanger, right? So for each plate heat exchaner or group of them you can use its ICS+CVT that I mentioned and also mount another pilot the EVM...so it would be an ICS with CVT+EVM pilots. By the way I'm talking about the DANFOSS valves.

    Wherever the water flow that feed one of the plate exchanger groups stops (due to the process function) the pilot EVM close the ICS that feed the plate exchanger with R717. The water pumps can continue ON just for a while so ensuring the plate evaporator have no more liquid and so preventing the water inside the plate evaporator freezes (albeit the evaporating temperature is > 0ºC it is just a security manner).

    Gwapa,

    How is running this project? What did you decided to do about?