Hydraulic Lock/Exploding Pipework
Everyone who is not aware of Hydraulic Lock - should be
from the pics you can see this could have caused some-one serious harmLast edited by chillerman2006; 10-09-2011 at 05:09 AM.
If the World did not Suck, We would all fall off !
-
11-08-2011, 01:38 AM #2
Re: Hydraulic Lock/Exploding Pipework
A potential/ constant problem in industrial systems with sub cooled liquid lines. The power of warming liquid will split wide open a steel walled pipe.
-
11-08-2011, 01:47 PM #3
Re: Hydraulic Lock/Exploding Pipework
the cause behind this rupture was a fault with the expansion valve & a mistake by the customer
the circuit pumped down creating a fault alarm on the bms, so the customer decided as he had an a/c engineer attending site to carry out maintenance he would be able to rectify the problem more cheaply than my own company
the liquid line valve was closed by the engineer and was not re-opened
leaving subcooled liquid trapped between the two valves
within an hour of the engineer leaving site the trapped liquid's temperature rose & boom
It made such a bang that it was heard by the customer from his office
who needless to say learned very quickly - horses for courses
If the World did not Suck, We would all fall off !
-
12-08-2011, 05:19 AM #4
Re: Hydraulic Lock/Exploding Pipework
Hi Chillerman 2006,
I think your client has just become a captive listener, and afreind for life.
-
12-08-2011, 09:55 AM #5
-
26-08-2011, 11:37 PM #6
-
29-08-2011, 08:17 AM #7
Re: Hydraulic Lock/Exploding Pipework
You've obviously been miss-informed, I have had the site now for past 6 years & no-one is allowed near the plant on the roof anymore, there are 12 units totalling just under 5mw of cooling & even though they do their own coil cleaning, I have to be there ! cctv has also been installed ! It is as I said 'horses for courses' you may run rings around me doing a/c installs but your still be at the starting gate when I have finished on this sort of kit. About time we see some of your work pics annit or even a video, explaining how they work, I may even learn something !
If the World did not Suck, We would all fall off !
-
29-08-2011, 10:15 AM #8
Re: Hydraulic Lock/Exploding Pipework
col-i was highlighting the choice of of word-horses- as you say chillers yep-blackmans magic-i can work on em ,change compressors and **** but as for stripdowns,stuff that.
i did an install on sat did 4 flares and didnt **** up haha-will get some pics up-not of me mrs though too many pink pixels haha
-
29-08-2011, 10:22 AM #9
-
29-08-2011, 11:47 AM #10
Re: Hydraulic Lock/Exploding Pipework
The piping schedule seems pretty thin, I must say.
If the correct wall thickness is used, then the piping should have a burst pressure of around 70 bar(g), unless fully annealed. Even then, I'd expect an expanding liquid to be less than this. Would be very interesting to do the calculations on the evolved pressure.
Interesting.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
29-08-2011, 11:59 AM #11
Re: Hydraulic Lock/Exploding Pipework
If the World did not Suck, We would all fall off !
-
29-08-2011, 12:02 PM #12
Re: Hydraulic Lock/Exploding Pipework
doubt it the scrap monkeys will have had it off!!!!
-
29-08-2011, 01:27 PM #13
Re: Hydraulic Lock/Exploding Pipework
If the World did not Suck, We would all fall off !
-
29-08-2011, 01:36 PM #14
Re: Hydraulic Lock/Exploding Pipework
we had to rip out 10x 3m lengths of 800a bus bar track each section weighed 70kg. full of copper bar and about 10kg of plastic/aluminium.we stripped it out and stacked it all up. the customers electrical contractors weighd it in,the project manager went apesh*t accusing us of having it off,luckily theres more cameras in a debenhams loading bay than stock so my arse was covered!! yay the joys of cctv