AHU condensation problem
Hello,
We ve just had a A.H.U. installation with a downflow configuration with raised floor.
After installing the unit, and during commissioning, when turn it on we have noticed condensation driping from the Drain Pan.
I may have to mention here that the raised floor has not yet being installed. Condensation maybe relevant to this? (i.e. air turbulance?)
Any advice welcome.
thanks
-
10-08-2011, 10:39 AM #2
Re: AHU condensation problem
hi zenen,
is the drip tray piped up? is there a pee trap on the vertical pipework? is the air volume making the condence water splash over the drip tray? is it condenceation on the drip tray , or is it leaking ?
happy hunting = sedgy
-
10-08-2011, 01:37 PM #3
Re: AHU condensation problem
Assuming unit is level, a p-trap must be correctly installed to ensure water flow out of condensate pan.
-
01-09-2011, 10:27 AM #4
Re: AHU condensation problem
check the air velocity leaving the coil,if it exceeds 1.8 m/s in ANY place condensate will carry over.Fan speed & proximity to coil can influence this; good luck!
-
01-09-2011, 12:21 PM #5
Re: AHU condensation problem
Forgot the F'n Flare NUT. Welcome to Refrigeration Engineer. Think we can shorten your name to... ah., FFN, ' how's that? So, which part of Australia are do you live?.. Mike.
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
-
01-09-2011, 12:33 PM #6
Re: AHU condensation problem
air volume making the condence water splash over the drip tray, i believe was the problem. After the raised floor installed we have no condensation problems.
thanks everyone
-
04-09-2011, 01:20 PM #7
Re: AHU condensation problem
Beers 2 you Mike,currently in Albury/Wodonga but formerly from Cairns (1987-2007) Still got maroon blood!
-
04-09-2011, 01:33 PM #8
Re: AHU condensation problem
is that "for goth flarenut" or abbreviated?
just out of intrest what is the sucess rate of your flares? i did 6 this week first time and im wondering if i am a flare jedi? have u ever forgot the flare nut or put the flare the wrong way ?haha
-
05-09-2011, 11:15 AM #9
Re: AHU condensation problem
what flares have to do with condensation, I dont understand...
-
05-09-2011, 12:48 PM #10
Re: AHU condensation problem
abbreviated,dear monkey!and yes,after 30 years I still occasionally forget the freaking flare nut!!!
as to your previous assertion,a true flare jedi would never boast of his prowess!
-
07-09-2011, 06:27 AM #11
Re: AHU condensation problem
again.... what flares have to do with condensation mate?
-
07-09-2011, 01:20 PM #12
Re: AHU condensation problem
zenen,I apologise for hijacking your post.I'm new to this forum(and forums as a whole) flares have nothing to do with condensation in this case,and i should continuue in the chat area,glad to hear you resolved your issue.
Cheers,FFN
-
17-09-2011, 03:30 AM #13