    correct running pressure/temperature formular



    Hi all, I need your help, I'm confused, can you please tell me if there is a formular I can use to work out the correct running pressure/temperatures of any refrigerant system I may come across in the field, ie 407c, 410a, 22, 404a, 134a. If I have a r22 split and a r22 freezer both running correctly, will they both have the same hi/lo pressure/temperatures or does it vary upon application? thanx for your time, please exsplain as if you are talking to a baby so I can fully understand, cheers



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: correct running pressure/temperature formular

    Hi Daniel

    temps/pressures vary

    suction pressure will relate to the evaporater temp
    suction temp will relate to superheat
    discharge pressure relates to suction pressure & ambient temp
    discharge temp relates to the compressors abillity to do work
    liquid line temp relates to subcooling

    A good place to start is

    http://prostores1.carrierzone.com/se...com/StoreFront
    If the World did not Suck, We would all fall off !