    problem with toshiba ras-10skv-e



    Hi,
    my air conditioner stopping cooling my room.
    Led green and yellow are on.
    Fault code 1F.
    If I set temperature to 25C or 18C the fan speed of compressor running same speed.
    Room temperature 28C without cooling.
    Air conditioner is 3 years old.

    What is there wrong on my air conditioner?



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: problem with toshiba ras-10skv-e

    hope this helps pos faulty comp or contactor

    More specific codes may be obtained, while in the fault mode through the wireless controller

    1. Press CHK to enter service mode

    2. Navigate through TIMER
     buttons until all LEDs flash, accompanied by the internal buzzer – compare the displayed code with the table below

    3. Press CLR button to clear the existing fault code (controller displays 7F)

    Press ON/OFF button to exit service mode.
    Initial code/display
    Code



    Description



    01 



    0C



    TA sensor open or short circuit

    0d



    TC sensor open or short circuit

    11



    Indoor fan motor problem

    12



    Indoor PCB problem

    01 



    04



    Indoor to outdoor communication (includes compressor thermostat)

    05



    Indoor to outdoor communication

    02 



    14



    Inverter low voltage or short circuit protection

    16



    Compressor position circuit

    17



    Compressor current detected during off-cycle

    18



    TE or TS sensor open or short circuit

    19



    Td sensor open or short circuit

    1A



    Outdoor fan motor problem

    1b



    TE sensor fault

    1C



    Compressor drive circuit

    03 



    07



    Indoor to outdoor communication (includes compressor thermostat)

    08



    Indoor heat exchanger changes temperature – but in wrong direction

    1d



    Compressor locked rotor current protection

    1E



    Compressor - high discharge temperature

    1F



    Compressor current remains too high – after current release