    Ice building up



    I have problems with air condition unit Denco Model U5AG. Ice is building up on lower part of evaporator and a lot of ice building up around expansion valve and suction stop valve. Sight glass is clear with no bubbles. I tryed to fill 300 gram with R22 but it is not getting better.
    I have some measurings before and after filling.
    Before:
    Evaporator pressure 1,8 bar
    Condensator pressure 11 bar
    Suction temp -14 degrees
    Pressure temp 56 degrees.

    After filling 300 gram and 30 minutes running a lot of Ice had again build up and readings was:
    Evaporator pressure 1.1 bar
    Condensator pressure 10 bar
    Suction temp -7 degrees (use IR temp reading so maby not correct)
    Pressure temp 56 degrees

    Differential pressure before and after dry-filter is 1 bar.

    What can be wrong here?
    Please help!



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Hi Karlsen

    sounds like blocked drier (dry-filter) - if I understand your post correctly

    I have ir thermometer - supposed to be good (fluke) but it's always reading wrong
    ok for rough guide - not trouble shooting
    If the World did not Suck, We would all fall off !

  3. #3
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    Thank you Chillerman! Will a blocked drier result in ICE on expansion valve, suction stop valve and evaporator? If so, I will change out filter. Thanks..

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by Karlsen View Post
    Thank you Chillerman! Will a blocked drier result in ICE on expansion valve, suction stop valve and evaporator? If so, I will change out filter. Thanks..
    if the drier is blocked you will not get a clear feed of liquid between drier and txv

    you then got frosting on valve and first section of evaporator

    easy check - even though ir is not accurate - you can check for temperature drop

    either side of drier - on pipework

    hard for me to say for definate whats going on as

    pressures & temperatures do not add up to me - probaly IR thermometer
    If the World did not Suck, We would all fall off !

  5. #5
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    Hmm.. Just checked temp before and after filter. Temp before filer 21,8 degrees and 21,6 degrees after filter. Diff temp.0,2 degrees. Maybe not drier than?.. A lot of ice on txv valve, first section of evaporator and a lot on suction stop valve on compressor.
    But this pressure readings sounds normal doesent it? (R22 on the system)
    Evaporator pressure 1.1 bar
    Condensator pressure 10 bar
    It is a air condition unit. Room temp 28 degrees. Air outlet of evaporator = 15degrees. That is ok I think. The problems is due to Frost/Ice occuring after some hours running. This block the air passing evaporator. Leads to poor cooling of room.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice building up

    Quote Originally Posted by Karlsen View Post
    Hmm.. Just checked temp before and after filter. Temp before filer 21,8 degrees and 21,6 degrees after filter. Diff temp.0,2 degrees. Maybe not drier than?.. A lot of ice on txv valve, first section of evaporator and a lot on suction stop valve on compressor.
    But this pressure readings sounds normal doesent it? (R22 on the system)
    Evaporator pressure 1.1 bar
    Condensator pressure 10 bar
    It is a air condition unit. Room temp 28 degrees. Air outlet of evaporator = 15degrees. That is ok I think. The problems is due to Frost/Ice occuring after some hours running. This block the air passing evaporator. Leads to poor cooling of room.
    Sounds like an evaporator airflow problem to me. Try cleaning the evaporator coil and the blower wheel.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Sorry Karlsen

    Gary is on the ball

    I missunderstood "suction stop valve"

    If your icing right back to the compressor, your not putting heat into the evaporator = low superheat

    And as Gary said - air flow problem

    everything going wrong tonight, have been doing three things at once

    putting links on here for manuals & now google have locked me out
    If the World did not Suck, We would all fall off !

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice building up

    Quote Originally Posted by chillerman2006 View Post
    everything going wrong tonight, have been doing three things at once
    I know how that works. If I try to walk and chew gum at the same time, I trip over my own feet and choke on the gum.

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by Gary View Post
    I know how that works. If I try to walk and chew gum at the same time, I trip over my own feet and choke on the gum.
    nice one mate

    Put your theory to the test the other day - worked well thankyou

    Got me out of trouble when I was looking at counter

    only had a shreider fitting on suction + had to decant + recharge

    Got all my probes set up as you advised

    charged to 1 degree C subcooling 8 degree superheat, it ran perfect

    cheers

    you might like the links on here mate

    http://www.refrigeration-engineer.co...-york-pac-work
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    I understand, but my last readings after adding 300gram R22 are:
    Suction pressure 1,1 bar = -26 degrees
    Suction temperatur measured with IR-Termometer = -14 degrees.
    This is 12 degrees superheat isn`t it?
    I am thankful for more input to continue troubleshoting. This unit make a lot of ICE... I dont need ICE

  11. #11
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Ice building up

    Ah, suction should be around zero C, 400 divided by 6.92,...Eh, PSi of 57.8... divided by 14.7 is now..3.9 bar on R22. So how does one get ice on suction line with such a low suction pressure?? Did you follow Gary's advice in post above?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  12. #12
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    Ok so Suction pressure is far to low.. I think air flow seems ok, but I can do a survey of kondition of the fan. Evaporator is clean. Other things than low air flow that result in that low suction pressure? Something wrong with TXV maybe?

  13. #13
    Join Date
    Mar 2009
    Location
    piraeus greece
    Age
    71
    Posts
    5
    Rep Power
    0

    Re: Ice building up

    Is the compressor manufacturer or a smart guy has replaced by a biger one??

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice building up

    Quote Originally Posted by Karlsen View Post
    Suction temperatur measured with IR-Termometer = -14 degrees.
    Get a real thermometer (not IR).

    Measure the temperature of the air entering the evap coil and the temperature of the air leaving the evap coil. These measurements should be taken close to the coil.
    Last edited by Gary; 16-08-2011 at 03:14 PM.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice building up

    The difference between entering air and leaving air is the coil's delta-T or dT. Contrary to popular opinion, the pressures are not the most important measurements on the system. Delta-T overrides everything. Unless/until the system has proper airflow through both coils, nothing else matters and all other measurements are meaningless. Always check the airflow first.

  16. #16
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    Manufacturer compressor

  17. #17
    Join Date
    Feb 2011
    Location
    Norway
    Posts
    10
    Rep Power
    0

    Re: Ice building up

    Thanks, will do more research on air flow than..

  18. #18
    Join Date
    Mar 2009
    Location
    piraeus greece
    Age
    71
    Posts
    5
    Rep Power
    0

    Re: Ice building up

    i bielive you have lower temperature outside of the room so you can fix on the condenser fan a speed control to keep the condensator pressure min 16bar

  19. #19
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Ice building up

    This should be fairly easy to solve. Perhaps take another engineer for assistance..

  20. #20
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    19

    Re: Ice building up

    Mr, K N.

    IF POSSIBLE CHECK PRESSURE ON BOTH SIDE OF THE EVO IN & OUT IT SHOULD BE SAME!

    rgds.

  21. #21
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by Gary View Post
    Get a real thermometer (not IR).

    .
    Just throw that IR & listen to Gary

    GET A REAL THERMOMETER

    You cant take temperature with a ir thermometer its just rough guidance on surfaces

    And Jack Diddly on Air

    Or as already told "call an engineer"
    If the World did not Suck, We would all fall off !

  22. #22
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Ice building up

    ok guys sorry to say it but it looks like were all pi**ing in the wind,if u have a suction pressure of 1 bar then check belts and filters if theyre ok ring denco!

  23. #23
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Ice building up

    forgot to mention 1 bar suction 10 bar discharge on r22!!!! its not a vector unit,pressure test it to 28 bar fix leak and run it at 58suction 200 head (4 bar and 16bar) fit a sight glass near the expansion valve to ensure full of liq

  24. #24
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by install monkey View Post
    ok guys sorry to say it but it looks like were all pi**ing in the wind,if u have a suction pressure of 1 bar then check belts and filters if theyre ok ring denco!
    Or failing that its time for "Super Vector"
    If the World did not Suck, We would all fall off !

  25. #25
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by install monkey View Post
    forgot to mention 1 bar suction 10 bar discharge on r22!!!! its not a vector unit,pressure test it to 28 bar fix leak and run it at 58suction 200 head (4 bar and 16bar) fit a sight glass near the expansion valve to ensure full of liq
    You beat me to it !

    If the World did not Suck, We would all fall off !

  26. #26
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Ice building up

    whilst posting, my cake muncher is watching east enders -ur the ian beale of RE haha

  27. #27
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    You might not be so keen when you read the last few on copeland scroll that you missed last night

    Unless you gonna do the taste test anyway !
    If the World did not Suck, We would all fall off !

  28. #28
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: Ice building up

    To diagnose this correctly i will need a bit more detail, but straight away i am concerned with the suction/discharge pressures.

    So to correctly identify i need the following information:

    Suction pressure
    Discharge pressure
    Superheat
    Subcooling
    Full model no of unit (indoor and outdoor)
    Airflow
    Filter condition
    Any ductwork fitted
    Refrigeration charge
    Application (ie data centre etc etc)
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

  29. #29
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: Ice building up

    how old is the unit, gas could be contaminated, mositure, or a break down in a compressor, dirty gas

    also not tryna be patronising, but you charged with 300grams of r22. is the system r22, or 407c?

    if gas charge is ok , and your getting to heat absorbed in evaporator the gas could be bad!

  30. #30
    Rajeev Prasad's Avatar
    Rajeev Prasad Guest

    Re: Ice building up

    1. It could be `cause of either or combination of 2 reasons I understand this to be as overcharge of refrigerant. Please let us know the ambient air temperature around the condenser. Also, you must release some gas from the suction side and check. Also, mention if you find Ice on the compressor body as well.

    2. Please check your expansion valve. Many a times, you`ll find the expansion valve flooding and this will result in such situations.

  31. #31
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Ice building up

    Quote Originally Posted by Rajeev Prasad View Post
    1. It could be `cause of either or combination of 2 reasons I understand this to be as overcharge of refrigerant. Please let us know the ambient air temperature around the condenser. Also, you must release some gas from the suction side and check.
    Rajeev
    Welcome to RE

    Instructing people to release refrigerant to atmosphere is certainly not in line with best practices . Never mind the legal implications.
    We as professionals have an obligation to ensure best practices are adhered to ,be it moral or legal , irrelevant of location .

    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  32. #32
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Ice building up

    weve not had an update since 16/8 so hes either fixed it or blew himself up overcharging it!!

  33. #33
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Ice building up

    Quote Originally Posted by stufus View Post
    Rajeev
    Welcome to RE

    Instructing people to release refrigerant to atmosphere is certainly not in line with best practices . Never mind the legal implications.
    We as professionals have an obligation to ensure best practices are adhered to ,be it moral or legal , irrelevant of location .

    Cheers
    Stu
    Well spotted Stu

    thats probaly why you cant get any cold food/drink from the corner shops here

    R's chillerman
    If the World did not Suck, We would all fall off !

  34. #34
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Ice building up

    Quote Originally Posted by chillerman2006 View Post
    Well spotted Stu

    thats probaly why you cant get any cold food/drink from the corner shops here

    R's chillerman
    No comment !!

    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  35. #35
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: Ice building up

    doyour job properly or get a professional.


    de gass the split!!! pressure test and triple vac!!! its sounds like you have a blockage if you arent having airflow issues. while on pressure test clean condensor coil and evaporator!!!! if your throwing 300gramm of r22 in you shouldnt be working on the unit imo, perhaps 15 years ago, not these days

  36. #36
    fercmal2's Avatar
    fercmal2 Guest

    Re: Ice building up

    dear sirs

    i am not a reefer technician but my situation warrants an immediate solution so i seek your professional help.15102011257.jpg

    we have done initial precooling to -20C before loading the -18C products. however after 20 hrs of cooling only -9C was reached, compressor covered in ice and sight glass white with bubbles. shud i unload and return to the cold stores? kindly advise

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Ice building up

    Quote Originally Posted by fercmal2 View Post
    dear sirs

    i am not a reefer technician but my situation warrants an immediate solution so i seek your professional help.15102011257.jpg

    we have done initial precooling to -20C before loading the -18C products. however after 20 hrs of cooling only -9C was reached, compressor covered in ice and sight glass white with bubbles. shud i unload and return to the cold stores? kindly advise
    Defrost it.

  38. #38
    fercmal2's Avatar
    fercmal2 Guest

    Re: Ice building up

    thank you very much. will do so as advised