  1. #1
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Walk-in freezer + multideck problem, please help!



    Hi,

    I have a faulty walk-in freezer in a shop, haven't inspected properly yet, I just kind of want to prepare myself for the possibilities.
    Symptomps are: About 12.5 bar pressure in both suction and discharge line while compressor is running. No signs of evaporator getting colder or condenser warmer, sight glass is clear, no signs of liquid.
    Is it a faulty expansion valve? Or can it be compressor fault? What is the method of fault-finding?

    Other issue: 2 Multideck just don't want to go below 8-9 degrees. I suspected that its because of poor ventillation, so we put extra fans behind and more space from the wall. It went down a littlebit but not good.
    Suction line pressure is 4.2 bar. What should I check on them? What would be the correct pressure?

    Any ideas please?



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Problem 1. about 12.5 high and low side probaly nitrogen in system not refrigerant, + no pressure change when running = compressor is not pumping

    You need to call an engineer

  3. #3
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Should the pressure change when its filled with nitrogen?

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Yes

    I could go into detail but I will not apart from confirm the obvious

    reasons

    1. I'm doing a fellow engineer out of work feeding you info

    2. (most importantly) leave it alone before you hurt yourself, if thats nitrogen and that compressor had worked your pipework or part of the system could have burst

    Its all well and good helping someone build a coldroom but not to work on a system

  5. #5
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    20

    Re: Walk-in freezer + multideck problem, please help!

    If your suction pressure is about the same as your discharge then you could have a broken
    crankshaft, broken valves or a leaking pressure relief valve. The compressor may run smooth if
    the crankshaft is broken. A compressor valve check can be done by pumping the compressor
    down. If it will not pump down, or pumps down slowly, one or more suction valves may be bad.
    If the compressor pumps down and off but the pressure on the suction side rises rapidly, one or
    more discharge valves are bad, the pressure relief valve is leaking, or you have a blown gasket

    http://www.brainerdcompressor.com/_pdf_files/Why2.PDF

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by passandscore View Post
    If your suction pressure is about the same as your discharge then you could have a broken
    crankshaft, broken valves or a leaking pressure relief valve. The compressor may run smooth if
    the crankshaft is broken. A compressor valve check can be done by pumping the compressor
    down. If it will not pump down, or pumps down slowly, one or more suction valves may be bad.
    If the compressor pumps down and off but the pressure on the suction side rises rapidly, one or
    more discharge valves are bad, the pressure relief valve is leaking, or you have a blown gasket

    http://www.brainerdcompressor.com/_pdf_files/Why2.PDF
    have you read the 12.5bar and fact this fella is not an engineer
    Last edited by chillerman2006; 08-08-2011 at 01:27 AM. Reason: too many emoticons

  7. #7
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Yeah, you know, I've seen your "fella" working on our refrigeration..
    Once:
    -Compressor changing, no access valve:
    -Cutting off end of the pipe, 1.5 kg of fefrigerant (R404A) goes to the atmosphere... good advice: put gloves on the fire alarm, it might start the system.
    Another:
    -Regassing a chest freezer, no access valve.
    -Fellas solution: cut off pipe ends, 0.8 kg of R134A goes to the atmosphere.
    -My question: Isn't it harmful for the health or something?
    -Solution: We can pull it out to the air.
    I just said leave it, but felt really wrong.

    After that, I've done my C&G 2079 in category 1 with 90% passing mark. Since that I have installed a walk-in fridge+freezer and changed a seized compressor. Once I stripped down a huge walk-in and regassed a lot of them successfully. Never ever in my life reliesed more than the allowed level of refrigerant to the air (remaining pressure in an equalised gauge), storing and keeping track of every gramm of refrigerants I have, including rubbish, recycled and new.

    By the way, the fella who I was mentioned, working for a huge 100% British firm, covering all London, 20 years in the industry. Don't even want to imagine how much damage did they cause for our planet...They charged £1500 for changing a compressor and min.£200 for regassing, depending on the amount of refrigerant the system needed.

    I know that you are trying to keep the secrets what you have learnt in so many years in school, and then practised in the industry, but it doesn't mean that without 4 years of higher education you have no chance to learn it by your own initiative. Considering that I have already have a higher engineering diploma in electrical and mechanical engineering.

    I was hoping that you guys can make it easier to learn, and do quality job instead of what I've seen in practice, but all I can see here is huge concrete walls, no real help.

    Thanks for reading, if you did. Sorry for my accent, I'm working on it.

    Attila

  8. #8
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Sorry, Mr. Mighty Engineer. Thank You.

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Sorry, did not mean to offend was just looking out for your safety

    we have had the discussion about 2079/J11 many times now and the conclusion is they may as well give them out in xmas crackers

    If you could not work out what equalised running pressures are you have NO 2079

  10. #10
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    By the way, thank you very much for the information. I will study in the meantime and will try to figure out what happened.
    I hope that you don't think that these informations shouldn't be shared with starters like me.

  11. #11
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Ok, I'm sorry as well, I didn't want to offend you.
    I was just scared of writing anything because of answers like this.
    You know, its pretty hard to learn these things in a foreign language.
    I just want to make everything sure.

  12. #12
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    I have no problem helping any engineer what ever there level

    Your original post clearly shows that you chanced running a system that could have caused you harm

    Best thing you can do is recover the refrigerant and pressure test with oxygen and check for leaks, when you have done that come back and I'll talk you through all the other not to do's

  13. #13
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    I have chanced runnining the compressor, because it was attached together with a fridge, it was live, switching it on was just a touch of a button. If its filled with any other than refrigerant it should be marked and switched off. But now I know I should'nt, you're right. And I won't.

    Tomorrow I will evacuate and have a closer look.
    Thanks

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    have you read the 12.5bar and fact this fella is not an engineer
    If we don't know what refrigerant is in the system, then the 12.5 bar is meaningless.

  15. #15
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Gary View Post
    If we don't know what refrigerant is in the system, then the 12.5 bar is meaningless.
    It will be either, R22, R404a or a refrigerant of similar pressure

    Holding charge of nitrogen is only suspect

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Setting aside the possibility of R410A, given R22 or R404a (R507?) the 12.5 bar could conceivably reflect the ambient temp... or even high indoor temp.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Hmmm... maybe it's stuck in electric defrost mode?

  18. #18
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Gary View Post
    Setting aside the possibility of R410A, given R22 or R404a (R507?) the 12.5 bar could conceivably reflect the ambient temp... or even high indoor temp.
    I can see what your thinking here mate just you will not find R410a in a counter over here and unfortunatly for us we dont have your glorious Florida weather

    The norm here is 22 or 404

  19. #19
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Its 404A. Both the mul;tideck and the walk-in freezer as well.

  20. #20
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Well, actually I was reading back, and I realised that oil coming from the service valve indicates a compressor fault.
    This is exactly what happens, a huge amount of oil coming out when I'm connecting or disconnecting the gauge...

  21. #21
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Walk-in freezer + multideck problem, please help!

    A low run current can also point to a compressor thats not pumping,

    http://www.youtube.com/watch?v=FEtYI_OIHok

    I have two units side by side so am comparing a good one with a bad one, high side gauge is actualy on the suction of the good comp.

    Jon
    Mostly found in Oxfordshire, UK :)

  22. #22
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    Best thing you can do is recover the refrigerant and pressure test with oxygen and check for leaks, when you have done that come back and I'll talk you through all the other not to do's

    Doh!

    Or was that a test. :-)
    Health and safety first..........unless I'm in a hurry.

  23. #23
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Tayters View Post
    Doh!

    Or was that a test. :-)
    No, a method of making a bomb!

    Blow the coldroom up, no more problems

  24. #24
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by mad fridgie View Post
    No, a method of making a bomb!

    Blow the coldroom up, no more problems
    Thought my eyes were playing tricks on me but..NO.. there it is in black and white. Lets NOT use oxygen for pressure testing..Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  25. #25
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    I think the best thing to do when Joe Public come on here making claims that appear to be false is to contact the regulators and let them deal with it

    If we dont start police-ing the industry ourselves, there will never be any improvement

    F-Gas Support their number is = 0161 874 3663

  26. #26
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    I am happy to show my certificate to anyone who wish to see.
    I've done it in Ellis Training, took 1 week.
    Actually this reflects to the problem: in 1 week I'm not gonna be a refrigerator engineer, and I don't really want to be. I am maintaining equipments and I want to be able to fix fridges for the company who I work for.

    I am able to handle refrigerants in a safe way, and thats important.
    And want to learn as well.

  27. #27
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    I think the best thing to do when Joe Public come on here making claims that appear to be false is to contact the regulators and let them deal with it

    If we dont start police-ing the industry ourselves, there will never be any improvement

    F-Gas Support their number is = 0161 874 3663
    It would seem the JW has got his cert, and good on him, but it shows what a mockery simple courses make of our industry.
    There is nothing wrong with learning and everybody has to start somewhere. How much support we give does depend upon how you see each question.
    In this case i do think the cart is before the horse, and that JW should perhaps work with others first, instead of jumping in feet first!

  28. #28
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Johnny Walker View Post
    .
    Actually this reflects to the problem:.
    Your quite right it does, it reflects the problem with the new F-Gas Certs

    Anyone can get one and as I posted previously they should give them out in Xmas Crackers

    From your Original post it clearly shows, you are a danger to yourself and should not be working on equipment unsupervised

    This is not a direct dig at you but more so a dig at the state of the industry and the incompetance that is being allowed in

    It is absolutely ridiculous that a training course is available that allows individuals to gain a qualification in one week, deeming them competant when they clearly don't have a clue

  29. #29
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Atilla

    I'll show you mine if show me yours joke

    I can not be that far from you and if you like,

    Send me a private message with a contact number and this Saturday I have nothing better to do, so if your buying lunch I'll come down for the day and guide you through as much as I can

    It's only 1 day, but at least its 1 day more than the week you've had and you never know we might both learn something

  30. #30
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Thank you.
    I will send you a private message as soon as I have some time to write.

    I'm really sorry about the bad introduction, I didn't meant to be rude...

  31. #31
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Johnny Walker View Post
    Thank you.
    I will send you a private message as soon as I have some time to write.

    I'm really sorry about the bad introduction, I didn't meant to be rude...
    No problem

    You cant get ruder than me once I'm off

    Look forward to hearing from you

  32. #32
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    Your quite right it does, it reflects the problem with the new F-Gas Certs

    Anyone can get one and as I posted previously they should give them out in Xmas Crackers

    From your Original post it clearly shows, you are a danger to yourself and should not be working on equipment unsupervised

    This is not a direct dig at you but more so a dig at the state of the industry and the incompetance that is being allowed in

    It is absolutely ridiculous that a training course is available that allows individuals to gain a qualification in one week, deeming them competant when they clearly don't have a clue
    As I understand it, this is a material handling certificate and nothing else. It's intent is to qualify people to purchase and transport refrigerant... and nothing else. So... why does it take a weeklong course? During that week, they teach people just enough to be dangerous. They should be teaching people how to transport refrigerant from point A to point B... and nothing else.

    I have no problem at all with teaching refrigeration to anyone who wants to learn... but it should not be part of the material handling certification training.

  33. #33
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    Best thing you can do is recover the refrigerant and pressure test with oxygen and check for leaks, when you have done that come back and I'll talk you through all the other not to do's
    Speaking of teaching people just enough to be dangerous...

    I understand this is a joke, but someone may take it seriously. We should probably refrain from killing people... not funny.

  34. #34
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Johnny Walker View Post
    I am happy to show my certificate to anyone who wish to see.
    I've done it in Ellis Training, took 1 week.
    Actually this reflects to the problem: in 1 week I'm not gonna be a refrigerator engineer, and I don't really want to be. I am maintaining equipments and I want to be able to fix fridges for the company who I work for.

    I am able to handle refrigerants in a safe way, and thats important.
    And want to learn as well.
    Start here:

    http://www.refrigeration-engineer.co...rigeration-101

  35. #35
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Gary View Post
    It's intent is to qualify people to purchase and transport refrigerant....
    There's alot more to it than that

    Incuding

    BS EN378 2008
    Montreal Protocol
    Kyota Protcol
    Pressure testing
    Strength testing
    Charging
    Recovering
    SCT/SST
    Superheat
    Subcooling
    Brazing
    earths atmosphere
    Electromagnetic + Ultraviolet radiation
    COSHH
    Health & Safety at work Regs 1999
    Institute of refrigeration - Code of Practice
    Leak detection
    PPE

  36. #36
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Gary View Post
    Speaking of teaching people just enough to be dangerous...

    I understand this is a joke, but someone may take it seriously. We should probably refrain from killing people... not funny.
    Joke - of course

    From the above list you can see that in order tobe legal in the UK/EU you have to pass and prove compentent to carry out pressure testing

    If you can not, you fail and in affect are breaking the law by working on the system...

    How's it work your side of the pond ?

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by Johnny Walker View Post
    Actually this reflects to the problem: in 1 week I'm not gonna be a refrigerator engineer, and I don't really want to be. I am maintaining equipments and I want to be able to fix fridges for the company who I work for.
    Make up your mind. Do you want to maintain the equipment or fix it? If you want to maintain it, you should not have a set of gauges. Maintenance is limited to the air side of the system.

    [begin rant]

    While we are on the subject, it is my belief that apprentices should demonstate a very high level of expertise on airflow problems over a long period of time before they are allowed to use gauges. I have seen waaaaaaay too many people put gauges on the machine before checking for airflow problems. I just want to reach out and smack them, while screaming in their ear, "CHECK THE AIRFLOW FIRST, STUPID".

    [/end rant]
    Last edited by Gary; 08-08-2011 at 04:16 PM.

  38. #38
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    Joke - of course

    From the above list you can see that in order tobe legal in the UK/EU you have to pass and prove compentent to carry out pressure testing

    If you can not, you fail and in affect are breaking the law by working on the system...

    How's it work your side of the pond ?
    About the same. We have our fair share of idiots on this side of the pond, too.

  39. #39
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    I have no problem helping any engineer what ever there level

    Your original post clearly shows that you chanced running a system that could have caused you harm

    Best thing you can do is recover the refrigerant and pressure test with oxygen and check for leaks, when you have done that come back and I'll talk you through all the other not to do's
    Please tell me the oxygen comment is a joke!!

  40. #40
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    Joke - of course
    Just to make clear to anyone not qualified

    If you attempt to pressure test with OXYGEN YOU PROBALY KILL YOURSELF

  41. #41
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by chillerman2006 View Post
    There's alot more to it than that

    Incuding

    BS EN378 2008
    Montreal Protocol
    Kyota Protcol
    Pressure testing
    Strength testing
    Charging
    Recovering
    SCT/SST
    Superheat
    Subcooling
    Brazing
    earths atmosphere
    Electromagnetic + Ultraviolet radiation
    COSHH
    Health & Safety at work Regs 1999
    Institute of refrigeration - Code of Practice
    Leak detection
    PPE
    Clearly, it's all about propaganda... that's fine. Keep it about propaganda and stop teaching people to install gauges.

  42. #42
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Walk-in freezer + multideck problem, please help!

    this has to be the most pointless thread i have ever read

  43. #43
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by coolhibby1875 View Post
    this has to be the most pointless thread i have ever read
    Yet..You choose to join in and keep it going

  44. #44
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Walk-in freezer + multideck problem, please help!

    Quote Originally Posted by coolhibby1875 View Post
    this has to be the most pointless thread i have ever read
    And your point is... ??????

  45. #45
    Join Date
    May 2011
    Location
    UK
    Posts
    35
    Rep Power
    0

    Re: Walk-in freezer + multideck problem, please help!

    Just to finish this thread:
    The problem is solved. After measuring the multideck it had a high subcooling and low superheat so it was slightly overcharged. It had only suction valve so we had to remove all the refrigerant (R404A) and recharge it. It works fine.
    (And finally I learned how to regass properly and what to look for when taking measures as they don't really explain things on short courses...)

    The freezer's compressor is burnt, the oil smells terrible...
    A new compressor alone would cost £650 while I received a quote for a brand new system for £1300. They will decide on tuesday if they go for compressor or all system will go.

    Extra thanks for Chillerman2006