    Electric Defrost loads on Compressor configuration



    Hello, I'm a newbee (non-engineer), and currently ordering some condensing units. I was asked what the loads(V and Amp) were for the electric defrost.

    Can anyone explain how the electrical loads on the refrigeration cases will affect the Compressor function? Since they are on different power sources(120 vs 220), it seems odd to me.

    Thanks for the help.

    Bryan



  2. #2
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Electric Defrost loads on Compressor configuration

    Hi Bryanwa

    You should find the compressor cycles OFF during defrost

    When the defrost ends and the compressor restarts it will be under additional load from the heat of the hot evaporator, drawing more amps

    As the evaporator temperature drops so does the suction pressure which in turn lowers the load on the compressor and the amp draw

  3. #3
    bryanwa's Avatar
    bryanwa Guest

    Re: Electric Defrost loads on Compressor configuration

    Thank you Chillerman! That makes total sense now.

  4. #4
    Join Date
    Jul 2010
    Location
    Brazil
    Age
    46
    Posts
    12
    Rep Power
    0

    Re: Electric Defrost loads on Compressor configuration

    Hello,

    I wonder what is the optimal duration and period for electric defrost chamber -25 ° C.


    Thank

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,908
    Rep Power
    30

    Re: Electric Defrost loads on Compressor configuration

    Quote Originally Posted by Roberto Cancio View Post
    Hello,

    I wonder what is the optimal duration and period for electric defrost chamber -25 ° C.


    Thank
    Hi Roberto

    Defrost should be terminated by temperature and backed up with a timer in case the klixon fails

    How often is going to depend upon how often the evaporator starts to ice & restrict air flow

    You can set a timer to suit your needs or better still use a differential air switch
    If the World did not Suck, We would all fall off !

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Electric Defrost loads on Compressor configuration

    Hi Bryanwa,
    the case manufacturers with specify the heating/defrost power requirements. Example 3 phase 220vac x 3 x 60Hz,, 120vac x 1 x 60Hz., xyz watts. How they configure the elements will be prewired before delivery. Some suppliers can have star connected with 3 phase for low voltage, others across the line for high voltage. Or single phase . They will always state Amps supply and voltage supply.
    Defrost frequency per 24 hours will effect actual refrigeration requirements, while defrosting the system is not cooling, so selection of condensing units is critical. Defrost loadings has to be added to total loadings per 24 hours, compressor run times etc..
    Example: Low temp case @ -18'C holding. calculated loading per 24 hrs 500Kw + [ 6 defrost per 24 hrs @ 60 minutes per/5Kw per defrost] 30 kw + 10% safety margin = 500 + 30 + 530/10 = 583 Kw. Required run time = 16 hours per 24. So 583/16 = 36.50 Kw refrigeration capacity minimum required.
    Hope this helps