Results 1 to 6 of 6
  1. #1
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Bristol 2 speed comps



    Hi Guys,

    Got a Bristol two speed compressor to fit in place of a single speed next week, its the same duty when run on high speed.

    Anyone know how these things are wired up, i believe the motors can work on either 2 or 4 poles depending on how its connected.

    Cheers Jon


    Mostly found in Oxfordshire, UK :)

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Bristol 2 speed comps

    Jon.
    Are you sure you don't mean Dual Voltage?
    Series A + BG series?
    Basically they are wired as stand alone or in tandem.
    I will email some details.
    Grizzly

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Bristol 2 speed comps


  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Bristol 2 speed comps

    Cheers Guys! Looks like i have to link the low speed terminals together, and just power the high speed ones off the three phases.

    I've got a delay timer i shall fit too as i think the old one died due to cycling on the lp as its got a leak on the condenser.

    Jon
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Bristol 2 speed comps

    Hi Jon.
    The attached should help?
    Bristol do indeed recommend using a time delay to prevent comp short cycling.
    Grizzly

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Bristol 2 speed comps

    Thanks Grizzly!

    I've got no excuse now not to go and fit it!

    I've got a IMO timer that i think i can wire into the CCH feed so that once the comp goes off it starts counting down till it will allow a restart, or i might be able to get a feed from the lp/hp switch if its one of those dual ones with the four connections.

    Cheers Jon
    Mostly found in Oxfordshire, UK :)