Thread: Package units commissioning
-
04-08-2011, 12:27 PM #1
Package units commissioning
Dear fellow experts,
I have a package unit with downflown configuration, (raised floor 600mm), connected with an external condenser unit.
Refrigerant piping is 1, 3/8 & 7/8 no longer than 10meters. Refrigerant charge is around 24kg.
Design pressure test is at 24bar.
What pressure test would you advice that I use. 30bar or 40bar? and how long...lets say for 24hrs?
thanks,
Z
-
04-08-2011, 01:35 PM #2
Re: Package units commissioning
no more than 24bar
-
05-08-2011, 02:46 AM #3
Re: Package units commissioning
1.5 times the normal working pressure and below any safety releif valves, for 24 hours.