    R600a refrigerant system.



    Hey guys, if i going to design a refrigeration system using R600a, how do i calculate all those ,length and size for capillary tube and condenser if i already had the spec for compressor and evaporator?



  2. #2
    Join Date
    Aug 2011
    Location
    Malaysia
    Age
    35
    Posts
    8
    Rep Power
    0

    Re: R600a refrigerant system.

    Please Help!!!

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: R600a refrigerant system.

    Would this be any help?

    http://www.danfoss.com/businessareas...ils/dancap.htm

    I fix them not make them so wouldn't have a clue personally how to size a cap tube.

    Jon
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Aug 2011
    Location
    Malaysia
    Age
    35
    Posts
    8
    Rep Power
    0

    Re: R600a refrigerant system.

    thx a lot, but how about the condenser? any idea?

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: R600a refrigerant system.

    I would think you need a condenser with the same or sligthly bigger heat rejection than your systems cooling load at the ambient temperature it will be running in.