    Soft Stator Problem



    Dear Forum

    I am using Soft stator for my Bitzer screw Semihermetic Compressor of 125HP
    After 7 Months it was burnted {Picture Enclosed}

    Can any help , how can motor will burnt out with Soft Stator.

    Regards



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Soft Stator Problem

    Hello
    Was oil return sufficient at all (at most) of the working time of the compressor?
    Was windings temperature controlled with the help of the proper control devices?
    Reliable overcurrent protection was also installed?

  3. #3
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    Dear Sir


    Everything is fine ,we checked it .

    We came to know that if semi Conductor is Failed ,The motor burnt will takes place
    is that true .

    Regards

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Soft Stator Problem

    Everithing is possible, especially if the starter was of low quality, or insufficient functionality and you relied on it as a sole protection of your motor.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Soft Stator Problem

    Did you specified to Bitzer your compressor should be controlled by a softstarter?
    Arcing is very likely to happen with a soft starter.

    Was the softstarter also the and the only protection of the motor?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    Soft starter should have a parallel line contactor that takes load, I have heard of lots of failures with starters without them The SCR's fail and set up protection is not quick enough to stop winding failures, usually at max loads.

  7. #7
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    Their is no by-pass contactor , The complete one part winding is damaged ,My doubt was, the winding got bunted
    when the motor was in off .

    When the burnt has taken place when it is in running the carbon deposit will be in whole compressor and the oil will be in complete black color
    but it is in green color .

    The compressor has a saftey of High Winding Temperature Trip , even the thermistor was completly melted

    still we are finding for the exact cause

  8. #8
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Soft Stator Problem

    Hi
    what was the use of this bitzer ?was it instaled in a chiller?what was the brand?
    was your soft starter a " siemens" made ?
    we encounterd a simiilar burnout that was covered by warrnty!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  9. #9
    Join Date
    Jul 2007
    Location
    Italy
    Age
    55
    Posts
    18
    Rep Power
    0

    Re: Soft Stator Problem

    "Starting Time" configuration is critical on Soft Starters and should be strictly configured according manufacturer specifications.

    A too long starting time can generate a thermal "stress" of motor winding that can easily ends in a burnout.

    This can be easily verified stripping down the compressor and inspecting the defective motor (you should find a motor winding completely overheated).

    Anyway keep yourself "open minded" and consider also most "classic" reasons for burnout....

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    Hi
    the winding configuration and terminations in the compressor terminal box. Were the winding star connected or delta connected. That is to say low voltage or high voltage connections
    One winding failure of three windings, big blow hole in a winding or three windings cooked. What was the result of failure

  11. #11
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    Hi , the winding is delta connected, one winding is failure ,
    below the terminal plate out of six leads , three leads are melted.

    When the compressor is running at -18Deg Temperature this burnout has taken place
    at discharge side on suction side the winding is good.

    its a bitzer make

    I dint understand one thing , the motor burnout has taken exactly below the terminal plate , there is
    a high winding temperature thermistor is there to trip in high temperature ,even though it get failure .

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    Hi ssk,
    interesting failure result, flash over happened at the terminal block and one winding failed. Generally the flash over would happen at the weakest point, in your case the terminal block. The initial problem was in a winding failure, probably in the winding slots, possible cause would be contaminents,breaking down insulation on windings, creating high current draw on one winding and that same contaminate created the flash over at the terminal block. Suggest moisture was the intital problem. Winding thermistors would not react fast enough, and shock outage of failure would not be protected by starter

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Soft Stator Problem

    Quote Originally Posted by ssk7899 View Post
    Their is no by-pass contactor , The complete one part winding is damaged

    There you go. The soft starter should be connected to both windings at once, as in direct on line start. You soft started one winding, which is a no no.

  14. #14
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Soft Stator Problem

    HI
    as i stated above, we had a similar problem with a bitzer ,the soft starter that was used, only has two thyristors,one phase is always energized,for some crazy reason the soft starter malfunctioned and the entire compressor overheated until it shorted out ,allthough it had all the protectiones instaled like the criwan module etc.
    a intresting anomally!
    we still dont know what really happened ,the warranty covered this one !!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  15. #15
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    Warranty was not covered , but even bitzer people are saying that it was burnted because of thyristors fail.
    its get malfuncoined.
    But this a crazy thing .. i faced for a first time

    I like to know the exact working cylce of soft-stator , can any one suggest me.
    There is any website for this.

    Regards

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    Hi,
    I have to admit that I have never come across a soft starter that functions on only two phases. Leaving one winding live. What brand of soft starter did you install and I will keep away from them.
    But I have seen installed two phase contactors, scary stuff.
    Check Danfoss Drives for a reputable brand. All the bells and whistles protection. The HVAC series are basically designed for what you want.

  17. #17
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    It was not a brand make . But i like to know , What chances are there for Motor Burnt-Out , When it is running with soft starter .
    It is a Dol , there is no by pass line conductor .
    We connected all the six leads to the stater - where the stater has three bridges .
    Out of this One part winding has damaged.

  18. #18
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    Hi
    please clarify if part wind motor, if so you will have 12 terminals in the terminal box. Should be wired for high voltage start arrangement, or DOL / delta configuration. Which means you will have 6 links , or three per winding. The links should go top to bottom on each winding. Then connect supply from starter to each set of windings in the same patton . ie.,
    Can you post a picture of terminal box, this would make things a lot clearer for comments

  19. #19
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    I phone Pics 222.jpgI phone Pics 221.jpgI phone Pics 218.jpg
    Hi
    Yes it is part winding motor 50:50 , its a Dol Connection , on terminal plate it has six links , three links per winding.

  20. #20
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Soft Stator Problem

    one more picture please see it.burnt pic.bmp
    Attached Images Attached Images

  21. #21
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Soft Stator Problem

    The back of terminal block has six terminals. Interesting winding failure, half the stator cooked / slow burn and coil tails blown off. Possible loss of one phase started failure.

  22. #22
    Join Date
    Oct 2010
    Location
    Dubai
    Age
    57
    Posts
    15
    Rep Power
    0

    Re: Soft Stator Problem

    HI,

    This type of failure has got in part winding normal DOL (contactor ) Two contactor starter type due to contactor hold on problem and the shift timer problem. But here it is soft starter ,by soft starters winding burning like this , is very rare.The picture shows that it has been run few with high winding temperature(even if there is thermistor) .If the moisture presence inside the system the same type of problem has been observed . In screw compressors the terminal box inside getting moisture condensation and thus it gose to ground fault.In this situation if the ground fault protection configuaration is not perfect , it leads to winding failre.intresting analysis***** Keep on discussion.