    LG Dry Contact Issue



    Hi all,

    Im working with 3 units and fitting an LG PQDSB to each indoor coil to switch a booster fan. (The indoor units are MB09AHL's)

    Connected to the CN-CC port on the main board, as per the manual - but no life from the board.

    I could believe a faulty board, but not 3, and not on every unit!
    Is there something I've to do on the controller to enable these boards?

    Cheers

    Scott



  2. #2
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: LG Dry Contact Issue

    i pressume you are adding a fresh air fan in to system if so scroll controller to 2nd option and authorize it