Results 1 to 4 of 4
  1. #1
    Join Date
    Nov 2010
    Location
    Lemesos
    Age
    46
    Posts
    11
    Rep Power
    0

    Pressure transmitter , connection?



    hi,

    We have installed a DX AHU, with external condensers.

    On the condensers we ve got a Pressure Transmitter which needs to be installed on the suction line (according to manuals) to read refrigerant line pressure and operates Fans accordingly.

    From what I know, pressure transmitter converts pressure into linear electrical output signal.

    So in a few words, depending on the pressure of the refrigerant pipe line the condenser fans starts and stops accordingly.

    True?

    thanks,

    Z



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Pressure transmitter , connection?

    if your transducer is controlling the condenser fans then it should be fitted on the (thinner) liq line sometimes on the discharge line too,check the installation manual or if in doubt fit a schraeder stubb on both lines incase u have problems when comissioning

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Pressure transmitter , connection?

    Hi, Zenen

    Quote Originally Posted by zenen View Post
    hi,

    We have installed a DX AHU, with external condensers.

    On the condensers we ve got a Pressure Transmitter which needs to be installed on the suction line (according to manuals) to read refrigerant line pressure and operates Fans accordingly.

    From what I know, pressure transmitter converts pressure into linear electrical output signal.

    So in a few words, depending on the pressure of the refrigerant pipe line the condenser fans starts and stops accordingly.

    True?

    thanks,

    Z
    Yes, you are right, to keep condensing pressure constant you have to install pressure transmitter on condenser's gas header, close to inlet into your condensers.


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Nov 2010
    Location
    Lemesos
    Age
    46
    Posts
    11
    Rep Power
    0

    Re: Pressure transmitter , connection?

    thanks guys. it is fitted on the high pressure pipe line and controlling the fans just fine.

    Cheers