    Evaporator piping breakage in Carrier chillers



    Good afternoon Everybody
    I'm back after along silence here with a question , there is anybody that has experienced breakage on brand new Carrier chillers due to defective evaporator pipes?
    We just delivered a brand new ship with 4 Carrier 19XR chillers installed, at the start up one of them already have one pipe leaking in the evaporator , one month after delivery another chiller has been found completely empty (525Kg of ref.!!!) , and on other two ,some refrigerant has been already lost, some leaks were discovered on the safety valves, but even with the safety valves closed during the pressure test, the chillers are still leaking . And been in the Med in the middle of the summer knowing that your chillers could break down all together , it is scaring...
    Any comment or previous experience will be appreciated.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Evaporator piping breakage in Carrier chillers

    Possibilities, evap tubes over expanded, incorrectly expanded or not expanded on internal support sheets. Lofin tubng over rolled and cracking at root of low fin.
    What are Carrier saying/ doing about all the faults? Would seem to a disaster inprogress. Definitly scary.

  3. #3
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Evaporator piping breakage in Carrier chillers

    I have seen this problem with machines 19xl carrier, were cooled with seawater