    Daikin VRV 111 2 Pipe replacement Technology



    The guys on site have installed a Daikin vrv 2 pipe replacement technology system.
    Went to pressure test the weekend and wasn't getting a reading back on suction side!
    Checked gauges ,lines and valves.
    Checked flare nuts on fcu along system to see if nitrogen was present(ALL OK)
    I am wondering if the indoor units have solinoid valves in fcu and if power was applied to indoor unit or units they would close ?
    Any help would be appreciated.
    Regards



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV 111 2 Pipe replacement Technology

    only if it was powered up prior to pressure testing,u can drive the valves open on the outdoor unit in the setting mode