    Hi guys!
    I need some help here. My SABROE compressor, R404A refrigerant is having high discharge temperature. I already did the descaling of the condenser tubes because there was no delta T between the inlet and outlet of the cooling water. After the descaling the delta T of the cooling water is just 2 degree C and the discharge temperature remains 80 degree C.
    Apr 2010
    pakistan
    38
    5
    Re: High discharge temperature-SABROE compressors
    Dear
    Your system has some non condensable gasses and purge some air from your system till the normal discharge pressure of your compressor or condenser.
    Regard,
    Abid Ameen
    Abid.ameen@dec.com.pk
    Jul 2011
    Malaysia
    7
    refrigerant overcharge maybe?
    low delta t mean high water flow rate.
    3,357
    Reighman,
    Is it a screw or reciprocating compressor?
    If its a screw what is oil temp & others pressures, temps etc?