Effect of Suction Super heat in flooded evaporator using Ammonia
Dear all,
hello
i want to ask what is the effect of Suction Superheat in flooded evaporator using ammonia ?
does it same as in case of dry evaporator ?
how to handle it if i have a manual expansion valve ?
-
22-01-2012, 09:17 AM #2
Re: Effect of Suction Super heat in flooded evaporator using Ammonia
pushcar, no superheat on this type of system.
Liquid recirculation or overfeed has a rate of example 4 to 1
4 kg of refrigerant sent to evaporator, 3 comes back as liquid & 1 kg converted to saturated gas.
No real superheat is measured, only air on/off temps as per design or if surge drum, correct level is achieved
by approx liquid feed solonoid on 70% of the time under full load conditions. Set manual expansion valve to meet above requirments.
-
22-01-2012, 05:46 PM #3
Re: Effect of Suction Super heat in flooded evaporator using Ammonia
There was a really good thread on this sometime back.
http://www.refrigeration-engineer.co...hlight=brining
US Iceman wrote a paper on this. One of the best I have read. It is on the Internet, and a link is probably in the thread. I have it on my computer and will find it sooner or later.
-