    Condensor split temperature



    I encountered already several times in literature the term ' Condensor split temperatures' What does this mean because I never heard of it before and can't find it in the books I have.


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Mar 2001
    Location
    Otsego, MN
    Age
    52
    Posts
    22
    Rep Power
    0

    Re: Condensor split temperature

    I could be wrong, but when I hear condenser split temp, I think of the ambient temperature where we shut down half the condenser. This being the condenser split temperature.

    Norty

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Condensor split temperature

    hi peter,

    condenser split temp is the diference between the air temp entering the coil and air temp leaving the coil.

    There is also an evaporator split temp.


    Chemi

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Condensor split temperature

    3 different answers now.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Condenser split temperature

    Mine is the right one ,

    Of course

    I saw it in commissioning forms on the web, so it must be true.

    have a go yourself:
    http://www.google.com/search?sourcei...it+temperature

    Chemi

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Condensor split temperature

    Copied an pasted

    Splits, Swings, And Loads
    In air-cooled condensers, the temperature difference between the ambient and the condensing temperature is referred to as the condenser split. For example, if the condensing temperature is 110 degrees F and the ambient is 80 degrees, the condenser split would be 30 degrees.

    (The condensing temperature in any system is figured off of the condensing pressure using a pressure-temperature chart.)

    Condenser splits can range from 15 degrees to 30 degrees, depending on whether the condenser is a standard-, mid-, or high-efficiency unit. The higher the efficiency, the more coil surface area there will be, thus the lower the condenser split will be.

    In this article we will discuss a standard-efficiency condenser that normally runs a 25 degree to 30 degree split. Note that condenser splits are not affected by ambient temperature changes. If there is an increase in the ambient temperature, there will also be an increase in the condensing temperature, but the condenser split (difference between the two temperatures) will remain the same.

    On the other hand, condensing temperatures for a single condenser can vary depending on two factors: the ambient swing and the evaporator heating load.

    As the ambient temperature increases, less heat can be rejected from the air-cooled condenser to the hotter ambient. Therefore, more of the heat absorbed by the evaporator and suction line, as well as the heat of compression generated by the compressor, will remain in the condenser. This increases the condenser’s internal temperature and pressure. The condenser is now operating at an elevated condensing temperature for the elevated ambient; the difference between the condensing temperature and the ambient (condenser split) remains the same.

    On the other hand, if the evaporator sees more of a heat load, more heat has to be rejected to the condenser; its condensing temperature increases. With an increased condensing temperature, the condenser split is increased because the ambient temperature remained the same.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Condensor split temperature

    Quote Originally Posted by Peter_1
    3 different answers now.
    Chemi has given you the correct answer

    Victor

  8. #8
    BigDogDad's Avatar
    BigDogDad Guest

    Re: Condensor split temperature

    The term is actually referred to as "Temperature Split" not split temperature.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Condensor split temperature

    Hi Peter in Belgium.

    I have also heard the term "temperature split" used before and it means the difference between the air temperature and the saturated refrigerant temperature (which is implied, but not talked about) and most often used for air-cooled condensers or air-cooling evaporators.

    I think it is a bad term to use because it does not describe anything, other than it somehow relates to temperature.

    For me, this term is just some old language that won't die.
    If all else fails, ask for help.


  10. #10
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: Condensor split temperature

    I think it can or has also been called approach temp. although when I hear cond. split I think entering and exiting temps of the coil. Some mfg's here in the US will give ideal delta T's for their equipment. I'll try and find one. The Testo guide below explains the way you are referring which I would think would be better called over cond. over ambient temps.

    http://www.fileden.com/files/2008/6/...Guide_2007.pdf


    page 35.
    Last edited by BigJon3475; 10-07-2008 at 02:11 AM.

  11. #11
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: Condensor split temperature

    In air-cooled condensers, the temperature difference between the ambient and the condensing temperature is referred to as the condenser split. For example, if the condensing temperature is 110 degrees F and the ambient is 80 degrees, the condenser split would be 30 degrees. Condenser splits can range from 15 degrees to 30 degrees, depending on whether the condenser is a standard-, mid-, or high-efficiency unit. The higher the efficiency, the more coil surface area there will be, thus the lower the condenser split will be. Actually the temp. on and temperature off is the temperature split but the actual heat transfer is between the desuperheating, condensing and sub cooling taking place between the refrigerant and the ambient temperature thus (Condensing split)
    Last edited by wambat; 10-07-2008 at 02:51 AM. Reason: more information

  12. #12
    phxhvac's Avatar
    phxhvac Guest

    Re: Condensor split temperature

    Quote Originally Posted by Peter_1 View Post
    I encountered already several times in literature the term ' Condensor split temperatures' What does this mean because I never heard of it before and can't find it in the books I have.
    Condenser split temperature is the temperature difference between the condensing temperature and the ambient air temperature. So for the condenser to reject the absorbed heat, it must be higher than the ambient air temperature.

  13. #13
    Join Date
    May 2007
    Location
    NC
    Posts
    264
    Rep Power
    17

    Re: Condensor split temperature

    Quote Originally Posted by phxhvac View Post
    Condenser split temperature is the temperature difference between the condensing temperature and the ambient air temperature. So for the condenser to reject the absorbed heat, it must be higher than the ambient air temperature.
    I've seen that avatar before

  14. #14
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0

    Re: Condensor split temperature

    I was taught that the term was called the CCD or correct condensing temperature. This was determined by predicting what the CCD should be and then comparing what you actually have. You then compare the two, to see if it was high or low .....
    This is done by measuring the air temp around the condenser coil and then reading the high side pressure. Then check what the actual condensing temp of the refrigerant is inside the condenser coil from the TP chart. Now comparing the delta T of the actual condenser saturated temp and the ambient air temp gives you the ACTUAL CCD, or that which has been refered to as the condenser split.
    My wife says I don't listen to her....or something like that....

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Condensor split temperature

    Difference between entering air and leaving air = delta-T or dT
    Difference between entering air and saturation temp = TD
    Difference between leaving air and saturation temp = Approach

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  2. re ref. circuit
    By shsalameh in forum Fundamentals
    Replies: 5
    Last Post: 06-08-2007, 12:59 PM
  3. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 02:43 PM
  4. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •