    I need cold storage for wine.
    11,000 sq. Ft.
    24' ceilings with R30
    Walls 6" concrete tilt up
    Maintain 55 degrees F
    Will be used as a packing and shipping area
    Would like to use AC system but my hvac contractor says that would be t low of a temp.
    Looking for a design and information.
  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,451
    Rep Power
    41
    Re: Warehouse wine storage
    Leo
    Send on a cheque and a return ticket i'll be right over!!
    Your contractor is right 55f (13c) is too low for standard air con, you need a good refrigeration company to specify and design for you, there are a few posting here, may be able to point you in the right direction.