    EEV open 260%



    Hi just a quick question, I have come across a chiller that has a electronic expansion valve open at 260% it's on a mcquay chiller, i've not really had much experience with the mcquay, is this valve defective



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: EEV open 260%

    Is the valve open in percentage terms (%) or is it in pulse steps?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: EEV open 260%

    The joys of electronics.
    The processor is possibly looking at suction Pressure and coil temperatures and a dozen other things and is indicating % of valve rated capacity, particually on pull down.